Results 1 to 8 of 8

Thread: What can bypass earth leakage and is it safe?

  1. #1
    New Member
    Join Date
    Jul 2016
    Location
    Randburg
    Posts
    8
    Thanks
    1
    Thanked 0 Times in 0 Posts

    What can bypass earth leakage and is it safe?

    Electricians rewired the full db board. Never heard it before but the circuit was broken into 2 sections, plugs after the earth leakage ;and stove, aircons, lights, geyser after only the local switch(ie no earth leakage). Is this standard practice and does it not put my family life in danger. The argument is earth leakage can't handle the load, items that operate with gas, water etc, ie aircons and stove must not go on earth leakage. And lights not on earth leakage in case it trips so that there is still lights. This is all new to me and I'm concerned that it's not correct.
    Thanks

  2. #2
    Diamond Member AndyD's Avatar
    Join Date
    Jan 2010
    Location
    Cape Town
    Posts
    4,924
    Thanks
    576
    Thanked 934 Times in 755 Posts
    The current electrical regs require that all socket outlets are supplied via the earth leakage, lighting circuits and certain other circuits can be optional so it's possible that what you were told is correct. My personal preference would be a split DB with 2x earth leakages, one for socket outlets and the other for stove, geyser etc or even using RCBO's but there are cost implications.
    _______________________________________________

    _______________________________________________

  3. #3
    Site Caretaker Dave A's Avatar
    Join Date
    May 2006
    Location
    Durban, South Africa
    Posts
    22,665
    Thanks
    3,309
    Thanked 2,676 Times in 2,258 Posts
    Blog Entries
    12
    Gilberto, what you describe is compliant with SANS 10124-1 edition 1.8 which is applicable today. Flicking through the Edition 2.0 draft however, I note that changes may be coming; the draft has geysers requiring earth leakage protection.

    I had to say reading it, my first thought was Andy's point not that long ago that RCBO's probably are the way to go.

  4. #4
    Gold Member Sparks's Avatar
    Join Date
    Dec 2009
    Location
    Port Elizabeth
    Posts
    898
    Thanks
    21
    Thanked 127 Times in 96 Posts
    Something I noticed too is that the aircon is not through the ELCB. That is incorrect. All electric motors, pumps, fans and aircons must also ghave ELCB protection. If the geyser is installed inside the bathroom it must also be supplied by the ELCB.

    The claim that the ELCB cannot handle the load is bull. They are usually 60Amps which is almost if not the same as the main switch.
    Last edited by Sparks; 16-Jul-16 at 09:18 AM. Reason: Addition.

  5. #5
    New Member
    Join Date
    Jul 2016
    Location
    Randburg
    Posts
    8
    Thanks
    1
    Thanked 0 Times in 0 Posts
    Thank you very much gentlemen. Part of me makes me feel more comfortable with what was done. Now I just need to worry about the upcoming geyser change, the potential that the aircon is not behind a ELCB. I'll be looking further into this.

  6. #6
    Site Caretaker Dave A's Avatar
    Join Date
    May 2006
    Location
    Durban, South Africa
    Posts
    22,665
    Thanks
    3,309
    Thanked 2,676 Times in 2,258 Posts
    Blog Entries
    12
    Quote Originally Posted by Sparks View Post
    Something I noticed too is that the aircon is not through the ELCB. That is incorrect. All electric motors, pumps, fans and aircons must also ghave ELCB protection.
    In terms of which part of the current code, Sparks?

    Yes, there are some specific circumstances, but as I recall saying "all" is going a bridge too far.

  7. Thanks given for this post:

    mikilianis (16-Jul-16)

  8. #7
    Email problem
    Join Date
    Sep 2010
    Location
    cape town
    Posts
    308
    Thanks
    3
    Thanked 43 Times in 37 Posts
    hi sparks. why should an aircon be on earth leakage relay if its supplied by an isolator not a socket outlet? also other pumps and motors that are not for pools,jacuzzis etc do not have to be on earth leakage relay if supplied by an isolator. (fixed appliances)

  9. #8
    New Member
    Join Date
    Feb 2017
    Location
    Joburg
    Posts
    1
    Thanks
    0
    Thanked 0 Times in 0 Posts
    Lights need to be after earth leakage if you have ceiling fans. And most houses have ceiling fans.

    Also, having lights connected after earth leakage will probably give you a smaller shock when changing a light bulb than if the 10Amp circuit breaker had to trip?

    Would you prefer the earth leakage to stop you from being shocked or the stove's 40Amp circuit breaker?

    There's a sticker on my Defy stove/oven saying "This appliance does not need to be connected through the earth leakage system(SABS code 0142). Nuisance tripping will occur in damp conditions if connected to the earth leakage unit as the cumulative leakage current of all of the oven and other appliance elements may exceed the trip value."

    I would guess that placing sensitive electronics (printed circuit boards etc) after the earth leakage might help protect with lightning, like a stove/oven digital clock, aircon electronics, remote controlled ceiling fan? If the lightning causes the earth leakage to trip before a larger current reaches the appliance?

Similar Threads

  1. Does a stove need to be on an earth leakage?
    By Leecatt in forum Electrical Contracting Industry Forum
    Replies: 63
    Last Post: 23-Jan-18, 08:26 AM
  2. Earth Leakage
    By Gtfast in forum Electrical Contracting Industry Forum
    Replies: 2
    Last Post: 10-May-16, 10:11 PM
  3. Earth leakage
    By Electrix in forum Electrical Contracting Industry Forum
    Replies: 1
    Last Post: 24-Feb-16, 09:10 PM
  4. [Question] Inverter's and earth leakage
    By padayad28 in forum Electrical Contracting Industry Forum
    Replies: 4
    Last Post: 11-Jul-15, 09:08 AM
  5. Earth Leakage
    By Pieter00 in forum Electrical Contracting Industry Forum
    Replies: 13
    Last Post: 27-May-13, 12:03 PM

Tags for this Thread

Did you like this article? Share it with your favourite social network.

Did you like this article? Share it with your favourite social network.

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •