    Old circuit breakers

    Can anybody advise me whether 30 year old circuit breakers are ok for a COC

  2. #2
    Platinum Member
    Join Date
    Jun 2017
    Location
    Port Elizabeth
    Posts
    1,264
    Thanks
    34
    Thanked 306 Times in 260 Posts
    If the C/breakers are still in a workable condition and no visible damage and comply to the code, I see no reason to scrap them
    With that said and not knowing the size of DB, supply and fault level you are referring to , double check and do not assume that they are working

    We have come across old C/breakers in boards that when you switch to the off position , don't actually switch off all the phases so you need to check.
    Also some spring type charged CB don't always operate correctly when switched off an on again and sometimes need to be serviced.

    The amp rating and KA rating must be visible on the CB


    6.6.1.3 Each item of electrical equipment used in a distribution board shall
    comply with the requirements of clause 4.


    4.2 Notices, labels and rating plates
    Any notices, labels or rating plates that are required in terms of this part of
    SANS 10142 shall be durable and not removable except by determined and
    deliberate action. The inscriptions shall be legible and indelible. Details on the
    topics given in column 2 of table 4.2 can be found in the relevant subclauses
    in column 1 and the warning labels shall comply with SANS 1186-1.

  3. #3
    New Member
    Join Date
    Jan 2022
    Location
    Sandton
    Posts
    3
    Thanks
    0
    Thanked 0 Times in 0 Posts
    Many thanks with my problem ,you saved me some money . Thanks Again

Similar Threads

  1. Check them cheap circuit breakers.
    By Derlyn in forum Electrical Contracting Industry Forum
    Replies: 5
    Last Post: 12-Feb-21, 03:37 PM
  2. Miniature circuit breakers
    By LukasF in forum Electrical Contracting Industry Forum
    Replies: 1
    Last Post: 04-May-18, 12:46 PM
  3. [Question] Do circuit breakers need to be SABS APPROVED
    By Gilberto Silva in forum Electrical Contracting Industry Forum
    Replies: 27
    Last Post: 28-Jul-16, 02:19 PM
  4. [Question] Installation of circuit breakers
    By Harry S in forum Electrical Contracting Industry Forum
    Replies: 5
    Last Post: 30-Jan-16, 07:12 AM
  5. Circuit breakers
    By adrianh in forum Electrical Contracting Industry Forum
    Replies: 3
    Last Post: 25-May-10, 12:37 AM

Did you like this article? Share it with your favourite social network.

Did you like this article? Share it with your favourite social network.

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •