    Time to design and install my solar system for the workshop.

    what is the goal, load solution or save money, this is the most important question, especially if there is a budget

    My goal is to save money, I want to produce enough electricity during the day to keep my office and workshop functional.

    Before I do anything, I need to look and the roof space available, now that I have the panel template on the roof, I can see that there is not that much space, and it is not high enough to stack 2 rows, that huge problem. I was hoping top get about 20kwp on the roof , instead it is more like 8kwp and even that is pushing it, because the roof is made up of different levels and directions.

    I have a north east facing roof which will only see sun after lunch due to massive trees ( no they are not getting cut down) .

    The other north east facing roof can only fit 2 panels ( not worth fitting).

    I have an east facing roof which will get the majority of panels, its flat and one level.

    Then the west facing roof will get 6 panels with a push, multi level, so it is a bit of a challenge and shading will be a challenge if the panels are not centralized.

    I have a south west facing roof , the other side of the main building, no trees and the most roof space. I could fit 32 panels, but that will be a last resort.
    Comments are my opinion, unless regulations are attached to support the comment. This is social media, not a court room.

  2. #2
    Bronze Member
    Join Date
    Mar 2022
    Location
    Little Falls, Roodepoort
    Posts
    122
    Thanks
    54
    Thanked 9 Times in 8 Posts
    Quote Originally Posted by Isetech View Post
    Time to design and install my solar system for the workshop.

    what is the goal, load solution or save money, this is the most important question, especially if there is a budget

    My goal is to save money, I want to produce enough electricity during the day to keep my office and workshop functional.

    Before I do anything, I need to look and the roof space available, now that I have the panel template on the roof, I can see that there is not that much space, and it is not high enough to stack 2 rows, that huge problem. I was hoping top get about 20kwp on the roof , instead it is more like 8kwp and even that is pushing it, because the roof is made up of different levels and directions.

    I have a north east facing roof which will only see sun after lunch due to massive trees ( no they are not getting cut down) .

    The other north east facing roof can only fit 2 panels ( not worth fitting).

    I have an east facing roof which will get the majority of panels, its flat and one level.

    Then the west facing roof will get 6 panels with a push, multi level, so it is a bit of a challenge and shading will be a challenge if the panels are not centralized.

    I have a south west facing roof , the other side of the main building, no trees and the most roof space. I could fit 32 panels, but that will be a last resort.
    Hi. I suggest using http://OpenSolar.com to plan it out. It's free and very accurate

    Sent from my SM-A226B using Tapatalk

  3. #3
    Platinum Member
    Join Date
    Mar 2022
    Location
    South Africa
    Posts
    2,066
    Thanks
    56
    Thanked 98 Times in 94 Posts
    What inverter will I need ? An 8 KW should do the job and by looking at all the current projects that we have completed, it is the best bang for your buck, a 3.5 kw is just too small and considering the price is only a few grand less than a 5 kw, its not worth the hassle, a 5 kva is a nice entry level load shedding solution, but not suitable for slightly larger loads. I did consider going bigger to get the higher solar rating, but with my roof space challenge, the 8 KW will be the best value for money.

    The next question is which brand, well we all know which brand I use, I think I am on no 15 now after this weekend, not 50 yet, but hey if you look at my projects they would all pass the warranty inspection, the test report and COC, safe guidelines for lithium battery installations and most import, only one recorded fault, due to customer error, which he was warned about prior to the installation, which we have since modified to the way I suggested we split the essential and non essential.

    Time to look at the spec sheet,

    Max DC input power - 10400 watts
    PV input voltage - 370 (125-500)
    MPPT range - 150 - 425
    Start up voltage - 125 (this is important if you only have a few panels or going to split into 4 strings)
    PV input current - 26ADC +26 ADC
    Max PV Isc - 44ADC+44ADC
    No. of trackers -2
    No. of strings 2+2 ( this important and we will go into details)
    Comments are my opinion, unless regulations are attached to support the comment. This is social media, not a court room.

  4. #4
    Platinum Member
    Join Date
    Mar 2022
    Location
    South Africa
    Posts
    2,066
    Thanks
    56
    Thanked 98 Times in 94 Posts
    By the way, I have been told that I should stick to DIY groups because I ask stupid questions and dont have the skills, knowledge or experience to be installing solar systems. So how does that saying go "dont try this at home' Rather consult with a 50 plus installer

    The way I see it, we all have to start somewhere, so if you feel any information shared in this thread is incorrect, please feel free to correct the information.
    Comments are my opinion, unless regulations are attached to support the comment. This is social media, not a court room.

  5. #5
    Bronze Member
    Join Date
    Mar 2022
    Location
    Little Falls, Roodepoort
    Posts
    122
    Thanks
    54
    Thanked 9 Times in 8 Posts
    The 8kW Sunsynk is an awesome machine if thats where you're going

  6. #6
    Platinum Member
    Join Date
    Mar 2022
    Location
    South Africa
    Posts
    2,066
    Thanks
    56
    Thanked 98 Times in 94 Posts
    Yip the budget is tight, so it would have been cheaper to go the luxpower, growatt, axpert or one of those units, but I want a long term solution with a company that is growing as fast as the solar industry, always looking at improving the technology.

    I did consider solar edge, Sungrow or Victron, but to start trying to find someone to educate me on the product or go sit in classes during week, just doesn't make sense.

    The Victron has too many bits and pieces, the Solar edge is limited with variety and Sungrow, I have only heard of them never actually seen any installation. A tip for people wanting to get into the SA market, I would suggest you offer lots of free training and not on Monday and Tuesday, when we are busy at work. I would be happy to go sit in a classroom for the weekend to learn about a different product. or better still, with technology today, who needs to sit in a classroom?

    The system which will eventually win the race to the top, will be the system with a lithium battery that is safe to install anywhere on the property.



    Quote Originally Posted by Andrew_van_Zyl View Post
    The 8kW Sunsynk is an awesome machine if thats where you're going
    Comments are my opinion, unless regulations are attached to support the comment. This is social media, not a court room.

  7. #7
    Diamond Member Justloadit's Avatar
    Join Date
    Nov 2010
    Location
    Johannesburg
    Posts
    3,490
    Thanks
    138
    Thanked 695 Times in 593 Posts
    Blog Entries
    1
    One thing that the suppliers of PV Combiner boxes, is that to make it cheaper, they leave out the isolating diode.
    Effectively if you have each string with an isolating diode, then you can have the same number of panels in each string, and then parallel this into the combiner box and have a single connection to the inverter.

    What is important here is that you could have a number of panels facing east, north, west, and which ever string has the most sun radiance, will power the inverter, the other panels will contribute less but are still active. The inverter will see the total power from all the strings and do the MPPT. As the sun changes during the day, so each bank will effectively come into supplying power to the inverter. The diodes ensure that this occurs. Not using the diodes, will cause issues as the panels are of different temperatures and therefor have different internal impedance's, and may affect the total operation of all the panels, and of the MPPT controller.

    BUT - using the diodes does have an issue, and that is the reason no one wants to have this in their equipment. The diodes must be able to carry the current of the string, and have the blocking capacity of the total string voltage.
    This means that the diodes have to be on a suitable heat sink.

    Lets take for instance we use silicon rectifying diodes, and they are rated at say 20A and 1000V, no problem, however, the diode has a 1.7V drop across the junction, so if we take 10A as a value to do comparisons with, then for silicon diode V X I = 1.7V x 10A = 17Watts, this is per string, so it requires a decent heat sink, and you do not want fans as there is a number of issues for that.

    Lets take for instance we use a Schotky rectifying diode, they may be rated at 600V at 12A, and has a 1.2V drop across the junction, so using the same formulae, V X I = 1.2V x 10A - 12Watts. A substantial difference since power is a non liner function and falls under the square type of curve. The cost of Schotky is no cheap device, but in no way beaks the bank. But under the right conditions, it makes sense in using it in your application of panels all over the place.
    Victor - Knowledge is a blessing or a curse, your current circumstances make you decide!
    Solar pumping, Solar Geyser & Solar Security lighting solutions - www.microsolve.co.za

  8. #8
    Platinum Member
    Join Date
    Mar 2022
    Location
    South Africa
    Posts
    2,066
    Thanks
    56
    Thanked 98 Times in 94 Posts
    I have scrapped the idea of installing the panels on the south side of the roof for now, I will be installing a small 3.5 kw inverter which will be grid tied and registered with municipality, which will require a small admin fee, calculated per KW, but more about that later.

    The inverter has 2 MPPT trackers which can connect 2 strings per MPPT (2+2)

    I will be using JA solar 545 watt panels.

    https://solar.co.za/wp-content/uploa...-525W-550W.pdf


    The kick start is 125-150 VDC, so we need at least 4 panels per sting

    The current is 26 amps so 2 strings of 13 amp will be fine

    I plan to install 10 panels on the east facing roof, spit into 2 x 5 panels and 6 panels on the west facing roof (thats all I can fit)

    I am going to build a carport and fit 10 panels on the carport all facing north

    String 2 (1 and 1.1) + 2 (2 and 2.1)

    String 1 - 5 panels x 49.75 x 5 = 248 VDC
    String 1.1 - 5 panels x 49.75 = 248 VDC

    String 2 - 6 panels x 49..75 x 5 = 298.5 VDC
    No string 2.1

    Once I get the carport built, we will revisit the layout.
    Comments are my opinion, unless regulations are attached to support the comment. This is social media, not a court room.

  9. #9
    Platinum Member
    Join Date
    Mar 2022
    Location
    South Africa
    Posts
    2,066
    Thanks
    56
    Thanked 98 Times in 94 Posts
    I am busy with another project. The roof is big enough to double stack the panels. The reason I am sharing is because I get asked these questions at least once a week.

    "What is the max amount of panels you can connect to an 8 kw Sunsynk inverter"

    We plan to install 32 x 545 watt panels,

    8 per string on the east facing roof and 8 per string on the west facing roof.

    string 1 top row (east) - 8 panels x 49.75 VDC = 398 VDC
    String 1.1 bottom row east - 8 panels x 49.75 VDC = 398 VDC

    String 2 top row (west) - 8 panels x 49.75 VDC =398 VDC
    string 2.1 bottom row (west) - 8 panels x 49.75 = 398 VDC

    Optimal voltage 370, so it is just above.

    Looking at the STC values which are higher than the NOCT values so it should be ok, max power for a 545 watt panel is 13.04 x 2 = 26.12, border lining the 26 amp for the MPPT.

    The short circuit current is 13.93 amps.

    Which brings me to another very common question asked all the time "what size fuse must you install? " If the panel has a short circuit current of 13.93 amp, why do people fit 30 amp fuses, the answer because they use a 6 mm sq solar double insulated wire. Is the fuse the panels or the wire, according to any electrician to speak to, it is protect the wire. What do you think?

    Back to the panel:

    So we have 17440 kwp on the roof, you cant do that, actually you can, your voltages are within the VOC rating which is the most important factor when designing installations and your currents are within the limits.

    If these panel were all north facing, I probably wouldnt suggest this many panels, however there are a few things to consider, the east west facing roof, the angle of the roof and the losses in winter (which could be as much as 40 %) which means you can only produce a total of around 11kwp in june/july. If you are registered and feeding back into the grid to maximize ROI, best you push as much power as you can.

    Considering the price of panels, I am looking at only installing 1 x 5.1 kwh battery for now, just to keep the lights on and the rest of the money will be pushed into panels and inverter.

    There is talk that the load shedding will be done by the end of the year, I know I heard that back in 2008, so I wont be holding my breathe, however even if they do fix the load shedding. my goal is not to install a system for load shedding but rather saving money on my bill.

    Our utility charges a fee per kw which is around R143.75 per kw x 8 kw (hence the small grid tied) = R1150.00 per month.

    So you need to push as much power back into the grid to recover these cost. Having 6 panels on the roof with an 8 kw unit was a nice load shedding solutions, to top up your batteries without using the grid power, but will become a waste of money once they force you to register your system.

    Just think if you install a 16 kw unit x R143.75 = R2300 monthly charge, with a feed back tarriff of only around R1.40 , you gonna need a lot of panels.
    Comments are my opinion, unless regulations are attached to support the comment. This is social media, not a court room.

  10. #10
    Diamond Member Justloadit's Avatar
    Join Date
    Nov 2010
    Location
    Johannesburg
    Posts
    3,490
    Thanks
    138
    Thanked 695 Times in 593 Posts
    Blog Entries
    1
    Quote Originally Posted by Isetech View Post

    String 2 (1 and 1.1) + 2 (2 and 2.1)

    String 1 - 5 panels x 49.75 x 5 = 248 VDC
    String 1.1 - 5 panels x 49.75 = 248 VDC

    String 2 - 6 panels x 49..75 x 5 = 298.5 VDC
    No string 2.1
    Just I note, and I stand to be corrected here, I am not sure if you can use 2 different voltages on each MPPT input on the inverter.
    Victor - Knowledge is a blessing or a curse, your current circumstances make you decide!
    Solar pumping, Solar Geyser & Solar Security lighting solutions - www.microsolve.co.za

Page 1 of 4 123 ... LastLast

Similar Threads

  1. Golf cart solar panel
    By Dylboy in forum Electrical Contracting Industry Forum
    Replies: 7
    Last Post: 03-Apr-24, 02:22 PM
  2. Solar panel safety rating
    By Isetech in forum Electrical Contracting Industry Forum
    Replies: 6
    Last Post: 05-Feb-23, 06:26 AM
  3. Solar panel wiring. (Question)
    By Derlyn in forum Energy and Resource Conservation Forum
    Replies: 8
    Last Post: 07-Jun-22, 05:28 AM
  4. [Question] Solar Panel Certificate of Compliance
    By FrancoisERA in forum Electrical Contracting Industry Forum
    Replies: 0
    Last Post: 16-Jul-21, 04:40 PM

Did you like this article? Share it with your favourite social network.

Did you like this article? Share it with your favourite social network.

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •