    If you read carefully he was measuring to the neutral wire AFTER disconnecting it from the neutral bar, in which case there shouldn't be a voltage unless the neutral is touching earth somewhere, which I suspect.

    The only time you gonna measure 220v between live and neutral is if the neutral is connected to the neutral bar.

  2. Thanks given for this post:

    aquamoon (09-Apr-24)

  3. #12
    Full Member
    Join Date
    Nov 2023
    Location
    South africa
    Posts
    25
    Thanks
    0
    Thanked 0 Times in 0 Posts
    True but there seems to be alot going on with his installation perhaps even a reversed polarity somewhere?

  4. #13
    New Member
    Join Date
    Apr 2024
    Location
    Johannesburg
    Posts
    6
    Thanks
    3
    Thanked 0 Times in 0 Posts
    Quote Originally Posted by Derlyn View Post
    You mention that when on grid power there are intermittant trips but not when in islanding mode.

    From the above I seem to think that there's no earth neutral bridge when the inverter is in islanding mode, so the earth leakage cannot trip even if there's an earth fault.

    I'm gonna stick my neck out and say there are 2 faults.
    1. An intermittant earth fault on the neutral.
    2. No earth neutral bridge when in islanding mode.

    Good luck.
    The Victrons have a relay that makes an earth neutral bridge when in islanding mode.


    Sent from my iPhone using Tapatalk

  5. #14
    Platinum Member
    Join Date
    Jun 2017
    Location
    Port Elizabeth
    Posts
    1,304
    Thanks
    36
    Thanked 314 Times in 263 Posts
    Quote Originally Posted by aquamoon View Post

    Should the inverters be connected directly to mains and not via the earth leakage? When on grid there are essentially 2 earth leakages power will flow through to any endpoint. The sans recommended layout for a UPS system seems to indicate doing it the way I have done it.


    Sent from my iPhone using Tapatalk
    Something sounds wrong with the positioning of your ELU - Should be mains power - inverter - earth leakage -plug CB

    I am reading that you have the ELU before the inverter ?

    The Annex P shows ELU but be careful that they are not referring to a +/- 100ma unit because no decent earth can be obtained

  6. #15
    New Member
    Join Date
    Apr 2024
    Location
    Johannesburg
    Posts
    6
    Thanks
    3
    Thanked 0 Times in 0 Posts
    Quote Originally Posted by GCE View Post
    Something sounds wrong with the positioning of your ELU - Should be mains power - inverter - earth leakage -plug CB

    I am reading that you have the ELU before the inverter ?

    The Annex P shows ELU but be careful that they are not referring to a +/- 100ma unit because no decent earth can be obtained
    I do have the inverters connected after the main EL. I also have an EL for each of the 2 outputs of the combined inverters outputs.

    So when on grid power, power flows through 2 EL’s to an endpoint (e.g a plug point) Could this, having power flow through 2 EL’s be causing a problem?

    I felt that having the inverters on the min EL would be a safer option if something were to go wrong with the inverters themselves although Aircon’s are not connected to EL because they often cause nuisance trips being exposed to the elements. They are also “supposedly” out of reach of users.

    Could you explain more about your comment on Annex P?


    Sent from my iPhone using Tapatalk

Page 2 of 2 FirstFirst 12

Similar Threads

  1. High neutral earth reading
    By Thys LOW Elektries in forum Electrical Contracting Industry Forum
    Replies: 6
    Last Post: 27-Mar-22, 02:26 PM
  2. Over voltage and lost neutral protection
    By ians in forum Electrical Contracting Industry Forum
    Replies: 7
    Last Post: 13-Mar-20, 07:16 PM
  3. Voltage between Neutral and Earth - When is it a fault?
    By Justloadit in forum Electrical Contracting Industry Forum
    Replies: 5
    Last Post: 20-Jul-19, 09:23 PM
  4. ELEVATED VOLTAGE TO NEUTRAL ABOVE 50 V -NOTICE OF POTENTIAL DANGER
    By Tshepo Mokoena in forum Electrical Contracting Industry Forum
    Replies: 5
    Last Post: 26-Apr-18, 08:26 AM
  5. Elevated voltage on supply neutral measurement
    By PaulG in forum Electrical Contracting Industry Forum
    Replies: 8
    Last Post: 05-Mar-16, 07:45 PM

Did you like this article? Share it with your favourite social network.

Did you like this article? Share it with your favourite social network.

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •