    Kitchen sink bonding

    Hi

    Bonding questions.

    1 .A stainless steel sink supported by a stainless steel frame and legs.It has pvc drain pipes and those flexible metal braided pipes feeding from the copper water supply to the sink mixer.

    2.What if my resistance reading to the sink is 0.2 Ohms or less.

    Must this sink be bonded?

    Thanks for all the previous informative discussions.


    Sent from my CPH2197 using Tapatalk

  2. #2
    Platinum Member Derlyn's Avatar
    Join Date
    Mar 2019
    Location
    East london
    Posts
    1,526
    Thanks
    106
    Thanked 146 Times in 139 Posts
    From where are you measuring 1,2 ohms ? Between the sink and what ?

  3. #3
    Platinum Member Derlyn's Avatar
    Join Date
    Mar 2019
    Location
    East london
    Posts
    1,526
    Thanks
    106
    Thanked 146 Times in 139 Posts
    Sorry typo. 0,2 ohms.

  4. #4
    Full Member
    Join Date
    Apr 2016
    Location
    South Africa
    Posts
    75
    Thanks
    34
    Thanked 1 Time in 1 Post
    I have not measured it yet.
    It would be between switch socket outlet cover and sink.


    Sent from my CPH2197 using Tapatalk

  5. #5
    Junior Member
    Join Date
    Nov 2023
    Location
    South africa
    Posts
    22
    Thanks
    0
    Thanked 0 Times in 0 Posts
    I believe if it is less than 7.7 Kohm to the earth terminal it needs to be bonded.

  6. #6
    Full Member
    Join Date
    Apr 2016
    Location
    South Africa
    Posts
    75
    Thanks
    34
    Thanked 1 Time in 1 Post
    Thanks
    Where did you get this info from?


    Sent from my CPH2197 using Tapatalk

  7. #7
    Junior Member
    Join Date
    Nov 2023
    Location
    South africa
    Posts
    22
    Thanks
    0
    Thanked 0 Times in 0 Posts
    https://youtu.be/TFt3d77LujQ?si=YXW4slj0HgI-lLuh its not sans but how would one know when something is extraneous conductive?

  8. #8
    Full Member
    Join Date
    Apr 2016
    Location
    South Africa
    Posts
    75
    Thanks
    34
    Thanked 1 Time in 1 Post
    Interesting.
    Thanks


    Sent from my CPH2197 using Tapatalk

  9. #9
    Platinum Member
    Join Date
    Jun 2017
    Location
    Port Elizabeth
    Posts
    1,266
    Thanks
    34
    Thanked 308 Times in 260 Posts
    You Tube can be a dangerous place to take information and regard it as gospel - Rather check against the actual regulations

    Sans requires hot and cold water systems to be bonded and then also refers to everything within arms reach etc - So in short , I would say you need to test and make sure it is within 0.2ohm - It does not need to have a physical bonding strap

    Extract from SANS 10142-1 ed 3.1 below

    6.13 Bonding
    NOTE 1 The aim of bonding is to bring all the bonded parts to the same electrical
    potential.
    NOTE 2 No external conductor is required if compliance with the requirements for
    continuity can be proved by the test in 8.6.2.


    6.13.2.2 Hot and cold water systems
    Where the hot water system includes electric components and the water pipes
    are of conducting material, hot and cold water systems shall be bonded
    together and also be bonded to the earth continuity conductor system.

    8.6.2 Continuity of bonding
    Confirm the continuity of the bonding conductors between all exposed
    conductive parts within arms reach (or see annex A) of each other. When a
    test device or instrument is used, it shall have a supply that has a no‐load d.c.
    or a.c. voltage of 4 V to 24 V, and a current of at least 0,2 A. In each case, the
    resistance shall not exceed 0,2 Ω.

  10. #10
    Full Member
    Join Date
    Apr 2016
    Location
    South Africa
    Posts
    75
    Thanks
    34
    Thanked 1 Time in 1 Post
    Thanks
    Something I was wrestling with.My brain hit a miss. If all bonding is correct .What about touch potential .One hand touches the correctly bonded pipes with feet on the ground.Current should always take the easiest way to earth via bonding and earth bar.Not through the person.

    Sent from my CPH2197 using Tapatalk

Similar Threads

  1. [Question] Kitchen remodel
    By Chris_7 in forum Electrical Contracting Industry Forum
    Replies: 1
    Last Post: 07-Jun-22, 09:31 AM
  2. Bonding
    By Gtfast in forum Electrical Contracting Industry Forum
    Replies: 6
    Last Post: 22-Aug-19, 07:38 AM
  3. Kitchen appliances - recommendations?
    By Basment Dweller in forum General Business Forum
    Replies: 28
    Last Post: 02-Oct-14, 06:10 PM

Did you like this article? Share it with your favourite social network.

Did you like this article? Share it with your favourite social network.

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •