    When disconnecting the neutral of the cable supplying the pool db from the main db neutral bar and then measuring the voltage between the main db live and the disconnected neutral I get 230V, I would expect to get 0V. What am I missing?
    Mar 2019
    East london
    The neutral of the cable is probably down to earth somewhere. Megger test the cable.
    aquamoon (08-Apr-24)
  4. #3
    Mar 2019
    East london
    I suppose the earth leakage was tripping, the reason for you disconnecting the cable.
  5. #4
    Mar 2019
    East london
    Disconnect the cable at the pool end as well and then measure the voltage again.
  7. #5
    Apr 2024
    I was getting intermittent earth leakage trips, once I disconnected the neutral the trips went away.
    It only seemed to start after a db rewire where previously the pool was on its own leakage and now it’s part of the main earth leakage. That rewire was fine until it started raining, then the trips began.
    Sent from my iPhone using Tapatalk
  8. #6
    Mar 2019
    East london
    Yep. Cable down to earth somewhere, for sure.
  9. #7
    Apr 2024
    The trips have resumed, so it is not the cable to the pool causing the trips, since then I have disconnected the geysers neutrals as well, still trips.
    I have 2 Victron Multiplus connected in parallel mode. These are connected to the main db earth leakage. The Victrons each have 2 outputs, which are combined in parallel. Each of these outputs is connected to an earth leakage. All plugs and lights are on the first output and the stove on the second. I want to be able to program the system to only allow the second output to be on under certain conditions.
    I have no trips when the inverters switch to inverting or when they switch back to grid power. All worked well until recently. When on grid power I experience intermittent trips. No trips when on inverter power.
    Should the inverters be connected directly to mains and not via the earth leakage? When on grid there are essentially 2 earth leakages power will flow through to any endpoint. The sans recommended layout for a UPS system seems to indicate doing it the way I have done it.
  10. #8
    Apr 2024
    The geysers and pool were connected to the main db earth leakage as well, they are disconnected for now while I try and find the fault.
  11. #9
    Mar 2019
    East london
    You mention that when on grid power there are intermittant trips but not when in islanding mode.
    From the above I seem to think that there's no earth neutral bridge when the inverter is in islanding mode, so the earth leakage cannot trip even if there's an earth fault.
    I'm gonna stick my neck out and say there are 2 faults.
    1. An intermittant earth fault on the neutral.
    2. No earth neutral bridge when in islanding mode.
    Good luck.
  12. #10
    Nov 2023
    South africa
    I would expect to get around 230V between live and neutral how else is stuff going to work its probably flowing through a timer. I would disconnect both ends of the cable going to the pool db then megger that cable between live and earth, neutral and earth, live and neutral.Also im not sure you are a electrician looking at the questions your asking. Do you have a megger?
  1. High neutral earth reading
    Last Post: 27-Mar-22, 02:26 PM
  2. Over voltage and lost neutral protection
    Last Post: 13-Mar-20, 07:16 PM
  3. Voltage between Neutral and Earth - When is it a fault?
    By Justloadit in forum Electrical Contracting Industry Forum
    Last Post: 20-Jul-19, 09:23 PM
  4. ELEVATED VOLTAGE TO NEUTRAL ABOVE 50 V -NOTICE OF POTENTIAL DANGER
    By Tshepo Mokoena in forum Electrical Contracting Industry Forum
    Last Post: 26-Apr-18, 08:26 AM
  5. Elevated voltage on supply neutral measurement
    By PaulG in forum Electrical Contracting Industry Forum
    Last Post: 05-Mar-16, 07:45 PM