Results 1 to 7 of 7

Thread: transfomer junction box

  1. #1
    Suspended
    Join Date
    Oct 2007
    Posts
    2,346
    Thanks
    0
    Thanked 254 Times in 209 Posts

    transfomer junction box

    what are your thoughts on transfomers in the roof space?

    junction box or open?

  2. #2
    Gold Member Sparks's Avatar
    Join Date
    Dec 2009
    Location
    Port Elizabeth
    Posts
    909
    Thanks
    21
    Thanked 127 Times in 96 Posts
    Open terminals - ventilated box
    Shrouded terminals - acceptable open.

  3. #3
    Diamond Member AndyD's Avatar
    Join Date
    Jan 2010
    Location
    Cape Town
    Posts
    4,945
    Thanks
    582
    Thanked 938 Times in 759 Posts
    How about open terminals but insulation taped closed? I always insist they're screwed to a joist or baton. I don't allow them loose on the ceiling board.
    _______________________________________________

    _______________________________________________

  4. #4
    Gold Member Sparks's Avatar
    Join Date
    Dec 2009
    Location
    Port Elizabeth
    Posts
    909
    Thanks
    21
    Thanked 127 Times in 96 Posts
    Insulation tape melts and yes, they must be secured.

  5. #5
    Email problem
    Join Date
    Sep 2010
    Location
    cape town
    Posts
    308
    Thanks
    3
    Thanked 43 Times in 37 Posts
    Quote Originally Posted by AndyD View Post
    How about open terminals but insulation taped closed? I always insist they're screwed to a joist or baton. I don't allow them loose on the ceiling board.
    andy ,are you talking about the 50 va,s as well . most of the time i connect it on the ladder and then push them through the hole and for maintenance just pull it out. keeping in mind the distance the transformer must be from the lamp.

  6. #6
    Diamond Member AndyD's Avatar
    Join Date
    Jan 2010
    Location
    Cape Town
    Posts
    4,945
    Thanks
    582
    Thanked 938 Times in 759 Posts
    Admittedly it's not always practical but if the transformer has screw fixing slots and especially if the ceiling has insulation we require the transformers to be fixed. Ive come across a couple of installations with loose roof insulation that's been pumped in and the transformers have gone molten and caught fire. The transformers were installed after the insulation was pumped in but because of their weight they bury themselves over time.

    This is a notorious area of contention with little consensus between individual electricians. There was a relevant thread here not so long ago and it all boiled down to the use of the words 'should' and 'shall' in the 0142 regs.

    PVC/vinyl Insulation tape is rated to +70C so it ought to be suitable for insulation of transformer terminals. If the temp is higher than that the lighting should be cabled in silicone cable, not PVC.
    _______________________________________________

    _______________________________________________

  7. #7
    Email problem
    Join Date
    Jul 2011
    Location
    Boksburg
    Posts
    24
    Thanks
    0
    Thanked 1 Time in 1 Post
    Ok but obviously your plastic 50w downlight transformers "new type" dont apply to heat at all???

Similar Threads

  1. junction box
    By murdock in forum Electrical Contracting Industry Forum
    Replies: 3
    Last Post: 22-Sep-10, 10:07 PM
  2. sans junction box
    By murdock in forum Electrical Contracting Industry Forum
    Replies: 1
    Last Post: 20-Mar-10, 10:13 PM

Did you like this article? Share it with your favourite social network.

Did you like this article? Share it with your favourite social network.

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •