    Prepaid meter fault.

    Landis & Gyr 3 ph prepaid meter.

    When power comes on after loadshedding, the meter does not come back on and the display stays blank.

    Now if one bridges the line and load on phase 1 momentarily, it switches the meter on until the next loadshedding, then the meter doesn't switch on again after loadshedding.

    A first for me.

    Any ideas ?

  2. #2
    Platinum Member
    Join Date
    Jun 2017
    Location
    Port Elizabeth
    Posts
    1,304
    Thanks
    36
    Thanked 314 Times in 263 Posts
    Almost sounds like line and load has been reversed , or the internal relay wire has been taken from load side instead of line side

  3. #3
    Platinum Member Derlyn's Avatar
    Join Date
    Mar 2019
    Location
    East london
    Posts
    1,586
    Thanks
    113
    Thanked 151 Times in 143 Posts
    Found by mistake 🤣 Decided to temporarily bypass the meter so that the restaurant could carry on with business. Turned off all loads and as soon as I put in that first bridge, the meter switched on.

    Anyway, I'll wait for the next loadshedding and open the meter to check connections. What baffles me is that this is a new fault. This meter has been operating perfectly for 2 years.

    Thanks brother. Will give feedback.

  4. #4
    Platinum Member Derlyn's Avatar
    Join Date
    Mar 2019
    Location
    East london
    Posts
    1,586
    Thanks
    113
    Thanked 151 Times in 143 Posts
    Bit of feedback. @ GCE, you were 100% correct. Line and load swopped on all 3 phases.

    This is what I found. Thicker wires are line.

    Click image for larger version. 

Name:	20240110_144211.jpg 
Views:	168 
Size:	46.0 KB 
ID:	8869


    After a bit of investigating it was found that 6 months after the previous tenant moved in 2 years ago was the last electricity purchase.

    The meter was bypassed on the meter terminals. Then shortly before the tenant vacated the premises at end December, he got a buddy to remove the tamper but his buddy got the lines and loads wrong. The landlord is now taking legal action to recoup for the 18 months stolen electricity.

    Never a dull moment.

  5. Thanks given for this post:

    GCE (11-Jan-24)

Similar Threads

  1. Re setting a prepaid meter
    By Derlyn in forum Electrical Contracting Industry Forum
    Replies: 20
    Last Post: 14-May-23, 01:30 PM
  2. CIU PLC-WL1 Prepaid Meter Backlight
    By Smurfi in forum General Chat Forum
    Replies: 0
    Last Post: 08-Jun-21, 09:58 AM
  3. [Question] Prepaid electricity meter connection
    By Ferdie_l in forum General Regulatory Compliance Forum
    Replies: 1
    Last Post: 07-Aug-20, 05:37 PM
  4. [Question] COC for a private prepaid meter
    By Georgej in forum Electrical Contracting Industry Forum
    Replies: 1
    Last Post: 01-Jan-20, 04:09 PM
  5. Vat on Prepaid Sub Meter
    By Manko in forum Tax Forum
    Replies: 1
    Last Post: 24-Aug-18, 02:29 PM

Did you like this article? Share it with your favourite social network.

Did you like this article? Share it with your favourite social network.

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •