Thread: Socket outlets 3 phase - ELU

  1. #11
    Platinum Member
    Join Date
    Mar 2022
    Location
    South Africa
    Posts
    2,171
    Thanks
    59
    Thanked 102 Times in 97 Posts
    That makes sense, and considering you mentioned they have been there since 2006 and they still work, shows maybe its not such an extreme environment.

    I recall the shops we worked in the electrics took a proper beating. I use to hate working working in the fast food shops, peeling off fat from the fitting to get to the screws, eeeeish not something I miss. the hit and run revamp fellas were in and out ASAP.


    Quote Originally Posted by GCE View Post
    I am not aware of any that have exemptions - We have no nuisance tripping but you must put in a ELU per 3 machines
    The reason it was done is so they/staff can change a machine out , put it on the truck back to head office for repair etc - No electrician needed to disconnect - Also helps when they deep clean that they can move equipment out of the way
    Comments are my opinion, unless regulations are attached to support the comment. This is social media, not a court room.

  2. #12
    Platinum Member
    Join Date
    Mar 2022
    Location
    South Africa
    Posts
    2,171
    Thanks
    59
    Thanked 102 Times in 97 Posts
    This is an interesting topic, with many considerations to take into account.


    1/ Is the location suitable for a socket outlet?

    2/ Should it be treated as a stationary or portable appliance it has wheels and is moved around. It is certainly not a fixed appliance.

    3/ Can the socket be mounted directly above the appliance?

    4/ Should it be a dedicated socket outlet not connected to an ELU?

    6/ Should the socket be IP rated, considering the location, but also taking into account that there is an extractor fan which can create enough air movement to reduce the impact of the heat and moisture?

    7/ The type of cable used to connect the appliance to the socket outlet, heat and oil resistant, and double insulated.

    I am sure this topic has been discussed in detail with a panel of engineers for them to be exempt from ELU protection for certain fast food outlets (if that is the case, which I am sure it was, considering the source of the information).

    It is a topic that would certainly require some consideration.

    If you walked in the room and just looked at the location of the socket in comparison to the appliance, during normal operation your first impression would be ... who would be so stupid as to install a socket directly above an appliance like a chip fryer, with all that heat and moisture" but clearly the cost factor to install ELU for ever single 3 phase socket outlet in the shop"


    6.16.1.1 Fixed appliances do not form part of the electrical installation other than their positioning in relation to the supply and the wiring carried out between different parts of the appliances.

    b) a socket-outlet that is directly accessible at all times that any person is exposed to such appliance while the supply is on. In the case of a remotely installed appliance, the position of the disconnecting device shall be indicated by means of a notice in close proximity to or on the appliance.


    NOTE The socket-outlet has to be protected against earth leakage so, unless the protection device (see (b)) is in the control unit, the entire cooking appliance circuit has to be protected against earth leakage.


    b) a socket-outlet that complies with SANS 60309-1 (industrial type) with 30 mA earth leakage protection, however, the use of industrial type socketoutlets is not recommended for stove connections.


    6.16.3 Cooking appliances NOTE Cooking appliances include built-in stoves, oven hobs, and the like (see also 6.16.1).

    6.16.3.1 Switch-disconnector6.16.3.1.1 The circuit that supplies a cooking appliance through fixed wiring, a stove coupler (see 6.16.3.3), or an industrial type socket-outlet (see SANS 60309-1), shall have a readily accessible switch-disconnector. The switch-disconnector may supply more than one appliance.

    6.16.3.1.2 A switch-disconnector for a cooking appliance(s) shall a) be in the same room as the appliance(s), b) be at a height above floor level of not less than 0,5 m and not more than 2,2 m,c) preferably not be above the cooking appliance(s), d) be within 3 m of the appliance(s), but within 0,5 m of the appliance(s) if the switch-disconnector's purpose is not clearly indicated, and



    Not forgetting the OSHACT, I am sure there is a bunch of regs that should also be considered.
    Comments are my opinion, unless regulations are attached to support the comment. This is social media, not a court room.

  3. #13
    Platinum Member
    Join Date
    Mar 2022
    Location
    South Africa
    Posts
    2,171
    Thanks
    59
    Thanked 102 Times in 97 Posts
    You also need to consider that some of the appliance connected to the socket outlets are sealed during normal operation and not open.
    Comments are my opinion, unless regulations are attached to support the comment. This is social media, not a court room.

  4. #14
    Platinum Member Derlyn's Avatar
    Join Date
    Mar 2019
    Location
    East london
    Posts
    1,563
    Thanks
    110
    Thanked 148 Times in 141 Posts
    For me, it's quite simple.

    Had that installation been built yesterday, it would be a requirement for those socket outlets to be on earth leakage.
    That cannot be disputed.

    I cannot remember once ever not fitting an earth leakage to circuits that require them, irrespective of the date that the installation was installed.
    A socket outlet, without earth leakage protection, installed in 1990 has the same potential of injury or death as one installed yesterday without earth leakage protection.

    That is the reason why SANS has an Amdt 1 recommending that earth leakage be installed on all circuits requiring same, irrespective of the installation date.

    In answering GCE's original query, I think it's the right thing to install earth leakage protection and I would use the above recommendation as motivation.


    Have a lekker weekend.

  5. Thanks given for this post:

    GCE (18-May-24)

  6. #15
    Platinum Member
    Join Date
    Mar 2022
    Location
    South Africa
    Posts
    2,171
    Thanks
    59
    Thanked 102 Times in 97 Posts
    I wish it was that simple, not all socket outlets have to be on earth earth leakage.

    Quote Originally Posted by Derlyn View Post
    For me, it's quite simple.

    Had that installation been built yesterday, it would be a requirement for those socket outlets to be on earth leakage.
    That cannot be disputed.

    I cannot remember once ever not fitting an earth leakage to circuits that require them, irrespective of the date that the installation was installed.
    A socket outlet, without earth leakage protection, installed in 1990 has the same potential of injury or death as one installed yesterday without earth leakage protection.

    That is the reason why SANS has an Amdt 1 recommending that earth leakage be installed on all circuits requiring same, irrespective of the installation date.

    In answering GCE's original query, I think it's the right thing to install earth leakage protection and I would use the above recommendation as motivation.


    Have a lekker weekend.
    Comments are my opinion, unless regulations are attached to support the comment. This is social media, not a court room.

  7. #16
    Platinum Member Derlyn's Avatar
    Join Date
    Mar 2019
    Location
    East london
    Posts
    1,563
    Thanks
    110
    Thanked 148 Times in 141 Posts
    Quote Originally Posted by Isetech View Post
    I wish it was that simple, not all socket outlets have to be on earth earth leakage.
    We are all aware that there are certain instances such as listed in 6.7.5.5 where earth leakage protection is not a requirement

    however

    those socket outlets in the photo supplied by the poster and on which the query was based, do not fall into that category.

  8. #17
    Platinum Member
    Join Date
    Jun 2017
    Location
    Port Elizabeth
    Posts
    1,293
    Thanks
    36
    Thanked 314 Times in 263 Posts
    HI

    I received an answer from another source with regards to my query and was surprised to hear it has been around since 1993 - I unfortunately do not have SANS codes going back that far-The earliest I have is 2001 and that does have the ELU requirement in.

    Looking at the install and knowing who did the original design I can only assume that originally there were Isolators installed and that somewhere along the way when the franchise changed there machines to 3 phase plug tops a contractor went along and changed the isolators to 3 phase sockets without thinking/knowing the regulations.

    Present store owner is hopping up and down now as we have said either we fit ELU for which there is no space in the DB , which means a new DB which also has space constraints , or we change sockets back to isolators .
    He obviously does not want the expense or the shut down to his kitchen for a couple of hours while we change them

    He seems to think his other option will be to get a contractor that will sign it off , which unfortunately could happen as there is always somebody that will prostitute his license without realizing that down the line he could end up in a court case for manslaughter.


    Answer received from others
    With reference to SANS 10142-1,

    6.7.5.2 Industrial type single-phase and three-phase socket-outlets
    (including “welding” socket-outlets) shall comply with the requirements of
    SANS 60309-1 and SANS 60309-2 and, except as allowed in 6.7.5.5 and
    7.10.1.6, shall have earth leakage protection if the circuit is intended to supply
    portable or stationary class I appliances.

    This part of the code has not changes since 1993 so irrespective when the installation was done, the date of installation has no relevance to it.

  9. Thank given for this post:

    AndyD (22-May-24), Dave A (22-May-24), Derlyn (22-May-24)

  10. #18
    Diamond Member AndyD's Avatar
    Join Date
    Jan 2010
    Location
    Cape Town
    Posts
    4,927
    Thanks
    577
    Thanked 936 Times in 757 Posts
    This is an issue that's common with non-retrospective regs where it's difficult to establish both when the reg was implimented and when the installation took place. It's time consuming for the contractors to establish this. There ought to be an accessible repository of past regs and ammendments maintained by a reliable source and available to all electricians.
    _______________________________________________

    _______________________________________________

  11. #19
    Platinum Member
    Join Date
    Jun 2017
    Location
    Port Elizabeth
    Posts
    1,293
    Thanks
    36
    Thanked 314 Times in 263 Posts
    Quote Originally Posted by AndyD View Post
    This is an issue that's common with non-retrospective regs where it's difficult to establish both when the reg was implimented and when the installation took place. It's time consuming for the contractors to establish this. There ought to be an accessible repository of past regs and ammendments maintained by a reliable source and available to all electricians.
    Not a bad idea - have banged it through to ECA but I dont expect results

    Maybe we should start a thread and make it stick but it would need the first paragraph to be editable by some one so that you don't have to page through looking - It could be posted on the tread and then the first post could just keep adding dates .
    We have one and others that bounce to mind would be geyser on ELU - The introduction of euro socket. Those question will start and have started already

  12. #20
    Gold Member
    Join Date
    Jun 2020
    Location
    Fourways
    Posts
    769
    Thanks
    119
    Thanked 35 Times in 34 Posts
    I really think the older publications should be free, I was not around 30 years ago, well I was a baby, so how could I know the rules then, more so in my learnership the boss was not much older than me and his earliest edition was from 2006 I think or when it was edition 2.

    The knowledge from the older lads mostly goes to the grave with them so having the older additions free helps or even a document stating the major changes from each edition.

    As said above what to do with geysers and earth leakages? When did earth leakage need to be on geysers, like year and addition.



    Sent from my CPH2197 using Tapatalk

Page 2 of 3 FirstFirst 123 LastLast

Similar Threads

  1. New ZA socket outlets and plugs.
    By Derlyn in forum Electrical Contracting Industry Forum
    Replies: 2
    Last Post: 10-Apr-23, 01:17 PM
  2. Gas stove and socket outlets
    By Isetech in forum Electrical Contracting Industry Forum
    Replies: 2
    Last Post: 28-Mar-22, 07:16 PM
  3. Protected socket outlets
    By Derlyn in forum Electrical Contracting Industry Forum
    Replies: 9
    Last Post: 03-Mar-22, 12:16 PM
  4. Socket Outlets Wiring
    By swordfish in forum Electrical Contracting Industry Forum
    Replies: 5
    Last Post: 30-Sep-21, 07:19 PM
  5. SANS 163-2 Socket Outlets
    By RegElec in forum Electrical Contracting Industry Forum
    Replies: 14
    Last Post: 13-Jan-20, 07:26 PM

Did you like this article? Share it with your favourite social network.

Did you like this article? Share it with your favourite social network.

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •