Results 1 to 4 of 4

Thread: Geyser too close to DB?

  1. #1
    Site Caretaker Dave A's Avatar
    Join Date
    May 2006
    Location
    Durban, South Africa
    Posts
    22,788
    Thanks
    3,331
    Thanked 2,693 Times in 2,270 Posts
    Blog Entries
    12

    Geyser too close to DB?

    This geyser is just above the distribution board.

    Click image for larger version. 

Name:	geyser-db.jpg 
Views:	116 
Size:	27.3 KB 
ID:	8978

    There is also a socket outlet point and light switch point in pretty close proximity.
    Common sense suggests it is a problem, but are there specific clauses in SANS 10142-1 that prohibits this situation?

  2. #2
    Platinum Member
    Join Date
    Jun 2017
    Location
    Port Elizabeth
    Posts
    1,443
    Thanks
    40
    Thanked 337 Times in 283 Posts
    Immediately thought " flip Dave " that's str forward and see the reg says Tap , I thought it said water outlet

    Based on 6.6.1.7 c then it could be a bit grey depending on how you interrupt the drain tap/value on the geyser

    I would go to the favorite clause 5 which the code asks you to do under 6.6.1.2


    6.6.1.2 A distribution board shall comply with the requirements of clause 5.

    6.6.1.4 The distribution board shall be suitable for the environmental
    conditions in which it operates.




    5.3.8 Positioning and accessibility of electrical equipment
    Electrical equipment shall be so positioned that
    a) it does not impair the functioning or safety of other equipment,
    b) it is readily accessible for installation, replacement, operation, testing,
    inspection, maintenance, and repair (see 6.6.1.9 and 6.9.4 for the main
    switch). All parts of the installation shall be accessible without the need to
    enter any adjoining premises (for example, in an apartment building),
    NOTE Common areas (such as passages and entrance halls) are not regarded as
    adjoining areas.
    c) there is easy access to its location,
    d) it is not likely to be physically damaged,


    5.5.1 Prevention of mutually detrimental influence
    An electrical installation shall be so arranged that there is minimal mutually
    detrimental influence between it and any other installation (including
    non-electrical installations)
    on the premises.

  3. Thanks given for this post:

    Dave A (24-Jan-25)

  4. #3
    Platinum Member Derlyn's Avatar
    Join Date
    Mar 2019
    Location
    East london
    Posts
    1,706
    Thanks
    127
    Thanked 160 Times in 150 Posts
    Only got my edition 2 with me at the moment.

    Reading 6.6.1.7.c) A distribution board shall not be mounted c) within a radius of 1 m from a water tap or valve ( in the same room), UNLESS the enclosure provides a degree of protection of at least IP44.

    I would install a shallow wooden cupboard over the db, as I have done in the past, just to err on the side of safety.

  5. Thanks given for this post:

    Dave A (24-Jan-25)

  6. #4
    Platinum Member
    Join Date
    Jun 2017
    Location
    Port Elizabeth
    Posts
    1,443
    Thanks
    40
    Thanked 337 Times in 283 Posts
    Quote Originally Posted by Derlyn View Post
    Only got my edition 2 with me at the moment.

    Reading 6.6.1.7.c) A distribution board shall not be mounted c) within a radius of 1 m from a water tap or valve ( in the same room), UNLESS the enclosure provides a degree of protection of at least IP44.

    I would install a shallow wooden cupboard over the db, as I have done in the past, just to err on the side of safety.
    ED3.2 - c) within a radius of 1 m from a water tap (in the same room), unless the
    enclosure provides a degree of protection of at least IP44.


    They took at valve and I seem to recall previous they had water pipe in the clause

  7. Thank given for this post:

    Dave A (24-Jan-25), Derlyn (24-Jan-25)

Similar Threads

  1. Geyser on, geyser on. Does it save electricity?
    By Annetta in forum Electrical Contracting Industry Forum
    Replies: 11
    Last Post: 10-Aug-21, 03:56 PM
  2. [Question] Close Corporation
    By Athi88 in forum General Business Forum
    Replies: 2
    Last Post: 16-Jun-20, 08:48 AM
  3. [Question] I can't close my laptop lid, help?
    By arabianmaiden in forum Technology Forum
    Replies: 2
    Last Post: 24-Apr-18, 01:27 PM
  4. 2x bank accounts. Should I close one?
    By Perform Computers in forum General Business Forum
    Replies: 17
    Last Post: 25-Jul-13, 09:55 AM
  5. [Question] close business
    By tow123 in forum General Business Forum
    Replies: 2
    Last Post: 28-Jul-11, 11:22 AM