Quote Originally Posted by RegElec View Post
Thanks for the replies. The comments are as expected. I have bridged the earth / neutral in the main DB and left the sub DB's as TN-S. We will just have to monitor the conductors as I doubt I will get any luck with eskom to replace the earth wire at the transformer although I will try.
I would rather have done it at the meter box if possible at least then i would not have contravened 6.1.6 and if there is a huge surge down neutral earth bond it would happen outside
I say that not knowing cable sizes , positioning etc


SANS10142-1
6.1.6 The neutral conductor shall not be connected direct to earth or to the
earth continuity conductor on the load side of the point of control except as
allowed in 7.16.4.