    712.521.103 Wiring loops


    To reduce the magnitude of transient overvoltages, the PV array wiring shall be laid in such a
    way that the area of conductive loops is minimum (e.g. by laying cables in parallel as shown
    in Figure 712.10)
    Comments are my opinion, unless regulations are attached to support the comment. This is social media, not a court room.

  2. #12
    Diamond Member Justloadit's Avatar
    Join Date
    Nov 2010
    Location
    Johannesburg
    Posts
    3,507
    Thanks
    138
    Thanked 697 Times in 595 Posts
    Blog Entries
    1
    Quote Originally Posted by Isetech View Post
    Page 36 clears up the confusion with regards to solar wires in PVC/metallic wireways.

    If you decide to install single insulated cable in PVC conduit, it must be installed in a separate conduit, however

    IF you install double insulated PV specific cable, it should be installed inside the same PVC or metallic conduit.

    In fact as you read the document, you will see that every precaution should be taken not to separate the conductors to prevent other issues.

    The positive and negative should be installed as close as practical at all times, even between the panels, jumping for the top to the bottom string with only one conductors is not advisable.

    Lets get the fact correct.
    There is a reason to keep the 2 DC wires close as possible(parallel), being DC, there is a magnetic field created around the wire if it is individual. Having both close to each other cancels this magnetic field.

    Understanding that the wire could be similar to a wire in a generator, it can induce voltages in any other wire running close. Now in most cases there is a a high DC current flowing, and high lights how strong these magnetic fields become, now imagine the same thought with respect to battery supplied cables pushing +100A.
    Victor - Knowledge is a blessing or a curse, your current circumstances make you decide!
    Solar pumping, Solar Geyser & Solar Security lighting solutions - www.microsolve.co.za

  3. #13
    Platinum Member
    Join Date
    Mar 2022
    Location
    South Africa
    Posts
    2,274
    Thanks
    60
    Thanked 103 Times in 98 Posts
    I have seen installations where the panel wiring goes along the top pos. to neg. around the outside, then down to the next string and along the bottom and back up to top, creating a nice big loop.

    Some installations, every second panel is flipped also creating anice big open loop.

    Then you get the one where the pos. is on the left and the neg. is on the right of the string.

    But hey people learning as they go, there is still a lot to learn and unfortunately the customer is going to sit with the problems.



    Quote Originally Posted by Justloadit View Post
    There is a reason to keep the 2 DC wires close as possible(parallel), being DC, there is a magnetic field created around the wire if it is individual. Having both close to each other cancels this magnetic field.

    Understanding that the wire could be similar to a wire in a generator, it can induce voltages in any other wire running close. Now in most cases there is a a high DC current flowing, and high lights how strong these magnetic fields become, now imagine the same thought with respect to battery supplied cables pushing +100A.
    Comments are my opinion, unless regulations are attached to support the comment. This is social media, not a court room.

Page 2 of 2 FirstFirst 12

Similar Threads

  1. Split conduit for the solar wires
    By Isetech in forum Electrical Contracting Industry Forum
    Replies: 16
    Last Post: 24-Apr-24, 05:41 PM
  2. Fibre and network cables in electrical wireways
    By Isetech in forum Electrical Contracting Industry Forum
    Replies: 3
    Last Post: 10-Mar-24, 11:42 AM
  3. Double insulated wire
    By Isetech in forum Electrical Contracting Industry Forum
    Replies: 5
    Last Post: 12-Sep-22, 06:50 PM
  4. Oil filled paper insulated cable
    By skatingsparks in forum Electrical Contracting Industry Forum
    Replies: 8
    Last Post: 03-Mar-21, 11:36 AM
  5. Double tube Double headscratch
    By mikilianis in forum Electrical Contracting Industry Forum
    Replies: 4
    Last Post: 14-Apr-11, 06:38 PM

Did you like this article? Share it with your favourite social network.

Did you like this article? Share it with your favourite social network.

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •