    Just something regarding cabtyre flex.

    In previous editions of SANS 10142, the use of flexible cords in an installation was illegal as per the wording of 6.1.11. which stated that "flexible cords shall not be used as part of the electrical installation"

    However

    In the new SANS 10142 -1 Edition 3.1 the wording has been changed. It now reads "Where flexible cords are used as part of the electrical installation, the selection, installation and colour identification shall be done in accordance with this part of SANS 10142"

    So according to the above, cabtyre flex is now permitted as long as the colour coding is adhered to and according to 6.1.12, bootlace crimping ferrules must be used to prevent strands of the conductor being cut off in terminations.

    Just a bit of clarity regarding the regs and the use of cabtyre flex.
    Hope this helps.

  2. Thanks given for this post:

    Howler (04-Jul-23)

  3. #2
    Junior Member Howler's Avatar
    Join Date
    Jun 2023
    Location
    Centurion
    Posts
    19
    Thanks
    12
    Thanked 1 Time in 1 Post
    As you can see from the photo, bootlace crimp ferrules was not used.

  4. #3
    Platinum Member Derlyn's Avatar
    Join Date
    Mar 2019
    Location
    East london
    Posts
    1,578
    Thanks
    111
    Thanked 150 Times in 142 Posts
    Quote Originally Posted by Howler View Post
    As you can see from the photo, bootlace crimp ferrules was not used.
    Correct. Also, most cabtyre has a blue conductor for neutral. This must be changed to black, using either tape or heatshrink. Neutral wires MUST be black.

    GCE covered most of your query, but I just thought I'd mention the cabtyre issue as a large proportion of electricians think it's illegal to use on an installation, but according to the latest regs, not so.

    Seems as if you got a raw deal.
    Some people have no scruples.

  5. Thanks given for this post:

    Howler (04-Jul-23)

  6. #4
    Junior Member Howler's Avatar
    Join Date
    Jun 2023
    Location
    Centurion
    Posts
    19
    Thanks
    12
    Thanked 1 Time in 1 Post
    Quote Originally Posted by Derlyn View Post
    Correct. Also, most cabtyre has a blue conductor for neutral. This must be changed to black, using either tape or heatshrink. Neutral wires MUST be black.

    GCE covered most of your query, but I just thought I'd mention the cabtyre issue as a large proportion of electricians think it's illegal to use on an installation, but according to the latest regs, not so.

    Seems as if you got a raw deal.
    Some people have no scruples.
    So just to verify

    the exposed ends of the neutral that is exposed from the white casing, needs to be marked black (heatshrink or tape) at both ends of the cabtyre?

  7. #5
    Platinum Member Derlyn's Avatar
    Join Date
    Mar 2019
    Location
    East london
    Posts
    1,578
    Thanks
    111
    Thanked 150 Times in 142 Posts
    Quote Originally Posted by Howler View Post
    So just to verify

    the exposed ends of the neutral that is exposed from the white casing, needs to be marked black (heatshrink or tape) at both ends of the cabtyre?
    Yes.

    Reg 6.3.3.2 (1) A neutral conductor shall be identified by black only.

  8. #6
    Platinum Member
    Join Date
    Jun 2017
    Location
    Port Elizabeth
    Posts
    1,302
    Thanks
    36
    Thanked 314 Times in 263 Posts
    Quote Originally Posted by Derlyn View Post
    Just something regarding cabtyre flex.

    In previous editions of SANS 10142, the use of flexible cords in an installation was illegal as per the wording of 6.1.11. which stated that "flexible cords shall not be used as part of the electrical installation"

    However

    In the new SANS 10142 -1 Edition 3.1 the wording has been changed. It now reads "Where flexible cords are used as part of the electrical installation, the selection, installation and colour identification shall be done in accordance with this part of SANS 10142"

    So according to the above, cabtyre flex is now permitted as long as the colour coding is adhered to and according to 6.1.12, bootlace crimping ferrules must be used to prevent strands of the conductor being cut off in terminations.

    Just a bit of clarity regarding the regs and the use of cabtyre flex.
    Hope this helps.
    There is twin flex used - which is a definite no - Also no cabtyre under 1sqmm

    6.1.11 Where flexible cords are used as part of the electrical installation, the
    selection, installation and colour identification (see 6.3.3) shall be done in
    accordance with this part of SANS 10142. Flexible cords with cross sectional
    area less than 1 mm2 shall not be permitted.
    6.1.12 Where flexible cords are used, the strands of the conductors shall be
    mechanically protected with ferrules to prevent the strands from being cut off
    in terminations.

Similar Threads

  1. [Question] Complicated electrical wiring question/issues
    By BeInControl in forum Electrical Contracting Industry Forum
    Replies: 8
    Last Post: 04-Nov-18, 11:32 AM
  2. Single phase generator feeding 1 phase of 3 phase db - discuss.
    By skatingsparks in forum Electrical Contracting Industry Forum
    Replies: 6
    Last Post: 03-Jul-18, 10:06 AM
  3. [Opinion] 3 phase electrical distribution board wiring
    By Stephenvr in forum Electrical Contracting Industry Forum
    Replies: 9
    Last Post: 26-Nov-17, 07:02 PM
  4. [Question] Home Automation & Electrical CoC for Single Phase house
    By repix in forum Electrical Contracting Industry Forum
    Replies: 1
    Last Post: 09-Apr-17, 11:49 AM
  5. Three phase to single phase generator advice needed
    By joshthejew in forum Electrical Contracting Industry Forum
    Replies: 3
    Last Post: 08-Apr-15, 10:12 PM

Tags for this Thread

Did you like this article? Share it with your favourite social network.

Did you like this article? Share it with your favourite social network.

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •