    No earth wire!

    We're finding a lot of this - no earth wire!
    Mostly in light circuits, but every now and then...

    Click image for larger version. 

Name:	DSCN0008.jpg 
Views:	888 
Size:	44.9 KB 
ID:	5859

    Who needs an earth wire to a socket outlet?

    Or even the geyser (as long as it's bonded to something, right?)

    Click image for larger version. 

Name:	DSCN0019.jpg 
Views:	770 
Size:	52.2 KB 
ID:	5860

    Just an earth line between the geyser earth point and the water pipes - I kid you not.

    Pretty tempted to hunt down whoever issued the COC for the original installation on this one.

  2. #2
    Diamond Member AndyD's Avatar
    Join Date
    Jan 2010
    Location
    Cape Town
    Posts
    4,924
    Thanks
    576
    Thanked 934 Times in 755 Posts
    The socket looks like DIY, either that or a complete tosser. They've used a surface mount backbox in a flush mounted installation and it looks like they might have used singles house-wire buried straight in the plaster. Also there's no screws holding the backbox in place, they must have just plastered around it and the cable entry hole looks like it was made with a kitchen knife or something similar.

    The geyser also looks like housewire buried in the plaster and no sign whatsoever of an earth wire in the supply and is that a tape joint shortly after it comes out of the wall? Isolator....nahhh why bother. Geyser tray as per regs......nahhh also obviously not necessary. That bonding wire ring terminal looks like it was fitted with a hammer and chisel which in itself is no mean feat with a 4mm lug.

    Okay, enough commentary, now lets get down to the serious business of the scoring.

    Category 1, Aesthetics.
    The missing isolator and earth wiring give the installation a minimalist feel which is very fashionable at present. Look I'll grant you he's no Frank Stella or Yves Klein but the clean lines and lack of clutter by leaving the earth out of that socket is giving the nod toward the cubist movement and their complete rejection of inherited rules and values so, for a delicate combination of art, philosophy and electrical installation I'm giving him a 9 in this category.

    Category 2, Danger.
    Housewire buried in shallow plaster, complete lack of CPC's...not just unconnected....completely not there at all, tape joint and no isolator are all elements of a complete symphony that gets the heart racing and really delivers from beginning to end. From a danger point of view this little offering packs a punches way above its weight and leaves you begging for more so it's an 8 from me.

    Category 3, Overall Message.
    Overall the set up shows a strong and unyielding middle finger to all things health and safety. Whilst the highly visible dangling earth wire was a nice touch and the in line tape joint is always a crowd-pleaser I'd have preferred that some of the other little gems were generally more visible to casual observers without the 'use of a tool'. The fact that they're all concealed in a backbox or above a bulkhead ceiling in this particular case kinda dilutes the H&S 'fuck-you' somewhat; hence the less than perfect score in this category. Only a 7 from me I'm afraid.

    Conclusions.
    Overall score of 8/10 is very respectable, great effort and not without style and a certain bravado. Definitely an installer to look out for in future as I can only see great things coming from here on in.
    _______________________________________________

    _______________________________________________

  3. #3
    Diamond Member tec0's Avatar
    Join Date
    Jun 2009
    Location
    South Africa
    Posts
    4,624
    Thanks
    1,884
    Thanked 463 Times in 410 Posts
    Blog Entries
    3
    that is nothing.... LOL

    I wish i had a camera back in the day... in my days as contractor i saw a electrician using a hammer drill hammered a cavity placed the wire "normal electrical wire that you will find on a toaster" into the cavity running from the ground the roof. Now i don't know how it was connected up there but i recall he just plastered over the electrical wire.
    peace is a state of mind
    Disclaimer: everything written by me can be considered as fictional.

  4. #4
    Full Member
    Join Date
    Jul 2015
    Location
    Jouburg
    Posts
    40
    Thanks
    0
    Thanked 3 Times in 3 Posts
    At a site I was doing LED conversions at (and had to crawl in the ceiling) I found that some random Air Con installers had connected their power cable to a random Plug circuits and diverted the ECC there, so the Earth did not go to the plugs! Generally wiring in ceilings is such a mess, security and CCTV installers add to the havoc - bad practices, no training, no supervision, ...?

    In terms of lights, fittings do not need to be earthed if they meet certain conditions, one being out of arms reach from the floor,

  5. #5
    Diamond Member AndyD's Avatar
    Join Date
    Jan 2010
    Location
    Cape Town
    Posts
    4,924
    Thanks
    576
    Thanked 934 Times in 755 Posts
    Quote Originally Posted by kosmonooit View Post
    ........In terms of lights, fittings do not need to be earthed if they meet certain conditions, one being out of arms reach from the floor,
    Can you give the appropriate regulation to back that up please?
    _______________________________________________

    _______________________________________________

  6. #6
    Full Member
    Join Date
    Jul 2015
    Location
    Jouburg
    Posts
    40
    Thanks
    0
    Thanked 3 Times in 3 Posts
    Quote Originally Posted by AndyD View Post
    Can you give the appropriate regulation to back that up please?
    SANS 10142

    6.12.3.2 The following conductive parts do not need to be earthed:

    b) exposed conductive parts of fixed electrical equipment that are
    1) out of arm's reach from the floor (or walking) level,
    2) out of arm's reach from a structure that is bonded to earth, and
    3) not exposed to the weather or to the condensation, dripping,
    splashing or accumulation of water, and
    4) not touching a conductive surface;

    and/or

    6.14.4 Lamp holders
    6.14.4.1 A lamp holder shall be shrouded in insulating material or shall
    be earthed, unless it is simultaneously
    a) out of arm's reach from the floor or walkway level,
    b) out of arm's reach from a structure that is bonded to earth,
    c) protected from the weather and the splashing, dripping, or accumulation
    of water, and
    d) not touching a conductive surface.

  7. #7
    Diamond Member AndyD's Avatar
    Join Date
    Jan 2010
    Location
    Cape Town
    Posts
    4,924
    Thanks
    576
    Thanked 934 Times in 755 Posts
    Would you call this a lamp holder; Click image for larger version. 

Name:	images.jpeg 
Views:	348 
Size:	2.5 KB 
ID:	5870 or this? Name:  images2.jpeg
Views: 3305
Size:  6.0 KB
    _______________________________________________

    _______________________________________________

  8. #8
    Full Member
    Join Date
    Jul 2015
    Location
    Jouburg
    Posts
    40
    Thanks
    0
    Thanked 3 Times in 3 Posts
    Its a luminary and if its out of arms reach from the floor & structure bonded to earth, protected from weather / splashing etc and not touching a conductive surface it does not need to be earthed.

  9. #9
    Email problem
    Join Date
    Sep 2010
    Location
    cape town
    Posts
    308
    Thanks
    3
    Thanked 43 Times in 37 Posts
    out of arms reach from your scaffolding or steel ladder. lol
    that rule should have been taken out long ago. i fail everything not earthed properly regardless of what the book says.

  10. #10
    Email problem
    Join Date
    Sep 2010
    Location
    cape town
    Posts
    308
    Thanks
    3
    Thanked 43 Times in 37 Posts
    category 4: speed of installation

    save on labour costs 9/10

Page 1 of 3 123 LastLast

Similar Threads

  1. Earth Spike.
    By IMHO in forum Electrical Contracting Industry Forum
    Replies: 10
    Last Post: 29-Nov-13, 11:06 PM
  2. Is it common to find too-thin wire in an installation?
    By berndj in forum Electrical Contracting Industry Forum
    Replies: 43
    Last Post: 10-Aug-10, 07:44 AM
  3. US bank wants my "clearing code" for wire transfer
    By leuce2 in forum Business Finance Forum
    Replies: 4
    Last Post: 08-May-10, 12:18 PM
  4. Google Earth
    By Faan in forum General Business Forum
    Replies: 0
    Last Post: 30-Jul-08, 08:52 PM

Did you like this article? Share it with your favourite social network.

Did you like this article? Share it with your favourite social network.

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •