A socket circuit is allowed to feed fixed appliances as per reg6.15.4.2
A pool pump falls under reg 6.16 fixed appliances
The Circuit breaker should have been labeled as mixed loads
With regards to the wire size - If the upstream breaker , the one in the DB , is 20 Amp then 2,5sqmm wire is fine .
6.15.4 Mixed loading of circuits
6.15.4.1 Except as allowed in 6.15.4.2, 6.15.4.3 and 6.16.3.2.3, there shall
be no mixed loading of circuits.
6.15.4.2 Except as required in 6.16, a non-dedicated single-phase circuit that
has overcurrent protection rated at not more than 20 A may supply a mixed
load of a combination of any socket-outlets rated at not more than 16 A,
luminaires and fixed appliances.
NOTE 1 The number of points need not be limited, but the diversity of loads should be
considered.
NOTE 2 Mixed circuits should be carefully considered since this may result in nuisance
tripping.
6.15.4.3 Socket-outlets rated at 16 A or more that are connected to circuits
with mixed loading shall comply with the earth leakage requirements of 6.7.5.
NOTE 1 See 7.1 for the conditions under which a socket-outlet may be installed in a
bathroom.
NOTE 2 See 6.16.1.6 for the conditions under which a socket-outlet may be used for
the connection of fixed appliances.
6.16.5 Motors
NOTE Motors include the motors in automatic doors and gates, garbage disposal
units, pumps (pool, fountain, spa, etc.), and the like (see also 6.16.1).
A pool pump falls under reg 6.16 fixed appliances
The Circuit breaker should have been labeled as mixed loads
With regards to the wire size - If the upstream breaker , the one in the DB , is 20 Amp then 2,5sqmm wire is fine .
6.15.4 Mixed loading of circuits
6.15.4.1 Except as allowed in 6.15.4.2, 6.15.4.3 and 6.16.3.2.3, there shall
be no mixed loading of circuits.
6.15.4.2 Except as required in 6.16, a non-dedicated single-phase circuit that
has overcurrent protection rated at not more than 20 A may supply a mixed
load of a combination of any socket-outlets rated at not more than 16 A,
luminaires and fixed appliances.
NOTE 1 The number of points need not be limited, but the diversity of loads should be
considered.
NOTE 2 Mixed circuits should be carefully considered since this may result in nuisance
tripping.
6.15.4.3 Socket-outlets rated at 16 A or more that are connected to circuits
with mixed loading shall comply with the earth leakage requirements of 6.7.5.
NOTE 1 See 7.1 for the conditions under which a socket-outlet may be installed in a
bathroom.
NOTE 2 See 6.16.1.6 for the conditions under which a socket-outlet may be used for
the connection of fixed appliances.
6.16.5 Motors
NOTE Motors include the motors in automatic doors and gates, garbage disposal
units, pumps (pool, fountain, spa, etc.), and the like (see also 6.16.1).
Comment