Results 1 to 4 of 4

Thread: Calculate for full load conditions

  1. #1
    Full Member
    Join Date
    Apr 2016
    Location
    South Africa
    Posts
    78
    Thanks
    34
    Thanked 1 Time in 1 Post

    Calculate for full load conditions

    Good day

    As per the below reg what calculation is the calculation for full load conditions.

    I know we used 50 percent of circuit load in older regs.I am not sure what this is refering too.


    8.6.10 Voltage, at distribution board — on load
    Switch on the maximum available load and measure the voltage at the point of
    control. Calculate for full load conditions and notify the supplier (see annex H)
    if that voltage will be outside the regulatory limits (see 5.4.2).

    Thank you

    Sent from my CPH2197 using Tapatalk

  2. #2
    Platinum Member Derlyn's Avatar
    Join Date
    Mar 2019
    Location
    East london
    Posts
    1,708
    Thanks
    127
    Thanked 160 Times in 150 Posts
    Quote Originally Posted by Gtfast View Post
    Good day

    As per the below reg what calculation is the calculation for full load conditions.

    I know we used 50 percent of circuit load in older regs.I am not sure what this is refering too.


    8.6.10 Voltage, at distribution board — on load
    Switch on the maximum available load and measure the voltage at the point of
    control. Calculate for full load conditions and notify the supplier (see annex H)
    if that voltage will be outside the regulatory limits (see 5.4.2).

    Thank you

    Sent from my CPH2197 using Tapatalk
    You need not use 50% of full load. Any percentage will work as the volt drop will be directly proportional to the load drawn.

    Remember this test is not carried out to test any wiring on the installation.
    It is done to test the volt drop on the incoming supply cable.

    Example.

    A domestic 60A supply is a 15kW supply.
    Check what size element is in the geyser. For this exersize lets use 3Kw. ( 1/5th of full load )
    Turn off all loads.
    1. Measure voltage at point of control. ( main breaker )
    2. Turn on geyser (3kW)
    3. Measure voltage at point of control again.
    4. Note the difference.
    5. Multiply the difference by 5. That will be the volt drop at 15kW.
    6. Subtract the answer obtained in 5 above from the reading obtained with no load at point 1 above.

    The result must be within the parameters set out in 5.4.2

    If you use, for instance a load of 5kW for the test, then in point 5 above, you will multiply by 3 to get full load and so on.

    Hope this helps.

  3. Thank given for this post:

    Dave A (01-Jun-24), Dylboy (03-Jun-24)

  4. #3
    Full Member
    Join Date
    Apr 2016
    Location
    South Africa
    Posts
    78
    Thanks
    34
    Thanked 1 Time in 1 Post
    Thanks Derlyn
    I can know rest.

    Sent from my CPH2197 using Tapatalk

  5. #4
    Full Member
    Join Date
    Apr 2016
    Location
    South Africa
    Posts
    78
    Thanks
    34
    Thanked 1 Time in 1 Post
    Good day

    If one has a 3 phase and neutral system .How would one do the voltage at distribution board- on load calculation as per .

    8.6.10 Voltage, at distribution board — on load

    Switch on the maximum available load and measure the voltage at the point of

    control. Calculate for full load conditions and notify the supplier (see annex H)

    if that voltage will be outside the regulatory limits (see 5.4.2).

    Do the calculation as per annexure D?
    Use the same method as for single phase for live to neutral?

    Anyone know where I can get literature on this.



    Sent from my CPH2197 using Tapatalk

Similar Threads

  1. How did they calculate this ?
    By Dylboy in forum Electrical Contracting Industry Forum
    Replies: 31
    Last Post: 28-Jan-22, 10:16 AM
  2. [Question] How do i calculate value n category share.
    By yrstruly in forum Marketing Forum
    Replies: 0
    Last Post: 16-Mar-21, 07:32 PM
  3. how to calculate notional rent
    By Maijane in forum Accounting Forum
    Replies: 0
    Last Post: 24-Jun-20, 01:19 PM
  4. [Question] SANS question: Using black wires for load conditions
    By Razer0 in forum Electrical Contracting Industry Forum
    Replies: 1
    Last Post: 13-Jun-18, 03:43 PM
  5. Load Shedding to be revived in full force
    By irneb in forum Electrical Load Shedding Forum
    Replies: 15
    Last Post: 06-Nov-14, 05:43 AM

Did you like this article? Share it with your favourite social network.

Did you like this article? Share it with your favourite social network.

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •