    Neutral earthing

    Been familiarising myself once again with SANS 10142 with regards neutral earthing.

    Couldn't help but had a little chuckle when reading 7.16.4.5.

    Is that regulation really necessary ?

  2. #2
    Site Caretaker Dave A's Avatar
    Join Date
    May 2006
    Location
    Durban, South Africa
    Posts
    22,789
    Thanks
    3,331
    Thanked 2,694 Times in 2,271 Posts
    Blog Entries
    12
    To save folk looking up the clause:

    7.16.4.5 The neutral shall not be earthed beyond any earth leakage unit.

    I can imagine how that conversation went in the SANS committee:

    Derlyn: Is that regulation really necessary ?

    Cecil: If we don't put it in, some idiot will f. it up and then blame us for their f-up.

  3. Thanks given for this post:

    Dylboy (01-Dec-23)

  4. #3
    Platinum Member Derlyn's Avatar
    Join Date
    Mar 2019
    Location
    East london
    Posts
    1,708
    Thanks
    127
    Thanked 160 Times in 150 Posts
    It's the same as saying .... " the live should not be connected to the neutral or earth anywhere on the installation. 😂😂

  5. #4
    Platinum Member
    Join Date
    Jun 2017
    Location
    Port Elizabeth
    Posts
    1,443
    Thanks
    40
    Thanked 337 Times in 283 Posts
    Quote Originally Posted by Derlyn View Post
    Been familiarising myself once again with SANS 10142 with regards neutral earthing.

    Couldn't help but had a little chuckle when reading 7.16.4.5.

    Is that regulation really necessary ?
    I agree - Sometimes people don't think and bear in mind that some municipalities insist on an Adit unit when the supply is greater than 300KVA - The Adit unit may not pick up the neutral earth bridge due to it being set a lot higher than 30ma

Similar Threads

  1. Generator earthing
    By Jurie999 in forum Electrical Contracting Industry Forum
    Replies: 1
    Last Post: 05-May-23, 06:23 AM
  2. Earthing
    By TECHNICIAN 810 in forum Electrical Contracting Industry Forum
    Replies: 16
    Last Post: 04-Apr-23, 04:53 AM
  3. earthing
    By BEVIN in forum Electrical Contracting Industry Forum
    Replies: 2
    Last Post: 07-May-19, 03:29 PM
  4. Box earthing
    By Gtfast in forum Electrical Contracting Industry Forum
    Replies: 3
    Last Post: 13-Mar-17, 06:36 PM
  5. Earthing and the CoC
    By WallyL in forum General Regulatory Compliance Forum
    Replies: 11
    Last Post: 20-Jan-11, 12:06 AM

Did you like this article? Share it with your favourite social network.

Did you like this article? Share it with your favourite social network.

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •