Thread: Mixed circuits

Hybrid View

Previous Post Previous Post   Next Post Next Post
  1. #1
    Platinum Member
    Join Date
    Jun 2017
    Location
    Port Elizabeth
    Posts
    1,287
    Thanks
    36
    Thanked 310 Times in 261 Posts
    Can a Sub DB ... a plug circuit ... a light circuit ... an isolator feeding a fixed appliance ... all be fed from a single breaker ... labelled "mixed circuit"
    Not a sub DB - specifically states sockets , Luminaries and fixed appliances ( 6.15.4.2) - The C/breaker cannot be rated at more than 20 Amps
    The 20 Amp stipulation would exclude stoves - Aircons rated above 16Amp ( 6.16.4.1.1) need to be on dedicated circuit

    Lets say we have an aircon on a isolator ... a couple of socket outlets and a couple of lights connected directly to a day/night switch ... all fed from a 20 amp MCB using 2,5 mm wire ... labelled "mixed circuit" ?
    You would need to take into account 6.15.4.2 note 1 and note 2 - Needs to be carefully considered

    I would use a mixed load circuit for a swimming pool if getting access to the DB was a problem . The " pool DB" is actually a motor control center for the fixed appliance , being the pool.The minute I feed lights ( I would put the pool light as part of the pool) or plugs from the pool DB then it is no longer a motor control center but automatically becomes a sub DB and can no longer be on the circuit.

    I would mix load to a gate motor and lights at the boundary wall.

    Would use it for a garage that is stand alone and used for parking a car and using a socket for the vacuum cleaner. If the garage is going to be a laundry or workshop , then I would think twice.

    Would use for a braai Lapa set up in the middle of the garden .

    Personally think they are valid uses for mix loading but would not use it for general use and not trying to cut prices .The note about taking into account diversity and nuisance tripping are going to come back to haunt.

  2. Thanks given for this post:

    Justloadit (13-Oct-21)

  3. #2
    Platinum Member
    Join Date
    Jun 2017
    Location
    Port Elizabeth
    Posts
    1,287
    Thanks
    36
    Thanked 310 Times in 261 Posts
    Further to above
    Definitely not allowed on mixed circuits would be

    6.16.2.2 Dedicated circuits shall be provided for water heaters and there may
    be more than one water heater on each circuit.

    6.16.3.2.1 A dedicated circuit(s) shall be provided for cooking appliance(s)
    that are rated at more than 16 A.

    6.16.4.1.1 Dedicated circuits shall be provided for fixed space heating and
    cooling (air-conditioning units) that are rated at more than 16 A. There may be
    more than one unit on each circuit and the power supply to each unit shall be
    controlled by a switch-disconnector.

  4. Thank given for this post:

    Dave A (17-Oct-21)

Similar Threads

  1. 5A Unswitched Circuits
    By Jaboel in forum Electrical Contracting Industry Forum
    Replies: 2
    Last Post: 05-Aug-21, 04:28 PM
  2. Mixed circuit for outdoor requirements
    By saguy in forum Electrical Contracting Industry Forum
    Replies: 1
    Last Post: 08-Oct-20, 01:16 PM
  3. [Question] ELV Ring Circuits
    By Tang in forum Electrical Contracting Industry Forum
    Replies: 2
    Last Post: 24-Aug-19, 09:26 AM
  4. [Question] Geyser and plug on mixed circuit
    By FRENCHIE in forum Electrical Contracting Industry Forum
    Replies: 1
    Last Post: 17-Aug-19, 07:33 AM
  5. Underfloor heating circuits
    By kosmonooit in forum Electrical Contracting Industry Forum
    Replies: 11
    Last Post: 26-Oct-16, 02:52 PM

Did you like this article? Share it with your favourite social network.

Did you like this article? Share it with your favourite social network.

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •