Originally Posted by
Derlyn
If the installation is stock standard as you have mentioned, then the socket outlets will have metal bases and if your earth loop tests are satisfactory then it's considered reasonably safe and no extra earth wire is required, however, when a plastic socket outlet is fitted then you have a problem. An earth wire will then have to be pulled in between the consumer earthing terminal in the DB and the socker outlet.
It is then also advisable as per the note on page 158 to fit an earth leakage relay if there isn't already one, irrespective of the date of the original installation.
The above is how I would handle it. Let's hear what the other toppies say.