Welcome to The Forum SA. As a visitor you have read only access to the public content areas of this website. You will have to register as a member to access all content, post messages and network with our members. Membership is free and registering is quick and easy. You can click here to register now and become a member within minutes.
Vov generators connected to distribution board supply
The first thing to consider is that if there is no return path, there will be no "fault" current. (One of the basic principles of a safety supply).
The second thing to consider is as follows:
There is a supply side and a load side to an RCD.
The return path for a fault on the load side has to be via the supply side of the RCD for the RCD to trip.
If the fault point and return are both on the load side, the RCD will not trip as there is no difference in current at the points in the circuit it is measuring to sense a difference in current.
Hey Dave, had a couple of dops as it's my heritage haha. But don't you mean the Line side in the last paragraph or should I read it again tomorrow hahaha
We process personal data about users of our site, through the use of cookies and other technologies, to deliver our services, personalize advertising, and to analyze site activity. We may share certain information about our users with our advertising and analytics partners. For additional details, refer to our Privacy Policy.
By clicking "I AGREE" below, you agree to our Privacy Policy and our personal data processing and cookie practices as described therein. You also acknowledge that this forum may be hosted outside your country and you consent to the collection, storage, and processing of your data in the country where this forum is hosted.