    Another interesting issue I have experienced in the last couple of weeks, connecting gas stoves and induction plates.

    What's the big deal, just connect to the under counter oven or just join the wires behind the stove, nobody will see it, but can you that's the question.

    If you install a gas hob and under counter oven is it safe to cut off the plug top and connect the cabtyre directly to the terminals where the 4mm or 6 mm stove wires are connected and is a certified gas installer allowed to connect the wire once he cuts off the plug or connect the cabtyre directly to the 4/6mm wire be it in a junction box or not?

    I was put in a situation where we removed the hob and replaced it with 2 x induction plates, but there were no plug sockets to connect the plates, so I mounted a double socket outlet, connect the hob cable (4mm twin + e) into the socket outlet and fitted a 20 amp circuit breaker into the 4x4 extension box, cut a small slot so that just the breaker switch protrudes from the box. Trying to get a feed from another socket outlet to the hob location would have involved chasing walls in the dinning room and patching with the risk of damaging tiles in the R120 000 kitchen, which I wasn't prepared to take.

  2. #2
    New Member
    Join Date
    Aug 2012
    Location
    Cape Town
    Posts
    4
    Thanks
    0
    Thanked 3 Times in 3 Posts
    Hi ians

    I have experienced a similar issue in the past and I ended up buying SANS 10087 (gas installation regulations) I have no idea why it is not part of SANS 10142
    Basically it states that no electrical connection shall be made directly under the hob, including a socket outlet. The hob connection shall be made off into an isolator mounted at least 200mm away from the hob above the counter, or in an adjoining cupboard not directly below the hob.

    The plug with a separate 20A breaker isn't a bad idea provided the stove was connected through earth leakage, otherwise a dedicated plug could be used, provided it was in an adjoining cupboard.
    You could connect the cabtyre directly to the stove supply provided that the size of conductor in the cabtyre was at least equal to the ka rating of the mcb feeding the stove even if the amp rating exceeded what the cabtyre could handle.
    I believe that a stove and hob setup where the hob is basically a separate appliance, then two separate isolators should be installed. Often not very easy with modern kitchen designs, especially ovens in kitchen islands.

    This is my first post btw.
    Regards
    Ryan Taylor, electrician, CT

  3. Thanks given for this post:

    mikilianis (03-Sep-13)

  4. #3
    Diamond Member AndyD's Avatar
    Join Date
    Jan 2010
    Location
    Cape Town
    Posts
    4,926
    Thanks
    576
    Thanked 935 Times in 756 Posts
    Quote Originally Posted by RTsparky View Post
    Hi ians

    I have experienced a similar issue in the past and I ended up buying SANS 10087 (gas installation regulations) I have no idea why it is not part of SANS 10142
    I can kinda understand why it's not part of the electrical standards. Ian, if you'd like a copy of 10087 then Christmas has come early.

    If you follow the parent directories links you'll find standards and codes for various countries in their respective ibr/ directories if you're interested.
    _______________________________________________

    _______________________________________________

  5. Thanks given for this post:

    mikilianis (03-Sep-13)

  6. #4
    Diamond Member AndyD's Avatar
    Join Date
    Jan 2010
    Location
    Cape Town
    Posts
    4,926
    Thanks
    576
    Thanked 935 Times in 756 Posts
    Lol, the more I trawl through that site the more I couldn't help laughing. I just learned that Swaziland has its own national standards authority called the SZNS but from what I can see their standards bear more than a passing resembelence to the SANS equivalents. Just for a laugh here's the Swazi standard for fixed electric water heaters.....see, every day's a school day, I just learned something else.... they must have electricity in Swaziland.
    _______________________________________________

    _______________________________________________

  7. #5
    Diamond Member
    Join Date
    Apr 2010
    Location
    planet earth
    Posts
    3,943
    Thanks
    153
    Thanked 317 Times in 287 Posts
    Lucky the plug I installed wasn't under a hob, we removed the hob, had a stainless steel frame made to fit the 2 induction plates which come standard with 15 amp moulded plug (seen more fires and burnt wires from these plugs than any other) and the isolator is still connected on the wall so you can switch off the plug socket with the isolator so you don't have to go into the cupboard.

    By the way this is Africa, anything goes, sans regs are just for those who are not up to speed with red robots, driving in the orange line, etc, so I am sure my home made circuit breaker box thingy ma bob will work fine , or like the response I got from the technical advisor at the ECA "what's all the fuss about is just a 6mm wire connected to a 16mm wire in a box which is not weatherproof being cast in a concrete deck with a 60 amp breaker protecting the cable"

  8. #6
    Junior Member
    Join Date
    Dec 2011
    Location
    Bloemfontein
    Posts
    23
    Thanks
    3
    Thanked 1 Time in 1 Post
    Could somebody please explain to a noob like me the connection of an electric oven when it states on the back that it needs to be earthed but not be fed through the earth leakage breaker.

    So if there is a leakage in the oven, the earth leakage will trip but not shut off the oven? So the earthing offers no protection then correct?

    Thank you

  9. #7
    Diamond Member
    Join Date
    Apr 2010
    Location
    planet earth
    Posts
    3,943
    Thanks
    153
    Thanked 317 Times in 287 Posts
    In simple terms, in an electric installations you get an earth then everything else, what a lot of people including electricians don't always understand is unless you earthing is correctly selected and installed, you could end up with a dangerous installation. A very simple and common one I can refer to is people complain about getting shocked when they touch the washing machine or dishwasher, it could simply be that the earth is not connected, which could be very dangerous if you are standing bare foot touching the appliance.

    This is a trick question, your stove doesn't have to be connected to an earth leakage unit and as you enquired on another thread nor do light circuits under certain conditions. Generally you only have to connect plugs via an earth leakage unit. Making statements like I just have could get me into trouble, because it is not as simple as it sounds, there is a SANS book which has all the details which an electrician uses as guidelines to make the right choice.

    I have tried to answer your question without going confusing you or going into too much detail, Andy is a lot better at responding to questions.

  10. #8
    Gold Member Sparks's Avatar
    Join Date
    Dec 2009
    Location
    Port Elizabeth
    Posts
    902
    Thanks
    21
    Thanked 127 Times in 96 Posts
    I reckon that explanation is good enough Ian, the earthing must be done thoroughly and correctly and ELCB protection is not required, but as you pointed out about the lighting circuits it is not as simple as it sounds. I will mention this here as this is where this thread started. A socket outlet is only allowed on a cooker circuit provided it is enclosed in the same enclosure as the cooker isolator and has it's own separate protection. Because of the socket outlet this circuit must have ELCB protection. (also mentioned in a nutshell)

  11. #9
    Bronze Member
    Join Date
    Mar 2012
    Location
    Account_Deleted
    Posts
    165
    Thanks
    122
    Thanked 23 Times in 18 Posts
    Sorry to dig up old cows, but I was confronted by a "gas inspector ??" (yes i know) and asked how could i issue a coc with the isolator "near" the (newly installed) gas / solid plate /element combo stove in a kitchen. Apparently the new gas regs prohibits any isolators "near" a gas stove?

    All i have is my sans 10142 regs and according to the Regs a lpg gas stove and the area which it is located in is not a hazardous area?:

    7.14.3 The classification of the location and the selection of equipment
    permitted (such as flameproof, explosion proof and intrinsically safe
    equipment) shall be in accordance with SANS 10108. The installation of
    electrical equipment in explosive atmospheres and in the petroleum industry
    shall be in accordance with SANS 10086-1 and SANS 10089-2 respectively.

    NOTE Examples of hazardous locations are

    a) petrol pumps,
    b) spray painting booths,
    c) areas for the storage, mixing and use of flammable fuels, paints or solvents,
    d) grain silos and flour mills,
    e) coal storage facilities,
    f) wine cellars,
    g) areas for the storage and filling of LPG cylinders,
    h) battery charging locations, and
    I) sewage plant.


    but then again Regs 5.1.4 states clearly that:

    5.1.4 Positioning of equipment

    Electrical equipment which, under normal conditions will be

    a) exposed to flammable or explosive gas, vapour, dust or liquid, or to
    external influences such as direct sunlight, corrosive vapour or oil, or

    b) in a hazardous location,

    shall be so selected or enclosed that it is protected against harmful
    effects or it shall comply with the requirements of an applicable standard
    (or both).

    but then i have to comply with the following as well:

    6.16.3.1.2 A switch-disconnector for a cooking appliance(s) shall

    a) be in the same room as the appliance(s),
    b) be at a height above floor level of not less than 0,5 m and not more than
    2,2 m,
    c) preferably not be above the cooking appliance(s), (not necessarily)
    d) be within 3 m of the appliance(s), but within 0,5 m of the appliance(s)
    if the switch-disconnector's purpose is not clearly indicated, and
    e) not be fixed to the appliance.

    So what do i do with the stove isolator?
    Last edited by ACEsterhuizen; 06-Jan-15 at 02:31 PM. Reason: spelling

  12. #10
    Diamond Member
    Join Date
    Apr 2010
    Location
    planet earth
    Posts
    3,943
    Thanks
    153
    Thanked 317 Times in 287 Posts
    I am in a bit of a spot because the gas stove requires a socket outlet and the cable supplied with the plug top already connected is only 1.5 m long, so you literally have to either install a plug next to the gas stove at a lower level for it to reach or mount the plug directly above or just to the side of the stove. This could get interesting cant wait to see what the gas inspector has to say about it.

Page 1 of 3 123 LastLast

Similar Threads

  1. Connecting backup generators to existing electrical installation
    By Kevin Stubbs in forum Electrical Load Shedding Forum
    Replies: 35
    Last Post: 20-Jan-16, 07:28 PM
  2. how can I connecting a samsung galaxy s3 to a playstation 3
    By league_of_ordinary_men in forum Technology Forum
    Replies: 2
    Last Post: 29-Oct-12, 06:20 AM

Did you like this article? Share it with your favourite social network.

Did you like this article? Share it with your favourite social network.

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •