Generator connection

Collapse
X
 
  • Time
  • Show
Clear All
new posts
  • ians
    Diamond Member

    • Apr 2010
    • 3943

    #1

    Generator connection

    I am getting lots of generator inquiries again, people are getting nervous and want to prepare themselves for what they think is going to happen.

    I have a simple solution and would like to hear your thoughts.

    For my own house i am using a 2.2 kva generator.

    I have a changeover switch mounted directly above my meter box, fed from the 60 amp circuit breaker using a 16 mm wire into one side of the changeover switch.

    I have a 16 amp plug top with a 2.5 mm x 3 core feed from the generator to the other side of the changeover switch ( the generator has built in overload protection)

    from the other side of the changeover switch i have run a 16 mm wire which is connected to wire feeding the house in the meter box using a ferrule and heat shrink.

    For my application as an electrician i know what to switch on and off as i have a current clamp and have replaced my element in my geyser for example to a 1kw element.

    I would recommend a 5.5 kva generator or bigger to customers, but with this comes a few challenges.

    My question to you all fellas...

    1/ Would you recommend this setup to your customers, considering they dont have a current clamp?

    2/ How do you overcome the problem of supplying 20- 25 amps (5.5 kva generator) via a 16 amp sockets outlet?

    3/ Would you use a circuit breaker next to the generator to protect the cable or rely on the generator overload protection?
    Comments are based on opinion...not always facts....that's why people use an alias.
  • Justloadit
    Diamond Member

    • Nov 2010
    • 3518

    #2
    I think that the generator may not supply the current you think it can. Note that a grid has a low impedance and is able to supply the current demand, as per a generator, which has a high impedance, and would overload the motor any way to the point that it would probably choke and stop. All the generators that I have seen have a circuit breaker.

    With respect to the 16A plug, the generator will probably struggle to supply that , with the CEE plugs are under rated anyway, so the few extra amps wont do any heating of the plug. Bear in mind, that the generator would probably never run at full power for long periods of time anyway. Maybe include a moving iron amp meter which is relative inexpensive as a gauge for the customer.
    Victor - Knowledge is a blessing or a curse, your current circumstances make you decide!
    Solar pumping, Solar Geyser & Solar Security lighting solutions - www.microsolve.co.za

    Comment

    • AndyD
      Diamond Member

      • Jan 2010
      • 4946

      #3
      I would personally never recommend a generator for a domestic customer, by the time you work out the capital outlay, the installation, the fuel cost, the fuel storage, the servicing etc the real cost per kWh is absolutely extortionate and the smaller generators are often completely not suitable for connection to a DB plus unless it's a high-end unit the frequency and the voltage instabilities cause havoc with electronics etc.
      _______________________________________________

      _______________________________________________

      Comment

      • Justloadit
        Diamond Member

        • Nov 2010
        • 3518

        #4
        Hi Andy,

        I agree with you on your statement as far as a large generator is concerned however, what we are doing here in Jhb, is installing a 5.5KVA genny, with a manual change over switch, connected to the DB board, BUT, we isolate a number of circuits only which are connected to the generator. Usually lights, fridge circuit and entertainment circuit.

        Basically during a black out, the user starts the genny via a key switch on the genny, as most 5.5Kva have an electric start, once running, they change the switch manually to genny, have power during the black out, and when the power returns, they simply change over back to mains, switch the genny off and wait for the next one.

        This makes it safe for any one to use, and due to the simplicity can even be done by the home manager if required during the day.
        Victor - Knowledge is a blessing or a curse, your current circumstances make you decide!
        Solar pumping, Solar Geyser & Solar Security lighting solutions - www.microsolve.co.za

        Comment

        • wynn
          Diamond Member

          • Oct 2006
          • 3338

          #5
          When the power goes off I know to switch the 'Genny' on because there is no power, but how do I know the power is back on if my 'Genny' is running?
          "Nobody who has succeeded has not failed along the way"
          Arianna Huffington

          Read the first 10% of my books "Didymus" and "The BEAST of BIKO BRIDGE" for free
          You can also read and download 100% free my short stories "A Real Surprise" and "Pieces of Eight" at
          http://www.smashwords.com/books/view/332256

          Comment

          • ACEsterhuizen
            Bronze Member

            • Mar 2012
            • 165

            #6
            You can wire the change over switch with a pilot light and a pulse once (or more) alarm or a manual alarm cancel switch so you will know when eskom power is back on, or, as described above, if you only wire certain circuits through the change over switch, the other circuit will obviously become "live" once eskom is back on, eg you leave the some light on which is NOT wired to the Gennie and that light will remain off as long as eskom is off and will come on once eskom is on.

            Just remember to have the install done by a registered electrician (ask for proof and follow up and get a coc for the job) The Neutral Bar must be split according to the regs i have seen many installs where the neutral bar was not split. (except if it a 3 phase install at the mains)

            7.12.3.1.4 Where only part of an installation is switched to the alternative
            supply in the same distribution board, the neutral bar shall be split (see
            figures S.2 and S.3 in annex S).
            Last edited by ACEsterhuizen; 22-Jan-15, 12:36 PM. Reason: more info

            Comment

            • AndyD
              Diamond Member

              • Jan 2010
              • 4946

              #7
              The problem with a lot of the small generators is the the neutral is at an equal voltage as the live with respect to earth so they're configured 115(L)-0(Earth)-115(Neutral) L-N is 230v. You cannot connect this type of genny to a DB, it's designed for use with trailing leads only. Also genny's are notoriously poor at producing sufficient current in the case of a fault and don't achieve required disconnection times of circuit breakers or other OCPD's.
              _______________________________________________

              _______________________________________________

              Comment

              • Houses4Rent
                Gold Member

                • Mar 2014
                • 803

                #8
                I am thinking of a far simpler set up. I really only need power during load shedding and other outages for my PC, printer, router, screen etc. so I can continue working. Is it feasible if I buy a small genny (what size would I need?) and when the power went I just start up the genny and use an extension to plug my PC gear straight into the genny.

                What are the pros and cons/risks?
                Houses4Rent
                "We treat your investment as we treat our own"
                marc@houses4rent.co.za www.houses4rent.co.za
                083-3115551
                Global Residential Property Investor / Specialized Letting Agent & Property Manager

                Comment

                • wynn
                  Diamond Member

                  • Oct 2006
                  • 3338

                  #9
                  On 'The Other' Forum it was discussed that you would set up a series of batteries (Deep Cell) in a cage outside your office (say under the roof eaves) and run an inverter through them to your necessary equipment (PC, screen, printer, router, remote phone and emergency lights) so they would all work during a 'Load Shit' and as soon as power came back on it would recharge the batteries for the next 'Dump', like a giant UPS.
                  "Nobody who has succeeded has not failed along the way"
                  Arianna Huffington

                  Read the first 10% of my books "Didymus" and "The BEAST of BIKO BRIDGE" for free
                  You can also read and download 100% free my short stories "A Real Surprise" and "Pieces of Eight" at
                  http://www.smashwords.com/books/view/332256

                  Comment

                  • Dave A
                    Site Caretaker

                    • May 2006
                    • 22807

                    #10
                    Originally posted by ians
                    2/ How do you overcome the problem of supplying 20- 25 amps (5.5 kva generator) via a 16 amp sockets outlet?
                    Typically those generators have two socket outlets. If you expect to push past 15A, perhaps use both outlets in parallel?

                    Originally posted by Justloadit
                    I think that the generator may not supply the current you think it can. Note that a grid has a low impedance and is able to supply the current demand, as per a generator, which has a high impedance, and would overload the motor any way to the point that it would probably choke and stop. All the generators that I have seen have a circuit breaker.
                    Definitely go with voltage regulated generators. This solves lots of problems.

                    Originally posted by AndyD
                    The problem with a lot of the small generators is the neutral is at an equal voltage as the live with respect to earth so they're configured 115(L)-0(Earth)-115(Neutral) L-N is 230v.
                    Is the earth tapped in the middle like that, or is it just that without an anchor the live and neutral float off the "ambient" earth voltage in equal measure?

                    My experience so far is if you bridge the earth and neutral at the generator, the neutral stays at 0V and live goes to 220V relative to earth, which solves the problem. Of course, make sure your earthing system is appropriate (have an earth spike).
                    Participation is voluntary.

                    Alcocks Electrical Services | Alcocks Pest Control & Entomological Services | Alcocks Hygiene Services

                    Comment

                    • IanF
                      Moderator

                      • Dec 2007
                      • 2680

                      #11
                      Originally posted by Houses4Rent
                      I am thinking of a far simpler set up. I really only need power during load shedding and other outages for my PC, printer, router, screen etc. so I can continue working. Is it feasible if I buy a small genny (what size would I need?) and when the power went I just start up the genny and use an extension to plug my PC gear straight into the genny.

                      What are the pros and cons/risks?
                      That's what I do. Then when the power comes back the lights come on.
                      Only stress when you can change the outcome!

                      Comment

                      • KCS
                        Full Member
                        • Sep 2014
                        • 25

                        #12
                        We have kept it simple, as we don't need to power the whole house during the outages. My big concern was charging my laptop, phones, security and the fridge. The rest we can do without, and we use battery LED lights. Also have gas for cooking (braai!)

                        In view of this I bought a 3,5 kva generator which I installed with a nice thick lead to a multiplug, located near the fridge. During outages I just plug in the fridge, and switch off the fridge when we need to boil the kettle or charge any of the devices. The generator has a decent earth into the ground, as well as AVR (I assume this means Automatic Voltage Regulator?) as well as an overload cut-off.

                        This kept it really simple and the cost very low. Also, I never plug the computer straight into the generator power supply, only use it to charge, so I assume that the charger will take the brunt should there be a spike in current?

                        The question marks above are assumptions, I am not an electrician. Would welcome comments.

                        Cheers

                        KC
                        www.EvansCoolantsGauteng.co.za
                        www.ClassicCarHire.co.za

                        Comment

                        • ians
                          Diamond Member

                          • Apr 2010
                          • 3943

                          #13
                          Originally posted by AndyD
                          The problem with a lot of the small generators is the the neutral is at an equal voltage as the live with respect to earth so they're configured 115(L)-0(Earth)-115(Neutral) L-N is 230v. You cannot connect this type of genny to a DB, it's designed for use with trailing leads only. Also genny's are notoriously poor at producing sufficient current in the case of a fault and don't achieve required disconnection times of circuit breakers or other OCPD's.
                          Andy why did you have to go spoil it and bring that up. That is why you have to plug it in so that it doesnt become part of the electrical installation. We discussed this issue during the last load shedding episode. Just imagine trying to stop all these generators being connected, there are thousands of them connected to DB's. The worst i have seen to date are the suicide cords, with the plug on both ends of the cable.
                          Comments are based on opinion...not always facts....that's why people use an alias.

                          Comment

                          • AndyD
                            Diamond Member

                            • Jan 2010
                            • 4946

                            #14
                            Eek, 'plugging it in' would not be a wise move.

                            Originally posted by Dave A
                            Is the earth tapped in the middle like that, or is it just that without an anchor the live and neutral float off the "ambient" earth voltage in equal measure?

                            My experience so far is if you bridge the earth and neutral at the generator, the neutral stays at 0V and live goes to 220V relative to earth, which solves the problem. Of course, make sure your earthing system is appropriate (have an earth spike).
                            In some smaller site type generators the centre of the windings is actually tapped and bonded to the chassis as an earth which ties both L and N at 110v wrt earth, they're not floating. The problem is when the centre tapped earth is bonded internally to the generator chassis. If you bridge a centre tapped earth and neutral you're effectively shorting out half of the winding which would cause a fault condition and probably damage to the windings. This is what would happen with a cowboy connection into a DB.

                            These generators are designed to be used with extension leads only.
                            _______________________________________________

                            _______________________________________________

                            Comment

                            • Houses4Rent
                              Gold Member

                              • Mar 2014
                              • 803

                              #15
                              Hm, can you sparky's please tell me and KCS how to set up a very simple thing like a generator powering a few things of choice via an extension lead?

                              I won't need a fridge/freezer as it can survive 2.5h load shedding. I really only need to power my PC (desktop), router, printer and scanner without risking frying any of them due to problems induced by the generator (Voltage & Amp variations). I can charge my cell via USB from the PC
                              Houses4Rent
                              "We treat your investment as we treat our own"
                              marc@houses4rent.co.za www.houses4rent.co.za
                              083-3115551
                              Global Residential Property Investor / Specialized Letting Agent & Property Manager

                              Comment

                              Working...