    Estimating load with known diversity factors

    Good day all.

    I am going through old installation rules exam papers with no answers provided, and I attempmted to do one of the calculations as per topic title.

    Please could you have a look at this for me, and comment. I am a bit stumped by part two of the question as well, I cannot see another method of checking the result in the code.
    Also the max allowable loading of the supply transformer is 90% correct?

    Thanks in advance for your help.

    3.1 Calculate from the following information, the maximum amount of water heaters of 1kW each that may be installed according to the regulations:
    o 10kVa/220 v single phase transformer using a power factor of 0.95
    o Floor area 301m²
    o Two 0.75kW single phase motors
    o One electric oil heater of 500w
    o 20 lights

    3.2 Test your answer by making use of any other alternative method.



    3.1 answer:

    Total load :
    o Socket outlets -Floor area 301 m² = (5 kw for first 100 m²) + (1kw for second 100m²) +( 1kw for part of third 100m²) TOTAL = 7kw x diversity of .5 = 3.5kw
    o Motors = (.75kW x 2 ) = 1.5kW x diversity factor of 1 =1.5kW
    o Electric oil heater = 0.5kW x diversity of .5 = .25kW
    o 20 lights ( 20 x 60watts ) = 1200watts = 1.2kw x diversity of .5 = .6kW
    o
    o TOTAL LOAD ( 3.5kW+1.5kW+0.25kW+.6kW) = 5.85kW

    Therefore total current required = 5.85kW / 220v = 5850 /220 = 26.6A

    Max supply from transformer at full load (10000 *.95) /220 = 43.18 amps.

    43.18 max load x 90% = 38.86amps allowable.

    Therefore remaining amperage is 38.86-26.6 = 12.26Amps.

    Each heater requires: 1kw
    Therefore amps required per is 1kw/220 1000/220= 4.54 amps x diversity factor of 1 = 4.54 Amps.

    Therefore total amount of water heaters allowed is 12.26amps/4.54 amps = 2.7.


    To check total load with two connected : 26.6amps + (4.54 x 2) = 35.68
    To check total load with three connected 26.6amps + (4.53 x 3) = 40.19

    Therefore to enable the transformer to be loaded at 90% max only two may be added.

  2. Thanks given for this post:

    mikilianis (12-Oct-10)

  3. #2
    Email problem
    Join Date
    Aug 2010
    Location
    Free state
    Posts
    14
    Thanks
    1
    Thanked 6 Times in 4 Posts
    I think I may have answered the "check your answer with an alternative method"

    In other papers they ask you to use the current (I) method to test your answer, so I am thinking that you need to do the calculations in KW by not converting to amps, and then convert to amps to check.

  4. #3
    Platinum Member desA's Avatar
    Join Date
    Jan 2010
    Location
    South East Asia
    Posts
    1,023
    Thanks
    512
    Thanked 126 Times in 99 Posts
    Can I respectfully enquire from where you derive/determine the diversity factors used in your calculations?
    In search of South African Technology Nuggets(R), for sale & trading in South East Asia.

  5. #4
    Email problem
    Join Date
    Aug 2010
    Location
    Free state
    Posts
    14
    Thanks
    1
    Thanked 6 Times in 4 Posts
    I get the factors from page 302 of the sans 10142

  6. #5
    Platinum Member desA's Avatar
    Join Date
    Jan 2010
    Location
    South East Asia
    Posts
    1,023
    Thanks
    512
    Thanked 126 Times in 99 Posts
    I could well imagine cases where most, if not all of the power-points are operating together. No sense in using 0.5 diversity at those times, I'd expect. Surely that situation could/would leave you with an under-designed system?
    In search of South African Technology Nuggets(R), for sale & trading in South East Asia.

  7. #6
    Email problem
    Join Date
    Aug 2010
    Location
    Free state
    Posts
    14
    Thanks
    1
    Thanked 6 Times in 4 Posts
    The standards state, and the way this question is phrased state that you should take the loading of the socket outlets if unknown, to be as follows (annexD)

    5kw for the first 100m sq and thereafter 1kw per 100m sq or part thereof.

    then mutliply the result by the diversity factor to get potential load.

  8. #7
    Email problem
    Join Date
    Aug 2010
    Location
    Free state
    Posts
    14
    Thanks
    1
    Thanked 6 Times in 4 Posts
    Ok the lecturer got back to me. This is the way it must be answered, In table form.
    NOTE I got the calculation of the sockets wrong there is an extra 100m sq to be factored in ( for the 1m)
    Attached Files Attached Files

  9. #8
    Junior Member
    Join Date
    Sep 2010
    Location
    Windhoek
    Posts
    14
    Thanks
    4
    Thanked 0 Times in 0 Posts
    Morning Maccie. Pls foward me infprmation on handling and installation of cables not exceeding 33kv if u have. Peace

Similar Threads

  1. [Article] Conversion Factors Stage 6
    By Chatmaster in forum Marketing Forum
    Replies: 0
    Last Post: 22-Feb-10, 08:00 PM
  2. Load Readings
    By mikilianis in forum Electrical Contracting Industry Forum
    Replies: 2
    Last Post: 17-Jan-10, 10:39 PM
  3. And the lights go out again.
    By Dave A in forum Electrical Load Shedding Forum
    Replies: 71
    Last Post: 25-Feb-08, 04:38 PM
  4. Just how efficient is load shedding really?
    By Dave A in forum Electrical Load Shedding Forum
    Replies: 5
    Last Post: 23-Jan-08, 09:46 AM
  5. Replies: 0
    Last Post: 21-Jan-08, 03:26 PM

Did you like this article? Share it with your favourite social network.

Did you like this article? Share it with your favourite social network.

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •