    Yesterday the street muni transformer blew (IMHO due to no oil change in 8 years and very hot weather) leaving us with no grid electricity. So after a 6 hours I decided to start the three phase generator (with each phase servicing a specific single phase section of the house) to get the fridge and freezer cold again. The fridge (which is a brand new Bosch KGN36XI32 with power demand of 160W) simply refused to start up on the generator supply. That I could understand as the wave form on the phase is a bit dirty.

    So I switched the fridge supply to the standby 400W Victron sine wave inverter with a 2,5mm2 lead. Now the fridge's internal light came on, the touch control panel worked but the compressor did not start. At full load demand the fridge should start up ... not the case. So I pulled a spare 1,5kW Meanwell sine wave inverter out. Now the fridge's internal light works, but the touch control panel only randomly and the compressor refused to start.

    OK, my logical deduction is the fridge went with the transformer to electrical heaven. A nice way to start Christmas.

    After 12,5 hours a new transformer was installed and grid supply was reinstated. Let me try again I told the Boss, and she just laughed.

    Low and behold, plug Mrs Fridge in and there she starts up and purrs away ....

    Can anyone shed some light on the reason why the grid supply works, but two pure sine inverters do not?

  2. #2
    Diamond Member AndyD's Avatar
    Join Date
    Jan 2010
    Location
    Cape Town
    Posts
    4,932
    Thanks
    578
    Thanked 936 Times in 757 Posts
    Modern day appliances can be very complex devices with internal communications between different control boards and even between control boards and components and sensors. Sometimes the comms systems require a very low neutral earth voltage. The only thing I can think of is maybe a lack of N-E bond caused problems with the comms.
    _______________________________________________

    _______________________________________________

  3. #3
    Full Member
    Join Date
    Sep 2015
    Location
    Port Elizabeth
    Posts
    76
    Thanks
    6
    Thanked 3 Times in 3 Posts
    Thanks for the reply. That is one thing I have not thought of. Will measure and see if this is the issue!

  4. #4
    Full Member
    Join Date
    Sep 2015
    Location
    Port Elizabeth
    Posts
    76
    Thanks
    6
    Thanked 3 Times in 3 Posts
    You are spot on. The inverter(s) are V-0-V and there is a 70+V on N-E which the fridge does not like and will refuse to start. I did not realise the inverters were V-0-V so I now have a few decisions to make as I cannot connect these into my household circuits.

  5. #5
    Diamond Member Justloadit's Avatar
    Join Date
    Nov 2010
    Location
    Johannesburg
    Posts
    3,497
    Thanks
    138
    Thanked 696 Times in 594 Posts
    Blog Entries
    1
    Get a 600VA 1:1 ratio isolating transformer, primary side to the inverter and secondary side to the fridge. This will isolate the V-0-V issue.
    Victor - Knowledge is a blessing or a curse, your current circumstances make you decide!
    Solar pumping, Solar Geyser & Solar Security lighting solutions - www.microsolve.co.za

  6. #6
    Full Member
    Join Date
    Sep 2015
    Location
    Port Elizabeth
    Posts
    76
    Thanks
    6
    Thanked 3 Times in 3 Posts
    It pays to buy quality inverters. Feedback from Meanwell is that it will auto sense V-0-0 downstream of the outlet and adjust the inverter's output to V-0-0. I will try this tomorrow in a controlled way.

  7. #7
    Diamond Member AndyD's Avatar
    Join Date
    Jan 2010
    Location
    Cape Town
    Posts
    4,932
    Thanks
    578
    Thanked 936 Times in 757 Posts
    Glad you're on the right track. If it's any consolation I like all the Meanwell devices I've come across, their power supplies and drivers are well designed, nicely manufactured, functional and they're reliable. I haven't worked with their inverters yet but hopefully they're equally good.
    _______________________________________________

    _______________________________________________

  8. #8
    Full Member
    Join Date
    Sep 2015
    Location
    Port Elizabeth
    Posts
    76
    Thanks
    6
    Thanked 3 Times in 3 Posts
    So our local Muni transformer blew up again and we were without grid power for a long time. I took the opportunity to get the fridge going on an inverter, but alas no go.

    This is what I did. I made sure the supply by the inverter to the fridge is V-0-0 and it only runs from a battery that is charged and coupled to another battery charger supplying a charge current at the same time.

    I took readings of the voltage between pins and these were L-N = 230V; N-E = 0V; L-E = 230V.

    As said before the inverter is a pure sine wave 1500W output with spiking loads up to 125% the 1,5kW for 10 sec. This is much more than the fridge will require.

    When connected and switched on, the fridge never tried to start. It just sat there doing nothing except shining the control panel lights.

    When the grid came on, plug the fridge into the wall outlet and off she goes, purring like a kitten.

    So the only thing left in my opinion is that the sine wave from the pure sine wave inverter is not to the liking of the fridge's controller.

    Any ideas???

  9. #9
    Diamond Member
    Join Date
    Apr 2010
    Location
    planet earth
    Posts
    3,943
    Thanks
    153
    Thanked 317 Times in 287 Posts
    Try connecting other appliances to the inverter...kettle...drill etc and see what happens.

  10. #10
    Full Member
    Join Date
    Sep 2015
    Location
    Port Elizabeth
    Posts
    76
    Thanks
    6
    Thanked 3 Times in 3 Posts
    Quote Originally Posted by ians View Post
    Try connecting other appliances to the inverter...kettle...drill etc and see what happens.
    And we have a winner ...

    Now why would this make a difference as the inverter is not in sleep mode?

Similar Threads

  1. Portable fridge/freezer wanted
    By Neville Bailey in forum General Chat Forum
    Replies: 4
    Last Post: 12-Dec-16, 06:06 AM
  2. Domestic Fridge Energy Consumption.
    By AndyD in forum Electrical Contracting Industry Forum
    Replies: 13
    Last Post: 27-Jan-16, 09:26 PM
  3. Invertors
    By ians in forum Electrical Contracting Industry Forum
    Replies: 8
    Last Post: 20-Apr-15, 12:36 PM
  4. Windows 8 - Combining a toaster with a fridge
    By AndyD in forum Technology Forum
    Replies: 19
    Last Post: 15-May-13, 08:42 AM
  5. light fittings in a fridge
    By ians in forum Electrical Contracting Industry Forum
    Replies: 10
    Last Post: 14-Dec-12, 10:22 AM

Did you like this article? Share it with your favourite social network.

Did you like this article? Share it with your favourite social network.

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •