I inspected a house for a COC and found the following:
Incoming SWA cable splits in a Pratley box. A 3-core 10mm2 cable goes to the house db and a 2-core 16mm2 cable goes to the garage db.
The earth wire is a 6mm wire from an earth spike to the garage db.
Questions:
Are both DB's now main db's?
Does the main breakers in both db's need to be 2-pole breakers, since both are currently 1-poles?
The earth wire needs to be a 10mm2 or bigger wire, and it must come from the Pratley box
The other things are small things and I know the answer to that but the rest are a grey area for me.
The house is an old house of 20 years or more, the supply had been upgraded. All cabling and wiring are plastered into the walls.
I plan on upgrading the breakers to 2-poles and installing a new earth wire, I was just curious about the rest