Page 1 of 2 12 LastLast
Results 1 to 10 of 15

Thread: Circiut Breakers

  1. #1
    Gold Member Martinco's Avatar
    Join Date
    Oct 2008
    Location
    Rustenburg
    Posts
    927
    Thanks
    175
    Thanked 136 Times in 108 Posts

    Circiut Breakers

    Just a question.....................say a circuit breaker at the main DB is rated at 20 amp and a circuit breaker at the sub DB 50 meters away is also 20 amp and of the same make and type. These breakers only supply one appliance and no other apparatus. In the case of an overload, which breaker will trip first ?
    Further, is there any significance in a breaker with an orange lever ?
    Last edited by Martinco; 30-Mar-11 at 09:16 AM.
    Martin Coetzee
    Supplier of Stainless Steel Band and Buckle and various fastening systems. Steel, Plastic, Galvanized, PET and Poly woven.
    We solve your fastening problems.
    www.straptite.com

    You may never know what results will come from your actions, but if you do nothing, there will be no results... Rudy Malan 05/03/2011

  2. #2
    Diamond Member Justloadit's Avatar
    Join Date
    Nov 2010
    Location
    Johannesburg
    Posts
    3,495
    Thanks
    138
    Thanked 695 Times in 593 Posts
    Blog Entries
    1
    Theoretically they will both trip on the overload.

    The orange lever basically tells you that the circuit breaker is not electro magnetic, but thermal overload. These breakers are usually used in circuits on which motors are connected, so that they do not trip when the motor is started.

    Some of our learned friends on the forum will give a more detailed explanation.
    Victor - Knowledge is a blessing or a curse, your current circumstances make you decide!
    Solar pumping, Solar Geyser & Solar Security lighting solutions - www.microsolve.co.za

  3. #3
    Diamond Member AndyD's Avatar
    Join Date
    Jan 2010
    Location
    Cape Town
    Posts
    4,927
    Thanks
    577
    Thanked 936 Times in 757 Posts
    In reality it would be a lottery which one trips first, it would depend very much on exactly what type of fault occurred and how big the fault was. If it was a short circuit at the appliance then in theory the breaker closest to the fault should trip faster because under those conditions the resistance cabling acts as a load. That doesn't mean however that both breakers wouldn't trip.
    _______________________________________________

    _______________________________________________

  4. #4
    Gold Member Martinco's Avatar
    Join Date
    Oct 2008
    Location
    Rustenburg
    Posts
    927
    Thanks
    175
    Thanked 136 Times in 108 Posts
    Lets say the fault is simply an overload.
    Martin Coetzee
    Supplier of Stainless Steel Band and Buckle and various fastening systems. Steel, Plastic, Galvanized, PET and Poly woven.
    We solve your fastening problems.
    www.straptite.com

    You may never know what results will come from your actions, but if you do nothing, there will be no results... Rudy Malan 05/03/2011

  5. #5
    Suspended
    Join Date
    Oct 2007
    Posts
    2,346
    Thanks
    0
    Thanked 254 Times in 209 Posts
    orange breaker has a slower trip curve 1 and a standard white lever is curve 2...the orange one would have a variety of uses one being to accomadate the start of lets say an aircon compressor...pool pump etc.

    what i have experienced recently...is they cannot operate correctly with invertor aircons...the aircons cause them to buzz...the suppliers response was thet there is a spring around the coil which is making the noise...

    my question would why would you want to install 20 amp circuit breakers in line with each other...thats like putting 2 e/l unit in line.

  6. #6
    Diamond Member AndyD's Avatar
    Join Date
    Jan 2010
    Location
    Cape Town
    Posts
    4,927
    Thanks
    577
    Thanked 936 Times in 757 Posts
    If it was a marginal overload the white lever breaker would trip before the orange lever breaker depending where the overload is on their curve of operation. I don't have data sheets immediately available but from memory there's a point where the two tripping curves meet. If the value of your overload coincided with this value on the curves then we're back to the lottery principal again.
    _______________________________________________

    _______________________________________________

  7. #7
    Gold Member Martinco's Avatar
    Join Date
    Oct 2008
    Location
    Rustenburg
    Posts
    927
    Thanks
    175
    Thanked 136 Times in 108 Posts
    No, just a hypothetical question to set some brains in motion.

    So what I can figure out from above answers is that if you have an orange CB at the main DB and a white CB at the sub and you have a motor at the end drawing close to 20 Amp for a short amount of time then the white one will trip first ? But if the motor draws 20 amp for a long time then it is a toss up as to which breaker will fall first. Right ?
    Martin Coetzee
    Supplier of Stainless Steel Band and Buckle and various fastening systems. Steel, Plastic, Galvanized, PET and Poly woven.
    We solve your fastening problems.
    www.straptite.com

    You may never know what results will come from your actions, but if you do nothing, there will be no results... Rudy Malan 05/03/2011

  8. #8
    Diamond Member AndyD's Avatar
    Join Date
    Jan 2010
    Location
    Cape Town
    Posts
    4,927
    Thanks
    577
    Thanked 936 Times in 757 Posts
    I apologize in advance if this is long winded and over simplified but I thought it might be helpful for the non-electrical people. Also this info was taught to me during my apprenticeship and refers to the old way that things were done before complex electronics were thrown into the mix.

    Breakers (MCB's) have two distinct tripping functions. High fault currents cause tripping by magnetism which happens very quickly, marginal overloads cause tripping by thermal action which happens much slower or delayed so it's effectively a two-function device.

    As a rule of thumb;
    A ‘C-curve’ breaker (white lever) has an instantaneous trip if the current through it is in excess of five times the rated current (In).
    A ‘D-curve’ breaker (orange lever) has an instantaneous trip if the current through it is in excess of ten times the rated current (In).

    So if you effectively have both types of breakers (C+D curve) rated at 20A protecting a circuit and a fault occurs causing over 200A to flow then both should trip instantaneously. The instantaneous tripping is performed internally in the MCB by magnetic action.

    The thermal tripping function of the breakers occurs when the overload is marginal (< 5x In for C-curve and < 10x In for D-curve). This marginal overload current causes heating of a small thermal element which operates a bimetallic latch causing the trip. Playing around with the performance of the heater and the composition and construction of the bimetallic strip causes different tripping characteristics for current against a time scale. They take a breaker and plot a graph or the tripping times for different currents and the resulting line on the graph is the tripping curve of that particular breaker.

    Below is a typical graph with the curve for a C-curve and a D-curve breaker. If you follow across from the point where the two curves meet it indicates the current would be approx 1.2 times the current rating of the breaker. So if you had a 20A C-curve and a 20A D-curve MCB protecting the same circuit and the current in the circuit was 24 Amps then in theory both breakers would trip at the same time.

    Please note all figures and curves shown are fictional and were drawn free-hand, they should not be used to make any real life calculations. The manufacturers of any MCB should be able to supply similar graphs on request.

    Click image for larger version. 

Name:	Breakers.jpg 
Views:	4129 
Size:	39.7 KB 
ID:	1928
    _______________________________________________

    _______________________________________________

  9. Thank given for this post:

    Justloadit (31-Mar-11), Martinco (31-Mar-11), mikilianis (30-Mar-11)

  10. #9
    Diamond Member Justloadit's Avatar
    Join Date
    Nov 2010
    Location
    Johannesburg
    Posts
    3,495
    Thanks
    138
    Thanked 695 Times in 593 Posts
    Blog Entries
    1
    Hi Andy,

    A very well thought out explanation, had forgotten some of the characteristics of the D-Curve CB, and even of the C-Curve
    Victor - Knowledge is a blessing or a curse, your current circumstances make you decide!
    Solar pumping, Solar Geyser & Solar Security lighting solutions - www.microsolve.co.za

  11. #10
    Suspended
    Join Date
    Oct 2007
    Posts
    2,346
    Thanks
    0
    Thanked 254 Times in 209 Posts
    just be careful because if you start looking on an orange CBI circuit breakers chances are you not gona find "D" curve anywhere...they are refered to as curve 2 "C2" (motor starter type breakers or eqipment with inrush currents)

    circuit breakers like M&G are refered to as "D" curve (motor starting breakers or equipment with inrush currents) and all the ones i have installed have always been black.

Page 1 of 2 12 LastLast

Tags for this Thread

Did you like this article? Share it with your favourite social network.

Did you like this article? Share it with your favourite social network.

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •