    Combining 2 incoming municipal electrical supplies

    Hi Guys,

    I've an interesting problem.
    I've got an potential client. It is a commercial property that used to be two separate businesses each with a separate 60 Amp single phase electricity municipal electricity supplies to the same building. The one company has gone bust while the other one has grown. The remaining company's electricity demand has grown to the point where 60 Amp is not enough.

    Is it possible to combine the two incoming 220v single phase supplies into one to supply peak loads. The 2 main dbs are relatively close to each other so adding cabling to combine will be easy and relatively cheap.

    The Company does not mind getting two electricity bills.

    Any recommendations will be appreciated.

    Regards

  2. #2
    Platinum Member
    Join Date
    Jun 2017
    Location
    Port Elizabeth
    Posts
    1,271
    Thanks
    34
    Thanked 308 Times in 260 Posts
    Hi
    Generally the municipality does not allow 2 supplies to one Erf and it seems unusual that they would have put 2 phases to a single Erf

    Often you have 3 phases to an erf and 3 single phase meters, metering the supply if it is under 100 Amps, generally 80 Amps.

    If it is one Erf and only supplied with 2 phases from the municipality then I see no problem combining the supplies but not from different DB boards.
    The 2 phase supply would need to originate together from the main DB for a number of reasons but mainly to be able to isolate the DB in the case of emergency.

    If it is across 2 erven then , No

    You would need to check Municipal bylaws but something does not sound right with the arrangement you mentioned above.

  3. #3
    Diamond Member
    Join Date
    Apr 2010
    Location
    planet earth
    Posts
    3,943
    Thanks
    153
    Thanked 317 Times in 287 Posts
    Quote Originally Posted by GCE View Post
    Hi
    Generally the municipality does not allow 2 supplies to one Erf and it seems unusual that they would have put 2 phases to a single Erf

    Often you have 3 phases to an erf and 3 single phase meters, metering the supply if it is under 100 Amps, generally 80 Amps.

    If it is one Erf and only supplied with 2 phases from the municipality then I see no problem combining the supplies but not from different DB boards.
    The 2 phase supply would need to originate together from the main DB for a number of reasons but mainly to be able to isolate the DB in the case of emergency.

    If it is across 2 erven then , No

    You would need to check Municipal bylaws but something does not sound right with the arrangement you mentioned above.
    In the past you could have 2 supplies ...I have sites in Durban which have 2 municipal prepaid meters on 1 domestic property... 1 prepaid to the house and 1 to the outbuilding... around 2008 i applied for additional 6 more properties to be converted to be converted...i got a letter from the electricity department informing me that they no longer allow 2 municipal prepaid meters ...unless the property was sub divided or sectional title... so we did just that and installed 5 prepaid meters on one site.
    Comments are based on opinion...not always facts....that's why people use an alias.

Similar Threads

  1. Incoming Supply and Prepaid metering.
    By Henthel in forum Electrical Contracting Industry Forum
    Replies: 7
    Last Post: 20-Mar-19, 10:57 PM
  2. No incoming earth again (and again, and again and again )
    By skatingsparks in forum Electrical Contracting Industry Forum
    Replies: 4
    Last Post: 14-Nov-18, 09:05 AM
  3. Incoming supply
    By Leonsparky in forum Electrical Contracting Industry Forum
    Replies: 3
    Last Post: 10-Aug-16, 10:42 PM
  4. Windows 8 - Combining a toaster with a fridge
    By AndyD in forum Technology Forum
    Replies: 19
    Last Post: 15-May-13, 08:42 AM
  5. [Question] COMBINING DATABASE TABLES
    By jonesey in forum Technology Forum
    Replies: 5
    Last Post: 05-Sep-12, 01:08 PM

Tags for this Thread

Did you like this article? Share it with your favourite social network.

Did you like this article? Share it with your favourite social network.

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •