Been thinking on this one - Do you have an isolator or CB as mains in the DB
If city power is 80Amp - I would put a 60 amp in the DB on mains to see if that trips first
My gut tells me you have a cable fault that is tripping when it blows clear which is why your megga test does not pick up an issue - An hour or so later once water has got back into the problem area it will sit and short until it blosws again
Test after and hour or 2 of being on.
Had similar on 2 x 120sqmm in parallel - Cable must have been damaged years ago and took almost 15 years before the fault become a complete nuisance - It was under a concrete yard and we were just lucky that while we were standing there we saw wisp of smoke come out between concrete joints - dug down and found the cable fault.
Andrew_van_Zyl (20-Apr-24)
Good suggestion GCE - Thank you. Weirdly the problem has gone away and the client is less noisy. I will re-visit this if and when.
Lol at wisps of smoke - generally a sign of trouble!