    I need to know if Twin & Earth premanufactured wiring can be installed on an outside surface without any protection such as in the image. Kindly refer me to the relevant sections and/or paragraphs.

    Click image for larger version. 

Name:	shutterboard.jpg 
Views:	859 
Size:	64.5 KB 
ID:	6729

  2. #2
    Full Member
    Join Date
    Sep 2015
    Location
    port elizabeth
    Posts
    26
    Thanks
    0
    Thanked 1 Time in 1 Post
    6.3.6 PVC insulated multicore cables with a bare earthing conductor and round cable with metal stiffening 6.3.6.1 The cables may be installed a) on the surface, b) under plaster, c) under a raised floor, d) in hollows (such as in walls and partitions) (no additional protection being needed), e) in roof spaces, f) direct in the ground (see 6.4.4.2, unarmoured buried cables), g) outdoors or exposed to water (but unless the manufacturer proves that the cables can withstand ultraviolet radiation, the cable shall be out of sight of the sky), and h) under screed if protected by an earth leakage protection device with a rated earth leakage tripping current (rated residual current) IΔn not exceeding 30 mA. 6.3.6.2 These cables shall not be buried direct in concrete.

  3. #3
    Full Member
    Join Date
    Sep 2015
    Location
    Port Elizabeth
    Posts
    76
    Thanks
    6
    Thanked 3 Times in 3 Posts
    I know the paragraph but I was taught T&E in covered locations and Surfix on unprotected locations. The paragraph 6.3.6 makes no distinction ....

    Interestingly, manufacturer specs read: "The cable shall not be buried direct in concrete or in screed."

  4. #4
    Full Member
    Join Date
    Sep 2015
    Location
    port elizabeth
    Posts
    26
    Thanks
    0
    Thanked 1 Time in 1 Post
    The heading states 6.3.6 PVC insulated multicolor cable with a bare earthing conductor (T&E) 'AND' round cable with metal stiffening (Surfix).

  5. #5
    Full Member
    Join Date
    Sep 2015
    Location
    port elizabeth
    Posts
    26
    Thanks
    0
    Thanked 1 Time in 1 Post
    sorry i meant multicore

  6. #6
    Full Member
    Join Date
    Sep 2015
    Location
    Port Elizabeth
    Posts
    76
    Thanks
    6
    Thanked 3 Times in 3 Posts
    Quote Originally Posted by Eskom View Post
    multicolor
    Thanks, you made my day!

  7. #7
    Gold Member Sparks's Avatar
    Join Date
    Dec 2009
    Location
    Port Elizabeth
    Posts
    901
    Thanks
    21
    Thanked 127 Times in 96 Posts
    Aberdare will confirm that T&E does not have UV protection but Surfix does.

  8. Thanks given for this post:

    mygoggie (12-Apr-17)

  9. #8
    Diamond Member AndyD's Avatar
    Join Date
    Jan 2010
    Location
    Cape Town
    Posts
    4,924
    Thanks
    576
    Thanked 934 Times in 755 Posts
    Quote Originally Posted by mygoggie View Post
    .....Interestingly, manufacturer specs read: "The cable shall not be buried direct in concrete or in screed."
    If the manufacturters spec says it can't be installed buried direct in concrete or screed then this would mean that conduit must be used even if the electrical regs say it's fine not to.
    _______________________________________________

    _______________________________________________

  10. #9
    Full Member
    Join Date
    Sep 2015
    Location
    Port Elizabeth
    Posts
    76
    Thanks
    6
    Thanked 3 Times in 3 Posts
    Quote Originally Posted by AndyD View Post
    If the manufacturters spec says it can't be installed buried direct in concrete or screed then this would mean that conduit must be used even if the electrical regs say it's fine not to.
    Yep, agree 100%

Similar Threads

  1. Hobby wiring: Wiring requirements for a DCC railway layout
    By icrob in forum Electrical Contracting Industry Forum
    Replies: 1
    Last Post: 23-Jul-16, 05:29 PM
  2. wiring an inverter to DB
    By cje in forum Electrical Contracting Industry Forum
    Replies: 1
    Last Post: 11-Jul-15, 09:09 AM
  3. Vacancy: External Sales Rep - Flexographic printing Industy
    By HR Solutions in forum Local Ads on TFSA
    Replies: 0
    Last Post: 09-Oct-13, 01:57 PM
  4. Replies: 0
    Last Post: 09-Jul-12, 11:11 AM
  5. [Question] Western Digital 2.5'' 1TB USB2 External Drive
    By AmithS in forum Technology Forum
    Replies: 10
    Last Post: 17-Apr-11, 09:35 PM

Did you like this article? Share it with your favourite social network.

Did you like this article? Share it with your favourite social network.

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •