    Many thanks.
    Excuse my ignorance but what is "PV cable" (Photo Voltaic?) and where does one find the official ratings for theses cables?
    I would like to know the rating for 2.5mm flexible cord
    To make a mistake is human, to learn from that mistake is knowledge and knowledge is strength.

  2. #12
    Platinum Member
    Join Date
    Mar 2022
    Location
    South Africa
    Posts
    2,274
    Thanks
    60
    Thanked 103 Times in 98 Posts
    Comments are my opinion, unless regulations are attached to support the comment. This is social media, not a court room.

  3. #13
    Platinum Member
    Join Date
    Mar 2022
    Location
    South Africa
    Posts
    2,274
    Thanks
    60
    Thanked 103 Times in 98 Posts
    Comments are my opinion, unless regulations are attached to support the comment. This is social media, not a court room.

  4. #14
    Silver Member
    Join Date
    Jul 2008
    Location
    Germiston, South Africa
    Posts
    402
    Thanks
    25
    Thanked 47 Times in 43 Posts
    Thank you for this but I am looking for the ratings for 2.5mm flexible cord. The above links only give the ratings for flexible cables which are 4mm and larger
    To make a mistake is human, to learn from that mistake is knowledge and knowledge is strength.

  5. #15
    Gold Member
    Join Date
    Jun 2020
    Location
    Fourways
    Posts
    771
    Thanks
    121
    Thanked 35 Times in 34 Posts
    Check 10142-1, I don't think fine stranded can be less than 4mm2

    Sent from my CPH2197 using Tapatalk

  6. #16
    Silver Member
    Join Date
    Jul 2008
    Location
    Germiston, South Africa
    Posts
    402
    Thanks
    25
    Thanked 47 Times in 43 Posts
    The following mentions flexible cords which the definition describes 4mm or smaller, or am I misunderstanding this definition?

    6.1.11 [I]Where flexible cords are used as part of the electrical installation[/I], the
    selection, installation and colour identification (see 6.3.3) shall be done in
    accordance with this part of SANS 10142. Flexible cords with cross sectional
    area less than 1 mm2
    shall not be permitted.
    6.1.12 Where flexible cords are used, the strands of the conductors shall be
    mechanically protected with ferrules to prevent the strands from being cut off
    in terminations.

    The definition of a flexible cord is as follows

    3.8.2
    flexible cable
    cable of which the conductors consist of strands of diameter not
    exceeding 0,51 mm and of which the insulation and covering are such that
    they afford flexibility and in which the nominal cross-sectional area of each
    conductor exceeds 4 mm˛
    3.8.3
    flexible cord
    cable of which
    a) the nominal cross-sectional area of each conductor does not exceed
    4 mm˛
    , and
    b) each conductor consists of strands of diameter less than 0,31 mm


    My understanding of this is that cord (cabtyre) of 2.5mm with fine wire is allowed. Or am i missing something?
    However, SANS does have amp ratings for flexible cables but not for flexible cords. Not sure why
    To make a mistake is human, to learn from that mistake is knowledge and knowledge is strength.

  7. #17
    Platinum Member
    Join Date
    Mar 2022
    Location
    South Africa
    Posts
    2,274
    Thanks
    60
    Thanked 103 Times in 98 Posts
    By the way this only applies to terminations where old screw type breaker and connector blocks it is not required for the new type of breaker terminal. We still use bootlace ferrules for pushin type connectors.

    6.1.12 Where flexible cords are used, the strands of the conductors shall be

    mechanically protected with ferrules to prevent the strands from being cut off
    in terminations.
    Last edited by Isetech; 09-Sep-23 at 01:15 PM.
    Comments are my opinion, unless regulations are attached to support the comment. This is social media, not a court room.

  8. #18
    Gold Member Sparks's Avatar
    Join Date
    Dec 2009
    Location
    Port Elizabeth
    Posts
    902
    Thanks
    21
    Thanked 127 Times in 96 Posts
    I think this is going off at a tangent. I have always and still believe that the flexible cables refered to in SANS are those which form part of the integral wiring of appliances. Between hob, oven and control panel for example. Just my 2cents worth, I will stick to hard wire. Call me old fashioned, I don't mind.

  9. #19
    Junior Member
    Join Date
    Oct 2018
    Location
    Gauteng
    Posts
    19
    Thanks
    2
    Thanked 2 Times in 2 Posts
    Quote Originally Posted by Leecatt View Post
    Thank you for this but I am looking for the ratings for 2.5mm flexible cord. The above links only give the ratings for flexible cables which are 4mm and larger
    Alvern Cables

    https://www.alverncables.co.za/downl...yre-cables.pdf

    Or scroll down to Cabtyre in aberdare:

    https://www.aberdare.co.za/product-c...general-wires/

  10. Thanks given for this post:

    Leecatt (12-Sep-23)

Page 2 of 2 FirstFirst 12

Did you like this article? Share it with your favourite social network.

Did you like this article? Share it with your favourite social network.

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •