    20 or 40 KA SPD

    Another topic that creates a ton of confusion, there is no grey area, just a lot of unskilled people doing installations.

    I have heard people say you have to use a 40 ka SPD, which is correct, however the majority of type 2 SPD's being installed at the moment look like they are 20 KA which is also correct.

    You need to read the label on the SPD.

    Looking at a Chint for example:

    NU6-11G

    40/275
    50/60 Hz
    In : 20 KA
    UC : 275
    I max : 40 KA (T2)
    Fused at 125A

    What does this all mean, it is a T2 SPD, suitable for AC installations.
    In 20 KA, stands for Nominal Discharge Current.
    UC 275 being the continuous voltage rating
    I max 40 KA, being the max discharge current.

    IF the circuit is higher than 125 amps, it must be fused with a 125 amp fuse.

    IF you are installing the SPD in a domestic property for example, then no fuse protection is required, provided you use the correct gauge wire for the circuit, IE 60 amp, 16 mmsq wire.

    If installed on the output of an 8 KVA inverter, rated at 32 amps, 4 mm wire would not require a fuse.

    It is very important to select the the correct SPD for AC and DC circuits, something many dont seem to understand.

  2. #2
    Platinum Member Derlyn's Avatar
    Join Date
    Mar 2019
    Location
    East london
    Posts
    1,706
    Thanks
    127
    Thanked 160 Times in 150 Posts
    Just an enquiry. Isn't 16 sqmm wire an overkill for 60A ?

  3. #3
    Bronze Member
    Join Date
    Feb 2025
    Location
    SA
    Posts
    139
    Thanks
    4
    Thanked 1 Time in 1 Post
    1.0 mm - 10 amp
    1.5mm - 16 amp
    2.5 mm - 20 amp
    4 mm 32 amp
    6 mm - 40 amp
    10 mm - 50 amp
    16 mm - 60 amp
    25 mm 80 amp

  4. #4
    Bronze Member
    Join Date
    Feb 2025
    Location
    SA
    Posts
    139
    Thanks
    4
    Thanked 1 Time in 1 Post
    You could use table 6.2 (a) on page 94 of the regs to consider various types of installation methods, but generally speaking the numbers shared in the previous thread would keep you in the CYA club.