    Twin and earth in cement.

    Are there any regulations that prohibit flat twin and earth from being cemented into walls without being in conduit.

    Busy with a coc and just wan't to make sure.

  2. #2
    Platinum Member
    Join Date
    Jun 2017
    Location
    Port Elizabeth
    Posts
    1,304
    Thanks
    36
    Thanked 314 Times in 263 Posts
    My understanding is that Twin and earth is covered under 6.4.6.2 - Clause 6.3.6 covers Surfix

    Manufacturers instructions will come into play as well and have pasted an extract from Aberdare

    In short , I would say yes it can be buried in plaster without conduit but if it goes through a concrete beam it would need to be failed

    6.4.6.2 Unarmoured multicore cables do not require additional mechanical
    protection if they are installed
    a) under plaster in walls, or
    b) under raised floors, in spaces above ceilings, in partitions or in wall cavities,
    but only if they will not be damaged during installation.


    6.3.6 PVC insulated multicore cables with a bare earthing conductor
    and round cable with metal stiffening
    6.3.6.1 The cables may be installed
    a) on the surface,
    b) under plaster,
    c) under a raised floor,
    d) in hollows (such as in walls and partitions) (no additional protection being
    needed),
    e) in roof spaces,
    f) direct in the ground (see 6.4.4.2, unarmoured buried cables),
    g) outdoors or exposed to water (but unless the manufacturer proves that the
    cables can withstand ultraviolet radiation, the cable shall be out of sight of
    the sky), and
    h) under screed if protected by an earth leakage protection device with a rated
    earth leakage tripping current (rated residual current) IΔn not exceeding
    30 mA.
    6.3.6.2 These cables shall not be buried direct in concrete.




    Aberdare Cable Brochure
    Cable Description
    Installation Information
    Properties
    Copper conductors to SANS 1411 Part 1, PVC insulated to SANS 1411 Part 2, laid up with a bare copper earth-continuity-conductor
    between them, UV stable PVC sheathed to SANS 1411 Part 2.
    Complies with SANS 10142/2001“Code of Practice for the wiring of Premises” Section 6, Clause 6.3.6:
    • Surface wiring • Under-plaster wiring • Roof access wiring • Wiring in hollowwalls

    The cable shall not be buried direct in concrete or in screed. Joints in the wiring shall be in boxes only.

  3. #3
    Platinum Member Derlyn's Avatar
    Join Date
    Mar 2019
    Location
    East london
    Posts
    1,586
    Thanks
    113
    Thanked 151 Times in 143 Posts
    Thank you my brother.
    Just wanted to confirm.

Similar Threads

  1. Using the earth wire of the twin+E as alive conductor
    By Isetech in forum Electrical Contracting Industry Forum
    Replies: 25
    Last Post: 26-Jun-22, 04:58 PM
  2. Twin and earth stripped.
    By Derlyn in forum Electrical Contracting Industry Forum
    Replies: 2
    Last Post: 25-May-21, 06:12 PM
  3. [Question] Twin-earth cable sheathing removed
    By Ishmaelmo in forum Electrical Contracting Industry Forum
    Replies: 10
    Last Post: 07-Jun-19, 08:39 AM
  4. Twin and earth connections .
    By Gtfast in forum Electrical Contracting Industry Forum
    Replies: 2
    Last Post: 23-Feb-18, 08:59 PM
  5. twin and earth question
    By Hotspot in forum Electrical Contracting Industry Forum
    Replies: 4
    Last Post: 20-Jun-16, 10:10 PM

Did you like this article? Share it with your favourite social network.

Did you like this article? Share it with your favourite social network.

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •