    There is a reason why there are are different curve breakers, to compensate for inrush current caused by motor staring or things like magnetic tables.

    There is no reason a 25 amp breaker should be used in place of a 20 amp, I have noticed aircon people use 25 amp breakers, because like the solar installers they dont have an electrical background and the 1 week electrical training does'nt teach them the difference between a restive load and inductive load.

    From my experience it looks like electricians are not taught much about electricity either, if you really want to see how bad it has got, go do a refresher course...... eeeeish.
    Comments are my opinion, unless regulations are attached to support the comment. This is social media, not a court room.

  2. #22
    Platinum Member
    Join Date
    Jun 2017
    Location
    Port Elizabeth
    Posts
    1,293
    Thanks
    36
    Thanked 314 Times in 263 Posts
    Quote Originally Posted by Sparks View Post
    Regarding the 25-20A breakers, some aircons require more than 20A to start whereafter their consumption drops. The motivation of providing 16A socket outlets is ridiculous. 4x6A loads is 24A, well within the capabillity of a 2.5mm cable. .
    It was not motivation that I was providing - It is the regulations and cannot be changed because you feel differently - If a 25Amp CB is on a socket circuit you cannot sign the COC - Clause 6.15.3 is pretty clear

Page 3 of 3 FirstFirst 123

Similar Threads

  1. Solar backup system challenges
    By Isetech in forum Electrical Contracting Industry Forum
    Replies: 1
    Last Post: 27-Mar-24, 09:48 AM
  2. Solar challenges
    By Isetech in forum Electrical Contracting Industry Forum
    Replies: 0
    Last Post: 21-Jul-23, 08:26 AM
  3. Solar install challenges
    By Isetech in forum Electrical Contracting Industry Forum
    Replies: 1
    Last Post: 11-May-23, 03:00 AM
  4. Backup/solar challenges
    By Isetech in forum Electrical Contracting Industry Forum
    Replies: 0
    Last Post: 16-Feb-23, 10:14 AM
  5. Solar/inverter/batteries installation challenges
    By Isetech in forum Electrical Contracting Industry Forum
    Replies: 7
    Last Post: 01-Dec-22, 03:53 PM

Did you like this article? Share it with your favourite social network.

Did you like this article? Share it with your favourite social network.

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •