Nope, that's not how I think. That's a no-no. I think SANS 10142.
The regulations say that plugged in leads to fixed appliances ( the gate motor is a fixed appliance) should not be longer than 3 meters so if the gate motor is further than 3 meters away from the socket outlet, I would definately not be thinking of just fitting a plugtop to it's supply. That's a false assumption.
As far as the lights are concerned, they are called luminaires in the code. Correct me if I'm wrong, but according to 6.16.1.3, a luminaire is only regarded as a fixed appliance when either a fan or heater is incorporated in the unit. The regs regarding fixed appliances therefore do not apply to luminaires that do not incorporate either a fan or heater.l