    Number of test reports for a grid-tie inverter SSEG

    I am just making sure I am not losing the plot here.

    Normally when you have SSEG, for each distribution board supplied by both the supply authority and the SSEG you would have a test report for when it is supplied by the supply authority and a test report for when it is supplied by the SSEG unit.

    However, for a pure PV SSEG grid-tie install, the inverter only supplies power when the supply authority's power is on. When the supply authority's power drops, the grid-tie also stops supplying power.
    Do you still do two test reports, one with just the supply authority connected, and one with both the supply authority and grid-tie SSEG connected?
    Or will one test report suffice?

    (Comparing the two, there appears to be no material differences in the test readings).

  2. #2
    Platinum Member
    Join Date
    Jun 2017
    Location
    Port Elizabeth
    Posts
    1,443
    Thanks
    40
    Thanked 337 Times in 283 Posts
    Quote Originally Posted by Dave A View Post
    I am just making sure I am not losing the plot here.

    Normally when you have SSEG, for each distribution board supplied by both the supply authority and the SSEG you would have a test report for when it is supplied by the supply authority and a test report for when it is supplied by the SSEG unit.

    However, for a pure PV SSEG grid-tie install, the inverter only supplies power when the supply authority's power is on. When the supply authority's power drops, the grid-tie also stops supplying power.
    Do you still do two test reports, one with just the supply authority connected, and one with both the supply authority and grid-tie SSEG connected?
    Or will one test report suffice?

    (Comparing the two, there appears to be no material differences in the test readings).
    I would say on a str grid tie, no 2nd test report as when you test you will be testing main incomer - it is not an alternative supply and cannot provide supply when main supply is not available - Looking at 7.12 , to me it appears to be only when mains is not there or used



    7.12 Alternative supplies
    NOTE Alternative supplies include but are not limited to low-voltage generating sets,
    photovoltaic (PV) installations, gas generators, diesel generators, wind turbines and
    hydropower plant.
    7.12.1 General
    7.12.1.1 Subclause 7.12 applies to an installation that incorporates
    alternative supplies intended to supply, either continuously or occasionally, all
    or part of the installation with the following supply arrangements:
    a) supply to an installation or part of an installation which is not connected to
    the main supply of a supplier;
    b) supply to an installation or part of an installation as an alternative to the
    main supply of a supplier; and
    c) appropriate combinations of the above.

    NOTE 1 Requirements of the supplier should be ascertained before any alternate
    supply is installed in an installation connected to the main supply of a supplier.
    NOTE 2 This part of SANS 10142 does not cover the generation plant, integration and
    synchronising requirements of an alternative supply operating in parallel with the main
    supply to an installation.

  3. Thanks given for this post:

    Dave A (21-Feb-25)

Similar Threads

  1. Who may issue a coc for SSEG ?
    By Derlyn in forum Energy and Resource Conservation Forum
    Replies: 4
    Last Post: 03-Feb-25, 09:08 AM
  2. On-Grid, Off-Grid & Hybrid system: what they are?☀☀☀
    By jennyzhang in forum Energy and Resource Conservation Forum
    Replies: 0
    Last Post: 11-Jan-24, 05:09 AM
  3. [Article] Hybrid Grid Tied Inverter with backup
    By Tonye in forum Energy and Resource Conservation Forum
    Replies: 2
    Last Post: 01-May-21, 09:47 PM
  4. [Question] Wiring my grid-tie inverter into the DB
    By recre8 in forum Electrical Contracting Industry Forum
    Replies: 1
    Last Post: 01-Dec-20, 03:21 PM

Tags for this Thread

Did you like this article? Share it with your favourite social network.

Did you like this article? Share it with your favourite social network.

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •