Originally Posted by
Isetech
I would like to hear what others feel about things like excluded points plugged into sockets?
The reason I am sharing the information as I am carrying out the tests is because these are the challenges we all face on a daily basis, and everyone seems to have different views, I would like to hear your view on them, so that we can have open discussion about them to find solution or at least decide what we can agree.
You have to pay attention to 6.16.1.1, 6.16.1.5, 6.16.1.10, 6.14.1.4 and 6.14.1.6.
6.16.1.1 Fixed appliances do not form part of the electrical installation other than their positioning in relation to the supply and the wiring carried out between different parts of the appliances.
6.16.1.5 A socket-outlet shall supply only one fixed appliance. The use of flexible cords of length exceeding 3 m is not recommended. The reason for this recommendation is an endeavour to ensure operation of the overcurrent protective device. (But see also 6.14.1.4 for luminaires.)
The requirement that a socket outlet may only supply one fixed appliance is often a killer. Even if we say the security light system is "one fixed appliance", you still have to navigate this:
6.16.1.10 The wiring between different parts of a fixed appliance that are installed separately is part of the fixed installation, even where it is supplied from a socket-outlet, unless such wiring is less than 3 m in length.
And let's not forget the balance of requirements for luminaires supplied via socket outlets -
6.14.1.4 In a lighting circuit, a luminaire that is in a false ceiling or in a roof space 4 m above the floor where there is no ceiling, or in a floor cavity, or in a wall cavity, or in a similar position, may be fed from a socket-outlet which may be unswitched and not protected by earth leakage protection, provided that the socket-outlet
a) complies with SANS 164-3 or SANS 164-2-1 (PD-D type),
b) supplies one luminaire only, not exceeding the rating of the socket-outlet,
c) is accessible for maintenance purposes, and
d) is within 3 m of the luminaire that it supplies.
6.14.1.6 In a lighting circuit, a luminaire may be fed from a socket-outlet on a wall (that may be unswitched), provided that the socket-outlet
a) complies with SANS 164-3 or SANS 164-2-1 (partially dedicated socket-outlet),
b) is protected by earth leakage protection, except in the case where SANS 164-2-1 (partially dedicated socket-outlet) socket outlets are fitted,
c) supplies one luminaire only, not exceeding the rating of the socket-outlet,
and
d) is within 3 m of the luminaire that it supplies.
At least one 16 A socket-outlet that complies with the requirements of 6.15.1.1 shall be installed in the same room.
For that last point, perhaps a discussion point is whether the socket outlet is switched at the socket outlet, or at a location away from the socket outlet.
(Essentially, at what point does a circuit become a "lighting circuit").