2 points, I think, worth mentioning are: ( please correct me if I am wrong )
1) Lights not working does not invalidate a COC. Lights are fixed appliances and as long as the supply is good up to the terminals on the fitting, it passes the COC test.
2) Geyser bonding: As long as continuity can be proven by the test described in 8.6.2 then no external bonding conductors are required.
8.6.2 Continuity of bonding
Test the continuity of the bonding between the consumers earth terminal and all exposed conductive parts using a supply that has a no-load d.c. or a.c. voltage of 4 V to 24 V and a current of at least 0,2A. In each case, the resistance shall not exceed 0,2 Ohms.