    Voltage reading between supply live and disconnected load neutral

    When disconnecting the neutral of the cable supplying the pool db from the main db neutral bar and then measuring the voltage between the main db live and the disconnected neutral I get 230V, I would expect to get 0V. What am I missing?

  2. #2
    Platinum Member Derlyn's Avatar
    Join Date
    Mar 2019
    Location
    East london
    Posts
    1,706
    Thanks
    127
    Thanked 160 Times in 150 Posts
    The neutral of the cable is probably down to earth somewhere. Megger test the cable.

  3. Thanks given for this post:

    aquamoon (08-Apr-24)

  4. #3
    Platinum Member Derlyn's Avatar
    Join Date
    Mar 2019
    Location
    East london
    Posts
    1,706
    Thanks
    127
    Thanked 160 Times in 150 Posts
    I suppose the earth leakage was tripping, the reason for you disconnecting the cable.

  5. #4
    Platinum Member Derlyn's Avatar
    Join Date
    Mar 2019
    Location
    East london
    Posts
    1,706
    Thanks
    127
    Thanked 160 Times in 150 Posts
    Disconnect the cable at the pool end as well and then measure the voltage again.

  6. Thanks given for this post:

    aquamoon (08-Apr-24)

  7. #5
    New Member
    Join Date
    Apr 2024
    Location
    Johannesburg
    Posts
    6
    Thanks
    3
    Thanked 0 Times in 0 Posts
    I was getting intermittent earth leakage trips, once I disconnected the neutral the trips went away.

    It only seemed to start after a db rewire where previously the pool was on its own leakage and now it’s part of the main earth leakage. That rewire was fine until it started raining, then the trips began.


    Sent from my iPhone using Tapatalk

  8. #6
    Platinum Member Derlyn's Avatar
    Join Date
    Mar 2019
    Location
    East london
    Posts
    1,706
    Thanks
    127
    Thanked 160 Times in 150 Posts
    Yep. Cable down to earth somewhere, for sure.

  9. #7
    New Member
    Join Date
    Apr 2024
    Location
    Johannesburg
    Posts
    6
    Thanks
    3
    Thanked 0 Times in 0 Posts
    The trips have resumed, so it is not the cable to the pool causing the trips, since then I have disconnected the geysers neutrals as well, still trips.

    I have 2 Victron Multiplus connected in parallel mode. These are connected to the main db earth leakage. The Victrons each have 2 outputs, which are combined in parallel. Each of these outputs is connected to an earth leakage. All plugs and lights are on the first output and the stove on the second. I want to be able to program the system to only allow the second output to be on under certain conditions.

    I have no trips when the inverters switch to inverting or when they switch back to grid power. All worked well until recently. When on grid power I experience intermittent trips. No trips when on inverter power.

    Should the inverters be connected directly to mains and not via the earth leakage? When on grid there are essentially 2 earth leakages power will flow through to any endpoint. The sans recommended layout for a UPS system seems to indicate doing it the way I have done it.


    Sent from my iPhone using Tapatalk

  10. #8
    Platinum Member
    Join Date
    Jun 2017
    Location
    Port Elizabeth
    Posts
    1,443
    Thanks
    40
    Thanked 337 Times in 283 Posts
    Quote Originally Posted by aquamoon View Post

    Should the inverters be connected directly to mains and not via the earth leakage? When on grid there are essentially 2 earth leakages power will flow through to any endpoint. The sans recommended layout for a UPS system seems to indicate doing it the way I have done it.


    Sent from my iPhone using Tapatalk
    Something sounds wrong with the positioning of your ELU - Should be mains power - inverter - earth leakage -plug CB

    I am reading that you have the ELU before the inverter ?

    The Annex P shows ELU but be careful that they are not referring to a +/- 100ma unit because no decent earth can be obtained

  11. #9
    New Member
    Join Date
    Apr 2024
    Location
    Johannesburg
    Posts
    6
    Thanks
    3
    Thanked 0 Times in 0 Posts
    Quote Originally Posted by GCE View Post
    Something sounds wrong with the positioning of your ELU - Should be mains power - inverter - earth leakage -plug CB

    I am reading that you have the ELU before the inverter ?

    The Annex P shows ELU but be careful that they are not referring to a +/- 100ma unit because no decent earth can be obtained
    I do have the inverters connected after the main EL. I also have an EL for each of the 2 outputs of the combined inverters outputs.

    So when on grid power, power flows through 2 EL’s to an endpoint (e.g a plug point) Could this, having power flow through 2 EL’s be causing a problem?

    I felt that having the inverters on the min EL would be a safer option if something were to go wrong with the inverters themselves although Aircon’s are not connected to EL because they often cause nuisance trips being exposed to the elements. They are also “supposedly” out of reach of users.

    Could you explain more about your comment on Annex P?


    Sent from my iPhone using Tapatalk

  12. #10
    New Member
    Join Date
    Apr 2024
    Location
    Johannesburg
    Posts
    6
    Thanks
    3
    Thanked 0 Times in 0 Posts
    The geysers and pool were connected to the main db earth leakage as well, they are disconnected for now while I try and find the fault.


    Sent from my iPhone using Tapatalk

Page 1 of 2 12 LastLast

Similar Threads

  1. High neutral earth reading
    By Thys LOW Elektries in forum Electrical Contracting Industry Forum
    Replies: 6
    Last Post: 27-Mar-22, 02:26 PM
  2. Over voltage and lost neutral protection
    By ians in forum Electrical Contracting Industry Forum
    Replies: 7
    Last Post: 13-Mar-20, 07:16 PM
  3. Voltage between Neutral and Earth - When is it a fault?
    By Justloadit in forum Electrical Contracting Industry Forum
    Replies: 5
    Last Post: 20-Jul-19, 09:23 PM
  4. ELEVATED VOLTAGE TO NEUTRAL ABOVE 50 V -NOTICE OF POTENTIAL DANGER
    By Tshepo Mokoena in forum Electrical Contracting Industry Forum
    Replies: 5
    Last Post: 26-Apr-18, 08:26 AM
  5. Elevated voltage on supply neutral measurement
    By PaulG in forum Electrical Contracting Industry Forum
    Replies: 8
    Last Post: 05-Mar-16, 07:45 PM

Did you like this article? Share it with your favourite social network.

Did you like this article? Share it with your favourite social network.

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •