    Fuse and cable selection for batteries used in backup systems.

    This has turned into an interesting topic, after receiving a notification from the battery supplier tech support, to notify me that the volt drop on a site is higher (2.0VDC) than it should be (V batt and V BMS) which could result in issues with BMS
    and charging and discharging the batteries. It could also compromise the battery warranty if the volt drop is higher than 1.5 VDC, we dont want that to happen.

    Lets look at what would normally be a straight forward selection, using a5 kw system as an example, then I will do the most common setup in 8 kw.

    5 kw inverter

    5 kwh lithium battery. Rated at C0.5 (charge discharge rate 50 amps)

    25 mm sq multi strand cable (Alvern cables permopower SABS 1507 cable 1000V) rated at 115 amps.)

    100 amp DC fuses

    Distance from the inverter to the DC fuse disconnect 1 metres and from the DC fuse disconnect to the battery 1 m.

    We need to look at the volt drop per metre and at what point you need to consider using a bigger cable.

    Then it might also be a good idea to look at the fault level.

  2. #2
    Bronze Member
    Join Date
    Feb 2025
    Location
    SA
    Posts
    139
    Thanks
    4
    Thanked 1 Time in 1 Post
    The part that is confusing me about the notification, when the batteries are charging or discharging V batt and BMS voltage are the same, there is no difference. The voltage difference is when the battery is at 100 % the gap open by a volt or 2. Once a load is applied the gap closes. I need to figure out how to screen shot and paste copy and paste.

  3. #3
    Bronze Member
    Join Date
    Feb 2025
    Location
    SA
    Posts
    139
    Thanks
    4
    Thanked 1 Time in 1 Post
    Try call Alvern cables to get technical info about their cables, I wish you luck.

  4. #4
    Bronze Member
    Join Date
    Feb 2025
    Location
    SA
    Posts
    139
    Thanks
    4
    Thanked 1 Time in 1 Post
    After a site visit and a couple hours of reviewing other site data. There will be about a 2 VDC split (V batt and BMS voltage) just after the battery reaches 100% SOC when viewed in the custom setting in the plant info.

    At any time the battery is charging or discharging, the gap between the V batt and BMS voltage will close to within 1 VDC.

    Carried out numerous Volt drop test at the inverter, DC fuse disconnect, master and slave batteries, while discharging the battery, and the volt drop at any point was less than 0.2 volts, so I would say the cable length and thickness is well within spec.

  5. #5
    Suspended
    Join Date
    Nov 2024
    Location
    New York
    Posts
    7
    Thanks
    0
    Thanked 0 Times in 0 Posts
    It looks like your 25 mm˛ cable is giving a voltage drop a bit above what you'd want, so it might be a good idea to either consider a larger cable or check if there are any connection issues that could be causing extra resistance. Also, factoring in the fault current level is key to ensure that your fuses can handle any potential surges.

  6. #6
    New Member
    Join Date
    Mar 2025
    Location
    Los Angeles
    Posts
    1
    Thanks
    0
    Thanked 0 Times in 0 Posts
    This sounds complicated, so I might as well just buy a ready-made multi-function whole house solar generator

Similar Threads

  1. Neutral earth bonding on backup systems.
    By Isetech in forum Electrical Contracting Industry Forum
    Replies: 145
    Last Post: 24-Mar-24, 04:37 PM
  2. Why Do Solar Energy Systems Require Batteries?
    By jennyzhang in forum Energy and Resource Conservation Forum
    Replies: 0
    Last Post: 12-Sep-23, 05:35 AM
  3. Batteries fuse disconnects and the like
    By Isetech in forum Electrical Contracting Industry Forum
    Replies: 6
    Last Post: 01-Jun-23, 06:14 PM
  4. battery cable selection
    By Isetech in forum Electrical Contracting Industry Forum
    Replies: 7
    Last Post: 26-Jan-23, 05:53 AM
  5. Separation of AC and DC wiring in backup systems
    By ians in forum Electrical Contracting Industry Forum
    Replies: 11
    Last Post: 01-Dec-21, 07:41 AM

Did you like this article? Share it with your favourite social network.

Did you like this article? Share it with your favourite social network.

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •