Results 1 to 6 of 6

Thread: Size of Earth conductor

  1. #1
    Bronze Member
    Join Date
    Mar 2022
    Location
    Little Falls, Roodepoort
    Posts
    122
    Thanks
    54
    Thanked 9 Times in 8 Posts

    Size of Earth conductor

    Just checking if I'm interpreting 10142 - "6.12 Earthing" correctly:-

    Can I use 1.5mm earth cable with 2.5mm phase conductors?
    -Single conductors - house wire.
    -Small domestic flat not exceeding 50m lengths - more like 20m max
    -20A circuit breaker

    Many thanks!

  2. #2
    Platinum Member
    Join Date
    Jun 2017
    Location
    Port Elizabeth
    Posts
    1,266
    Thanks
    34
    Thanked 308 Times in 260 Posts
    If you look at Table 6.28(a) - on a C/Breaker where Im = 10x In and the CB is 20Amp the max length of earth wire at 1,5sqmm will be 30m

    Don't run the 1,5sqmm to the geyser as that it another whole can of worms.

    I would say you can run a 1,5sqmm as long as the length is under 30m

  3. Thanks given for this post:

    Andrew_van_Zyl (07-Jun-22)

  4. #3
    Bronze Member
    Join Date
    Mar 2022
    Location
    Little Falls, Roodepoort
    Posts
    122
    Thanks
    54
    Thanked 9 Times in 8 Posts
    Many thanks GCE

  5. #4
    Bronze Member
    Join Date
    Mar 2022
    Location
    Little Falls, Roodepoort
    Posts
    122
    Thanks
    54
    Thanked 9 Times in 8 Posts
    Quote Originally Posted by GCE View Post
    If you look at Table 6.28(a) - on a C/Breaker where Im = 10x In and the CB is 20Amp the max length of earth wire at 1,5sqmm will be 30m

    Don't run the 1,5sqmm to the geyser as that it another whole can of worms.

    I would say you can run a 1,5sqmm as long as the length is under 30m
    GCE - for educational purposes, what are the issues when using the same rationale for a geyser? 6.28(a) Would indicate it's ok?

  6. #5
    Platinum Member
    Join Date
    Jun 2017
    Location
    Port Elizabeth
    Posts
    1,266
    Thanks
    34
    Thanked 308 Times in 260 Posts
    Quote Originally Posted by Andrew_van_Zyl View Post
    GCE - for educational purposes, what are the issues when using the same rationale for a geyser? 6.28(a) Would indicate it's ok?
    The bonding conductor must be 2,5sqmm - Was a long discussion in a previous thread and I have pasted the link and relevant pieces below
    https://www.theforumsa.co.za/forums/...ng-and-bonding


    If all pipes are pvc then the geyser needs to be bonded as per 6.16.2 - Then that is where the grey area of Twin & earth not having a full 2,5sqmm earth will come in.

    6.13.2.2 Hot and cold water systems
    Where the hot water system includes electric components and the water pipes
    are of conducting material, hot and cold water systems shall be bonded
    together and also be bonded to the earth continuity conductor system

    6.16.2 Water heaters
    NOTE Water heaters include geysers, instantaneous water heaters including units for
    boiling water, heat pumps, solar systems, induction water heaters and the like (see also
    6.16.1). electrode water heaters, steam generators and boilers are not included (refer
    to 6.16.7)
    6.16.2.1 All water heaters shall be bonded in accordance with 6.13 and a.c.
    supply circuits shall be protected by earth leakage protection with IΔn not
    exceeding 30 mA.
    NOTE To mitigate nuisance earth leakage tripping, an additional earth leakage may
    be provided.
    6.13 Bonding
    NOTE 1 The aim of bonding is to bring all the bonded parts to the same electrical
    potential.
    NOTE 2 No external conductor is required if compliance with the requirements for
    continuity can be proved by the test in 8.6.2.

  7. Thanks given for this post:

    Andrew_van_Zyl (07-Jun-22)

  8. #6
    Bronze Member
    Join Date
    Mar 2022
    Location
    Little Falls, Roodepoort
    Posts
    122
    Thanks
    54
    Thanked 9 Times in 8 Posts
    Quote Originally Posted by GCE View Post
    The bonding conductor must be 2,5sqmm - Was a long discussion in a previous thread and I have pasted the link and relevant pieces below
    https://www.theforumsa.co.za/forums/...ng-and-bonding
    Many thanks

Similar Threads

  1. Replies: 7
    Last Post: 14-Dec-21, 05:23 PM
  2. [Question] Earth Tag as Earth Continuity Conductor
    By Matt.24 in forum Electrical Contracting Industry Forum
    Replies: 3
    Last Post: 07-Oct-21, 09:02 AM
  3. [Question] Cable size
    By Jaboel in forum Electrical Contracting Industry Forum
    Replies: 2
    Last Post: 06-Dec-17, 07:24 AM
  4. Conductor identification
    By Gtfast in forum Electrical Contracting Industry Forum
    Replies: 5
    Last Post: 29-Nov-17, 07:29 PM
  5. How's this for size?
    By greasemonkey in forum Labour Relations and Legislation Forum
    Replies: 3