    Quote Originally Posted by RegElec View Post
    Thanks for the replies. The comments are as expected. I have bridged the earth / neutral in the main DB and left the sub DB's as TN-S. We will just have to monitor the conductors as I doubt I will get any luck with eskom to replace the earth wire at the transformer although I will try.
    I would rather have done it at the meter box if possible at least then i would not have contravened 6.1.6 and if there is a huge surge down neutral earth bond it would happen outside
    I say that not knowing cable sizes , positioning etc


    SANS10142-1
    6.1.6 The neutral conductor shall not be connected direct to earth or to the
    earth continuity conductor on the load side of the point of control except as
    allowed in 7.16.4.

  2. #2
    Full Member
    Join Date
    Oct 2012
    Location
    Durban
    Posts
    72
    Thanks
    0
    Thanked 5 Times in 4 Posts
    Quote Originally Posted by GCE View Post
    I would rather have done it at the meter box if possible at least then i would not have contravened 6.1.6 and if there is a huge surge down neutral earth bond it would happen outside
    I say that not knowing cable sizes , positioning etc


    SANS10142-1
    6.1.6 The neutral conductor shall not be connected direct to earth or to the
    earth continuity conductor on the load side of the point of control except as
    allowed in 7.16.4.
    Noted. I have access to the meter box so I will see whether it can be done there.

  3. #3
    Full Member
    Join Date
    Oct 2012
    Location
    Durban
    Posts
    72
    Thanks
    0
    Thanked 5 Times in 4 Posts
    Quote Originally Posted by RegElec View Post
    Noted. I have access to the meter box so I will see whether it can be done there.
    I think I jumped the gun there. I cannot join the earth neutral at the kiosk / meter box as there is no earth there. The supply to the kiosk is via aerial bundled conductor and there are only three phases and the neutral which is connected to a dumpy insulator but no earth termination is present.

Similar Threads

  1. [Question] Very specific tax invoice requirement spec
    By Hp10Bii in forum Tax Forum
    Replies: 1
    Last Post: 05-Sep-19, 11:09 AM

Did you like this article? Share it with your favourite social network.

Did you like this article? Share it with your favourite social network.

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •