Page 2 of 2 FirstFirst 12
Results 11 to 15 of 15

Thread: 220 V LED downlighters glowing when switched off

  1. #11
    Full Member
    Join Date
    Jul 2015
    Location
    Cape town
    Posts
    46
    Thanks
    18
    Thanked 5 Times in 5 Posts
    Quote Originally Posted by ians View Post
    We have also been encountering a similar problem...LED downlight flickers when switched off...on 3 occasions we found it to be the same make (Ellies) ...replaced the lamp with a different brand...problem solved.
    I have had this issue with the new osram LED downlight gu10s , the older ones never gave me this issue. Usually I install a bleed resistor in one of the OBO round pvc boxes with a few air holes in Lid, connected in parallel to the load of course

  2. #12
    Diamond Member AndyD's Avatar
    Join Date
    Jan 2010
    Location
    Cape Town
    Posts
    4,924
    Thanks
    576
    Thanked 934 Times in 755 Posts
    Here's one that should put the cat amongst the pigeons. Not for the faint hearted but you could also replace the standard light switch with a 2-way switch wired with the light on common, the live on one side and an earth on the other. When the switch is in one position (ON) it connects the light to the live supply, in the other position (OFF) it connects the light to the earth which sinks any stray voltages and stops the flickering problem. Can't be done if the light circuit is on earth leakage though...

    I'd be interested to know if you can find a regulation to forbid it, it's certainly guaranteed to confuse the hell out of DIY'ers and half awake sparkies alike so some documentation or at least a circuit sketch tucked into the switch for the poor soul who has to work on it next time. You'd also need documentation in the main DB to explian the insulation test results for that particular circuit.....not that anyone seems to be doing IR test any more
    _______________________________________________

    _______________________________________________

  3. Thanks given for this post:

    hartdev@hotmail.com (06-Sep-17)

  4. #13
    Full Member
    Join Date
    Jul 2015
    Location
    Cape town
    Posts
    46
    Thanks
    18
    Thanked 5 Times in 5 Posts
    That's a much better way. Why didn't i think of that.
    Definetly best if you can get a neutral down to the switch.
    The first time i worked on s3000 switches i noticed the leds connected to earth but was ok as the light circuits were not on earth leakage.
    Could make some nice led indicated s2000 switches with your idea!

  5. #14
    Platinum Member
    Join Date
    Jun 2017
    Location
    Port Elizabeth
    Posts
    1,266
    Thanks
    34
    Thanked 308 Times in 260 Posts
    Hi Andy

    Have to strongly disagree with your method - You would effectively be earthing the neutral which is not allowed under
    6.1.6 – pg 83 – Neutral shall not be connected direct to earth on the load side of point of control.ED 1.8

    It will also create a fire risk if for some reason you lose your incoming neutral from the street , The complete installation will be using the neutral/ earth , Star point as reference - The amperage could increase drastically on your pieces of 1,5sqmm wiring. Even worse if the complete street tries to earth through your star point

  6. #15
    Diamond Member AndyD's Avatar
    Join Date
    Jan 2010
    Location
    Cape Town
    Posts
    4,924
    Thanks
    576
    Thanked 934 Times in 755 Posts
    The method I outlined was kinda tongue in cheek, hence the emojis and suggestion it would put the cat amongst the pigeons. It wouldn't connect the neutral direct to earth as per the reg 6.1.6, the load of the lighting circuit would be between the neutral and earth so it would be a high resistance connection, not a direct one.

    Neutral faults on the supply side are always problematic with TN C S supplies hence they're more often than not PME'd to prevent elevated earth voltages. If a neutral fault occurs on a TN C S installation there's always a good chance the neutral current is going to find its way down some arbitary parallel path and cause an overload/fire hazard, I don't think this circuit wiring would increase the chance of this happening as such.
    _______________________________________________

    _______________________________________________

Page 2 of 2 FirstFirst 12

Similar Threads

  1. switched socket outlets or not!
    By joshthejew in forum Electrical Contracting Industry Forum
    Replies: 3
    Last Post: 18-Aug-16, 11:16 PM
  2. [Question] 12V Downlighters
    By cknipe in forum Electrical Contracting Industry Forum
    Replies: 33
    Last Post: 20-Apr-15, 12:29 PM
  3. [Question] Downlighters
    By CollenD in forum Electrical Contracting Industry Forum
    Replies: 7
    Last Post: 03-Feb-13, 09:28 AM
  4. downlighters
    By murdock in forum Electrical Contracting Industry Forum
    Replies: 3
    Last Post: 25-Mar-10, 08:00 AM

Did you like this article? Share it with your favourite social network.

Did you like this article? Share it with your favourite social network.

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •