    Good afternoon all

    What does the SANS regulation states relating to using a bigger size breaker compared to a smaller size cable.

    Thus, can you use a 25mm cable and connect it to a 250A Schneider CB, with a Micrologic trip unit, that can be turned down to protect the cable?

  2. #2
    Platinum Member
    Join Date
    Jun 2017
    Location
    Port Elizabeth
    Posts
    1,287
    Thanks
    34
    Thanked 310 Times in 261 Posts
    Hi

    There was a previous thread on basically the same question - have pasted the reg that I thought cleared me and the thread link further down

    5.4.3 Current
    The equipment shall be suitable for operation at the maximum steady
    (r.m.s.) current to which it is likely to be subjected. It shall also be able to
    carry the current that is likely to flow under abnormal conditions and for the
    period that the current is likely to flow.
    NOTE The period that an abnormal current will flow is equal to the operating time of
    any protective device

    6.7.2.4 Protective devices that have adjustable overload settings shall only
    be used if the means of adjustment is not accessible without the use of a
    tool and the adjustment can only be made by means of a tool.


    https://www.theforumsa.co.za/forums/...able-C-Breaker

  3. Thanks given for this post:

    Dave A (16-Aug-19)

Similar Threads

  1. Miniature circuit breakers
    By LukasF in forum Electrical Contracting Industry Forum
    Replies: 1
    Last Post: 04-May-18, 12:46 PM
  2. [Question] Do circuit breakers need to be SABS APPROVED
    By Gilberto Silva in forum Electrical Contracting Industry Forum
    Replies: 27
    Last Post: 28-Jul-16, 02:19 PM
  3. [Question] Installation of circuit breakers
    By Harry S in forum Electrical Contracting Industry Forum
    Replies: 5
    Last Post: 30-Jan-16, 07:12 AM
  4. [Question] Flash Barrier Protection on Circuit Breakers
    By BlueArc in forum Electrical Contracting Industry Forum
    Replies: 4
    Last Post: 16-Sep-15, 11:15 AM
  5. Circuit breakers
    By adrianh in forum Electrical Contracting Industry Forum
    Replies: 3
    Last Post: 25-May-10, 12:37 AM

Tags for this Thread

Did you like this article? Share it with your favourite social network.

Did you like this article? Share it with your favourite social network.

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •