    Section 3 of the test report

    This section should be discussed in more detail, too many people write absolute rubbish in this section.

    The description of the installation covered is only the part fed from the DB mentioned in the top left corner, not the entire site.

    If for example the pool DB was no longer referred to as an appliance because additional circuit were added, like a gate motor or garden lights etc.

    The top left would read - Pool DB

    The description of installation covered by this report would read - Pool DB fed from the main DB, includes the gate motor and gate lights along the fence.

    Lighting circuit - 1
    Light points - 3
    Socket outlet - 1 (Gate)
    Fixed appliance - pool pump - 1 (this is another tricky part)

    Earth leakage protects
    - complete installation - 1 (if the earth leakage in the main DB is used to protect the DB)
    - only part of the installation - ( this would be used if the earth leakage was mounted in the pool DB)

    Please feel free to add your comments, as we are all aware we all do things the way we think is right, but its doesnt always mean it is 100 % correct, I am not too old to learn.

  2. Thanks given for this post:

    Gene (17-Sep-22)

  3. #2
    Gold Member
    Join Date
    Jun 2020
    Location
    Fourways
    Posts
    776
    Thanks
    121
    Thanked 36 Times in 35 Posts
    I was tought that the description is what you certifying. For example, to certify the socket outlet in the main bedroom.

    For a full CoC would say to certify the entire installation.

    Sent from my CPH2197 using Tapatalk

  4. #3
    Platinum Member
    Join Date
    Mar 2022
    Location
    South Africa
    Posts
    2,274
    Thanks
    60
    Thanked 103 Times in 98 Posts
    Quote Originally Posted by Dylboy View Post
    I was tought that the description is what you certifying. For example, to certify the socket outlet in the main bedroom.

    For a full CoC would say to certify the entire installation.

    Sent from my CPH2197 using Tapatalk
    That is why you attach a supplementary test report the the original COC which is completed correctly.

    Under description you will write socket outlet in the main bedroom and complete the test report with the relevant details to that socket, not the entire installation.

  5. #4
    Gold Member
    Join Date
    Jun 2020
    Location
    Fourways
    Posts
    776
    Thanks
    121
    Thanked 36 Times in 35 Posts
    Ahhhh no you see I thought and was tought you do a Sup Certificate and a test report. Not just an additional test report to the initial CoC.

    Sent from my CPH2197 using Tapatalk

  6. #5
    Platinum Member
    Join Date
    Mar 2022
    Location
    South Africa
    Posts
    2,274
    Thanks
    60
    Thanked 103 Times in 98 Posts
    Quote Originally Posted by Dylboy View Post
    Ahhhh no you see I thought and was tought you do a Sup Certificate and a test report. Not just an additional test report to the initial CoC.

    Sent from my CPH2197 using Tapatalk
    You are correct, the supplementary COC/test report must be added to the original COC/test report. Unless you are the person who issued the original COC, then all your details will be on the original COC/test report, so I dont see it being a problem, just adding a supplementary test report to the original which covers that part of the installation.

  7. #6
    Platinum Member
    Join Date
    Jun 2017
    Location
    Port Elizabeth
    Posts
    1,401
    Thanks
    39
    Thanked 331 Times in 278 Posts
    The dates etc will be incorrect - It requires a COC which will need a test report

Similar Threads

  1. Coc and test report.
    By Derlyn in forum Electrical Contracting Industry Forum
    Replies: 2
    Last Post: 31-May-22, 08:41 AM
  2. The test report format
    By ians in forum Electrical Contracting Industry Forum
    Replies: 8
    Last Post: 27-Jan-22, 08:41 AM
  3. COC and test report
    By ians in forum Electrical Contracting Industry Forum
    Replies: 51
    Last Post: 25-Jan-22, 05:12 PM
  4. Completed Section 28 Trade Test, Please Suggest The Next Best Step
    By Deon1991 in forum Electrical Contracting Industry Forum
    Replies: 3
    Last Post: 21-Aug-17, 09:10 PM
  5. [Question] Pastel Tax Box Report & Vat Detail report giving different figures!
    By Cin8 in forum Accounting Forum
    Replies: 3
    Last Post: 22-May-12, 03:57 PM

Did you like this article? Share it with your favourite social network.

Did you like this article? Share it with your favourite social network.

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •