    I have a situation were i plug-tested the Earth Leakage (E/L), and it didnt trip, so i bought and installed a new cbi EL, plug tested and still not tripping.
    I ran a continuity test between Earth-Bar in DB and earth studs at sockets, also continuity between EL-Neutral-Bar and Neutral studs on sockets, and everything else is wired correctly and as it should be.
    I even touched neutral to earth, and even plugged in 2 plug-testers both at max settings, and EL is still not tripping.
    i installed the first EL into another DB, of site, and it does trip at 25mA
    What do i not know, or not taking into consideration.
    Any help would be greatly appreciated

  2. #2
    Platinum Member
    Join Date
    Jun 2017
    Location
    Port Elizabeth
    Posts
    1,287
    Thanks
    34
    Thanked 310 Times in 261 Posts
    Have you done an earth loop impedance test - Almost sounds like there is no earth coming into the property or the earth neutral strap is missing in the sub station .
    Try bridging earth and neutral before the earth leakage and see what happens and then test.
    What voltages are you getting between L- N and L-E and N-E

  3. Thanks given for this post:

    Fredre (09-Jun-20)

  4. #3
    New Member
    Join Date
    Dec 2015
    Location
    Cape town
    Posts
    8
    Thanks
    1
    Thanked 1 Time in 1 Post
    Thank you Sir, respect.

  5. Thanks given for this post:

    ACEsterhuizen (09-Jun-20)

  6. #4
    Platinum Member Derlyn's Avatar
    Join Date
    Mar 2019
    Location
    East london
    Posts
    1,547
    Thanks
    108
    Thanked 146 Times in 139 Posts
    Quote Originally Posted by Fredre View Post
    Good day everybody, Please help me with my question.
    I have a situation were i plug-tested the Earth Leakage (E/L), and it didnt trip, so i bought and installed a new cbi EL, plug tested and still not tripping.
    I ran a continuity test between Earth-Bar in DB and earth studs at sockets, also continuity between EL-Neutral-Bar and Neutral studs on sockets, and everything else is wired correctly and as it should be.
    I even touched neutral to earth, and even plugged in 2 plug-testers both at max settings, and EL is still not tripping.
    i installed the first EL into another DB, of site, and it does trip at 25mA
    What do i not know, or not taking into consideration.
    Any help would be greatly appreciated
    Hello brother

    Another thing to keep in mind is the supply voltage.

    If you are using a TEL1TLB socket tester by HellermannTyton then there is no guarantee that this particular tester will trip the earth leakage relay even if same is in perfect working order if the voltage is below 219V.

    When upping the voltage to 220V or above it works perfectly.

    I have checked this with multiple plug testers and earth leakages in the past and it is indeed so.

    Handy to keep this in mind.

    It will be interesting to get some feedback as to what the problem was.

    Cheers ... Derek

  7. #5
    Diamond Member AndyD's Avatar
    Join Date
    Jan 2010
    Location
    Cape Town
    Posts
    4,925
    Thanks
    576
    Thanked 934 Times in 755 Posts
    Does the earth leakage trip if you press the test button on the front of it?
    _______________________________________________

    _______________________________________________

  8. #6
    New Member
    Join Date
    Dec 2015
    Location
    Cape town
    Posts
    8
    Thanks
    1
    Thanked 1 Time in 1 Post
    Thanks to everybody that helped.
    The problem was that there was no Earth to the property, the Earth spike has been installed, but earth wire to db broke.
    Scary part is, I dont know how long this problem existed for, when did their earth cable break, the fact that their E/L wasnt able to trip, with 2 small children in the house. !!!
    Just glad i could help them and sort it out, with your help.

Similar Threads

  1. Earth Leakage Breaker (RCD) Tripping
    By AndyD in forum Electrical Contracting Industry Forum
    Replies: 33
    Last Post: 14-Jul-23, 02:53 PM
  2. Ceiling fan tripping earth leakage.
    By Derlyn in forum Electrical Contracting Industry Forum
    Replies: 12
    Last Post: 04-Feb-21, 09:04 AM
  3. earth leakage tripping issue
    By ians in forum Electrical Contracting Industry Forum
    Replies: 8
    Last Post: 16-Jan-19, 12:13 PM
  4. Earth leakage tripping when plug in snake rack
    By MattyN in forum Electrical Contracting Industry Forum
    Replies: 7
    Last Post: 22-Aug-15, 09:29 AM
  5. earth leakage tripping
    By ians in forum Electrical Contracting Industry Forum
    Replies: 12
    Last Post: 23-Jun-15, 11:27 AM

Did you like this article? Share it with your favourite social network.

Did you like this article? Share it with your favourite social network.

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •