This has turned into an interesting topic, after receiving a notification from the battery supplier tech support, to notify me that the volt drop on a site is higher (2.0VDC) than it should be (V batt and V BMS) which could result in issues with BMS
and charging and discharging the batteries. It could also compromise the battery warranty if the volt drop is higher than 1.5 VDC, we dont want that to happen.
Lets look at what would normally be a straight forward selection, using a5 kw system as an example, then I will do the most common setup in 8 kw.
5 kw inverter
5 kwh lithium battery. Rated at C0.5 (charge discharge rate 50 amps)
25 mm sq multi strand cable (Alvern cables permopower SABS 1507 cable 1000V) rated at 115 amps.)
100 amp DC fuses
Distance from the inverter to the DC fuse disconnect 1 metres and from the DC fuse disconnect to the battery 1 m.
We need to look at the volt drop per metre and at what point you need to consider using a bigger cable.
Then it might also be a good idea to look at the fault level.