    The insulation readings of a motors windings won't necessarily indicate how long it will last. This is especially true with a newly rewound motor. The insulation readings can change rapidly with the temperature. When the motor gets warmer any dampness will dry out giving better readings. Also you're using a thousand volt test. If the motor is 380-400v 3-phase, then a 500volt insulation test will be a better reflection of the insulation at the running voltage.

    A 380volt motor testing 200000 ohms @ 1000volts shouldn't be a safety issue.

  2. Thanks given for this post:

    mikilianis (18-Mar-10)

  3. #2
    Bronze Member mikilianis's Avatar
    Join Date
    Dec 2008
    Location
    Cape Town South Africa
    Posts
    125
    Thanks
    164
    Thanked 8 Times in 7 Posts

    Question Mikilianis

    I am under the impression or have been taught that a megger test should be done at twice the operational voltage that the equipment being tested is rated at. Also what is the permissable resistance (insulation) reading of a motor that has just been rewound, bearing in mind that rewinds are not done gratis.

  4. #3
    Suspended
    Join Date
    Oct 2007
    Posts
    2,346
    Thanks
    0
    Thanked 254 Times in 209 Posts
    a DC voltage twice that of the operating voltage is correct.

    insulation resistance must be higher than 1 Meg according to sans 10142

    has the motor been running and have you done and insulation resistance test since it has been reconnected?

    did they rewind the motor or put it in the oven to dry it out...you can always tell by the terminal wires.

    at what temperature is the motor running?

    have you checked phase to phase voltages and phase to earth voltages?

    why did you take the motor out to start with?

  5. Thanks given for this post:

    mikilianis (18-Mar-10)

Similar Threads

  1. Ceiling insulation effect on electrical work
    By duncan drennan in forum Electrical Contracting Industry Forum
    Replies: 9
    Last Post: 16-Jan-10, 05:04 PM

Did you like this article? Share it with your favourite social network.

Did you like this article? Share it with your favourite social network.

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •