    is it legal to install sabs approved flexible cables from a main DB to a sub DB.

    in other words run a circuit directly from a new DB installed in a basement

    via a 21 core sabs approved flexible cable

    then disconnect the existing circuits in the sub DB on the first floor and join then directly to the 21 core flex cable straight to the dedicated socket outlets...which are wired in house wire.

    how important are the numbers in the flexible cable?

    this is not a trick question i am

  2. #2
    Suspended
    Join Date
    Oct 2007
    Posts
    2,346
    Thanks
    0
    Thanked 254 Times in 209 Posts
    please note pg 84 of sans 6.1.11 flexible cords shall not be used as part of the elctrical installtion, except where...

  3. #3
    Platinum Member
    Join Date
    Mar 2022
    Location
    South Africa
    Posts
    2,274
    Thanks
    60
    Thanked 103 Times in 98 Posts
    Comments are my opinion, unless regulations are attached to support the comment. This is social media, not a court room.

  4. #4
    Diamond Member AndyD's Avatar
    Join Date
    Jan 2010
    Location
    Cape Town
    Posts
    4,946
    Thanks
    583
    Thanked 938 Times in 759 Posts
    As far as I'm aware you're not permitted to use flexible cords (cabtyre) between a main and sub DB. It's not just 0142 regs that forbid this, also IEC 60335-1. If I remember correctly, ammendment 3 clarified.
    _______________________________________________

    _______________________________________________

  5. #5
    Suspended
    Join Date
    Oct 2007
    Posts
    2,346
    Thanks
    0
    Thanked 254 Times in 209 Posts
    this thread is gona get interesting...busy with the generator thread have been all afternoon so once i have sorted that out i will come back to this thread.

  6. #6
    Gold Member Sparks's Avatar
    Join Date
    Dec 2009
    Location
    Port Elizabeth
    Posts
    909
    Thanks
    21
    Thanked 127 Times in 96 Posts
    Far as I know all cabling used should be SABS but, that does not mean it can be used for any purpose. The permanent installation far as I know should be "hard" wire.

  7. #7
    Suspended
    Join Date
    Oct 2007
    Posts
    2,346
    Thanks
    0
    Thanked 254 Times in 209 Posts
    what is important is understanding what the difference is in the definitions

    a cable...solid or stranded...with strands exceeding 0.51 mm

    flexible cable...consists of strands of diameter not exceeding 0.51mm and which th nominal cross section area of each conductor exceeds 4 mm square

    flexible cord...nominal cross sectional area of each conductor does not exceed 4 mm square and each conductor consists of strands of diameter less than 0.31mm

    6.1.11 flexible cords shall not be used as part of the electrical installation except a-e in sans code

  8. #8
    Silver Member
    Join Date
    Jul 2008
    Location
    Germiston, South Africa
    Posts
    404
    Thanks
    25
    Thanked 47 Times in 43 Posts
    Quote Originally Posted by murdock View Post
    is it legal to install sabs approved flexible cables from a main DB to a sub DB.

    in other words run a circuit directly from a new DB installed in a basement

    via a 21 core sabs approved flexible cable

    then disconnect the existing circuits in the sub DB on the first floor and join then directly to the 21 core flex cable straight to the dedicated socket outlets...which are wired in house wire.

    how important are the numbers in the flexible cable?

    this is not a trick question i am
    I wonder how relevant is this question when the new version of SANS 10142 gets introduced soon?
    To make a mistake is human, to learn from that mistake is knowledge and knowledge is strength.

  9. #9
    Platinum Member
    Join Date
    Mar 2022
    Location
    South Africa
    Posts
    2,274
    Thanks
    60
    Thanked 103 Times in 98 Posts
    By the way this only applies to terminations where old screw type breaker and connector blocks it is not required for the new type of breaker terminal. We still use bootlace ferrules for pushin type connectors.

    6.1.12 Where flexible cords are used, the strands of the conductors shall be

    mechanically protected with ferrules to prevent the strands from being cut off
    in terminations.
    Last edited by Isetech; 09-Sep-23 at 01:15 PM.
    Comments are my opinion, unless regulations are attached to support the comment. This is social media, not a court room.

  10. #10
    Silver Member
    Join Date
    Jul 2008
    Location
    Germiston, South Africa
    Posts
    404
    Thanks
    25
    Thanked 47 Times in 43 Posts
    I am resurrecting this thread due to something I saw in SANS 10142-1-2021

    6.1.11 Where flexible cords are used as part of the electrical installation, the
    selection, installation and colour identification (see 6.3.3) shall be done in
    accordance with this part of SANS 10142. Flexible cords with cross sectional
    area less than 1 mm2
    shall not be permitted.
    6.1.12 Where flexible cords are used, the strands of the conductors shall be
    mechanically protected with ferrules to prevent the strands from being cut off
    in terminations.

    Can I assume now that one can wire a house in cabtyre?

    The reason I ask is because I have just come across a circuit that is a 2.5mm cabtyre from circuit breaker to aircon isolator
    To make a mistake is human, to learn from that mistake is knowledge and knowledge is strength.