    Quote Originally Posted by Derlyn View Post

    I'm wondering what the thinking was for the socket outlet not to be switchable ? Other than welding type socket outlets, I don't think I've seen "normal" socket outlets that are used in domestic applications, that are unswitched. Maybe the thinking was that one shouldn't use a "standard" socket outlet in a dedicated water heating circuit.

    Your thoughts ?
    Have no idea why they would make that statement of unswitched - you get the module type sockets that are unswitched .
    Maybe it is to stop other appliances being plugged in if you say put it in for an undercounter geyser and a wash machine is close by.

  2. #12
    Site Caretaker Dave A's Avatar
    Join Date
    May 2006
    Location
    Durban, South Africa
    Posts
    22,789
    Thanks
    3,331
    Thanked 2,694 Times in 2,271 Posts
    Blog Entries
    12
    Quote Originally Posted by Derlyn View Post
    I'm wondering what the thinking was for the socket outlet not to be switchable ? Other than welding type socket outlets, I don't think I've seen "normal" socket outlets that are used in domestic applications, that are unswitched. Maybe the thinking was that one shouldn't use a "standard" socket outlet in a dedicated water heating circuit.

    Your thoughts ?
    I suggest so that you can't have the power off without also disconnecting the neutral. I expect the concern is people might (quite probably would) switch off at the switch and start working on the element or thermostat, but the neutral was still connected. Rather force the user to unplug first.

    Makes you think a bit about the classification of socket outlets as an isolating device in general application

  3. Thank given for this post:

    AndyD (13-Aug-24), GCE (14-Aug-24)

  4. #13
    Platinum Member Derlyn's Avatar
    Join Date
    Mar 2019
    Location
    East london
    Posts
    1,708
    Thanks
    127
    Thanked 160 Times in 150 Posts
    We are discussing water heaters but what does the ommission of Annex M mean ?

    May any registered person now issue a coc and test report for any installation irrespective of whether they are single phase tester, IE or MIE ?

  5. #14
    Platinum Member
    Join Date
    Jun 2017
    Location
    Port Elizabeth
    Posts
    1,443
    Thanks
    40
    Thanked 337 Times in 283 Posts
    Quote Originally Posted by Derlyn View Post
    We are discussing water heaters but what does the ommission of Annex M mean ?

    May any registered person now issue a coc and test report for any installation irrespective of whether they are single phase tester, IE or MIE ?
    No - not quite - What it does mean is that the OHSA definitions now stand for single phase tester which means any installation with a point of control that is single phase may be worked on by a Single phase tester no matter what is after the point of control eg , solar unless it is a " specialised electrical installation " eg hospital , petrol etc

    It is a joke - We have gone from an SPT only allowed to do lights and plugs in a dwelling smaller than 100sqm ( i think 100sqm was the cut off ) and no stove , geyser or low voltage lighting to full blown domestic electrician with absolutely no training on the regulations with regards to DC , loading etc


    Extract from OHSA EIR
    "[I]electrical tester for single phase" means a person who has been registered as an electrical tester for single phase in terms of regulation 11 (2) for the verification and certification of the construction, testing and inspection of electrical installations supplied by a single-phase electricity supply at the point of control, excluding specialised electrical installations;[/I]

  6. #15
    Platinum Member
    Join Date
    Jun 2017
    Location
    Port Elizabeth
    Posts
    1,443
    Thanks
    40
    Thanked 337 Times in 283 Posts
    Quote Originally Posted by Dave A View Post
    I suggest so that you can't have the power off without also disconnecting the neutral. I expect the concern is people might (quite probably would) switch off at the switch and start working on the element or thermostat, but the neutral was still connected. Rather force the user to unplug first.

    Makes you think a bit about the classification of socket outlets as an isolating device in general application
    That could make sense and as you say , open another can of worms

  7. #16
    Site Caretaker Dave A's Avatar
    Join Date
    May 2006
    Location
    Durban, South Africa
    Posts
    22,789
    Thanks
    3,331
    Thanked 2,694 Times in 2,271 Posts
    Blog Entries
    12
    Quote Originally Posted by GCE View Post
    No - not quite - What it does mean is that the OHSA definitions now stand for single phase tester which means any installation with a point of control that is single phase may be worked on by a Single phase tester no matter what is after the point of control eg , solar unless it is a " specialised electrical installation " eg hospital , petrol etc

    It is a joke - We have gone from an SPT only allowed to do lights and plugs in a dwelling smaller than 100sqm ( i think 100sqm was the cut off ) and no stove , geyser or low voltage lighting to full blown domestic electrician with absolutely no training on the regulations with regards to DC , loading etc


    Extract from OHSA EIR
    "[I]electrical tester for single phase" means a person who has been registered as an electrical tester for single phase in terms of regulation 11 (2) for the verification and certification of the construction, testing and inspection of electrical installations supplied by a single-phase electricity supply at the point of control, excluding specialised electrical installations;[/I]
    I'm not sure Annex M helped much in that fight (around SPT's doing/not doing DC and solar on single phase systems) anyway.

  8. #17
    Platinum Member Derlyn's Avatar
    Join Date
    Mar 2019
    Location
    East london
    Posts
    1,708
    Thanks
    127
    Thanked 160 Times in 150 Posts
    6.9.3.3 b) NOTE 3

    "The removal of a plug from a socket outlet is a means of safe disconnection.
    "

    It seems, as Dave has suggested, that the motivation of the socket outlet on a water heater circuit, if used, having to be of the non switchable type, is to force the removal of the plug as a means of disconnection as per the above NOTE 3.

    It boggles the mind though, as to why the non switchable socket outlet is applicable on water heaters only and not other fixed appliances.
    Here I'm thinking aircons, swimming pool pumps etc.

    Any confusion could have been avoided by adding the words "non switchable" before socket outlet in the NOTE 3 in 6.2.3.3 which would then have meant that should a socket outlet be used as a disconnecting device on ANY fixed appliance, it must be of the non switchable type.

    That, in my humble opinion, would have made more sense, but to single out water heaters makes no sense at all.
    Last edited by Derlyn; 14-Aug-24 at 07:40 AM. Reason: Punctuation and spelling

  9. #18
    Platinum Member
    Join Date
    Jun 2017
    Location
    Port Elizabeth
    Posts
    1,443
    Thanks
    40
    Thanked 337 Times in 283 Posts
    Quote Originally Posted by Dave A View Post
    I suggest so that you can't have the power off without also disconnecting the neutral. I expect the concern is people might (quite probably would) switch off at the switch and start working on the element or thermostat, but the neutral was still connected. Rather force the user to unplug first.

    Makes you think a bit about the classification of socket outlets as an isolating device in general application
    Looks like you were on the money with that logic - Just had sight of a document were it was discussed before implemented

    also informed that the was a
    recommendation to remove a switch on the socket-outlet
    next to the geyser and to have an isolator due to safety
    reasons which will break the live and neutral. The WG
    resolved to modify clause 6.16.2.2 as “ Dedicated circuits
    shall be provided for water heaters and there may be more
    than one water heater on each circuit. Where a socket-outlet
    is used, it shall be unswitched.

  10. Thanks given for this post:

    Derlyn (14-Aug-24)

  11. #19
    Platinum Member
    Join Date
    Jun 2017
    Location
    Port Elizabeth
    Posts
    1,443
    Thanks
    40
    Thanked 337 Times in 283 Posts
    In the foreword of the document there was a statement made referencing the removal of a clause on external light protection

    Table of Changes Amdt 2

    Amended to update referenced standards and
    the requirements for voltage drop, busbars
    and earthing, to replace reference to an
    association with a reference standard, to
    delete the clause on external lightning
    protection
    , and the annex on authority for
    issuing a test report and a Certificate of
    Compliance.


    This is the actual clause that was deleted

    From SANS 10142-1 Ed3.1
    6.7.7 External lightning protection
    NOTE Where external lightning protection is installed, it should be in accordance with
    the requirements of SANS 10313.


    It would appear that insurance companies were misinterpreting the clause and insisting that Lightening protection must be installed - The removal should sort the problem

  12. Thanks given for this post:

    Derlyn (14-Aug-24)

  13. #20
    Platinum Member
    Join Date
    Jun 2017
    Location
    Port Elizabeth
    Posts
    1,443
    Thanks
    40
    Thanked 337 Times in 283 Posts
    Quote Originally Posted by GCE View Post
    Looks like you were on the money with that logic - Just had sight of a document were it was discussed before implemented

    also informed that the was a
    recommendation to remove a switch on the socket-outlet
    next to the geyser and to have an isolator due to safety
    reasons which will break the live and neutral. The WG
    resolved to modify clause 6.16.2.2 as “ Dedicated circuits
    shall be provided for water heaters and there may be more
    than one water heater on each circuit. Where a socket-outlet
    is used, it shall be unswitched.
    During discussion in the workshop this morning the first thing that came up was " surely it is more dangerous unplugging on load" and the 2nd point was " do we need to install with euro" as the small undercounter geysers generally come out with moulded plug tops - Will make Isetech start on a tangent

Page 2 of 3 FirstFirst 123 LastLast

Similar Threads

  1. SANS 10142-1 (ed3)
    By ians in forum Electrical Contracting Industry Forum
    Replies: 8
    Last Post: 23-Apr-21, 06:29 AM
  2. SANS 10142 Edition 2
    By Karel Kriel in forum Electrical Contracting Industry Forum
    Replies: 4
    Last Post: 02-Jul-17, 08:20 AM
  3. need help cannot find it in sans 10142-1
    By roelie in forum Electrical Contracting Industry Forum
    Replies: 1
    Last Post: 24-Feb-17, 07:46 AM
  4. sans 10142-1:2012
    By Pieter00 in forum Electrical Contracting Industry Forum
    Replies: 8
    Last Post: 23-Apr-13, 05:56 PM

Did you like this article? Share it with your favourite social network.

Did you like this article? Share it with your favourite social network.

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •