    High earth loop

    Hello : )

    First time since going my own I have a property with a high loop, 4.15ohms.

    Is it the client to phone the power supplier to sort or is it up to me ?

    As I see it the client needs to do it but what is the consensus of who calls the power supplier ?

    I assume the fix they would do is to make it a TNC-S as it is TNS so they just add a large cable to join the neutral and earth.

    Old old property, bought in 2015 where the CoC for that sale the oke put in infinity symbol for the reading. So I assume been bad for a long time !

    A few things on it is just wrong so not worth the paper as usual but still need to get it sorted.

    Sent from my CPH2197 using Tapatalk

  2. #2
    Silver Member
    Join Date
    Jan 2021
    Location
    Orania
    Posts
    231
    Thanks
    12
    Thanked 21 Times in 19 Posts
    Normally they put a bridge between the earth and the neutral, easy cheap, and legal
    We have a kiosk on the outside of the houses where the council's supply comes in.
    We just put a bridge between the neutral and the earth stud inside the kiosk and the problem is sorted out
    TNC-S systems are old and we are phasing it out, replacing it with the TNS system.

  3. #3
    Gold Member
    Join Date
    Jun 2020
    Location
    Fourways
    Posts
    769
    Thanks
    119
    Thanked 35 Times in 34 Posts
    Yes ya I assume so and seen it before l. Basically make a TNS and TNC-S.

    Thing is with this is the TNS will be converted to TNC-S. Not sure of all the pros and cons other than on a TNC-S if the neutral is lost or becomes high restsitance a shit ton of current flows through the earth cables and plumbing and metal fittings.

    Wish I could get a paid for bursary and become and electrical engineer hahaha then I may have some answers haha

    Sent from my CPH2197 using Tapatalk

  4. #4
    Silver Member
    Join Date
    Jan 2021
    Location
    Orania
    Posts
    231
    Thanks
    12
    Thanked 21 Times in 19 Posts
    The problem started in the early 60's with the use of a 4-wire system, it was very common and cheap, mainly for 3-phase equipment with no earth.
    They brought the cable to a kiosk, without an earth, in the kisok they bridge everything to create an earth.
    Only later did they realise it might work good in a factory or comercial building but not in a house.
    https://www.youtube.com/watch?v=0nEsrlLpOzs

Similar Threads

  1. Pscc and earth loop
    By Dylboy in forum Electrical Contracting Industry Forum
    Replies: 2
    Last Post: 20-Oct-23, 10:04 PM
  2. High loop impedance reading
    By ians in forum Electrical Contracting Industry Forum
    Replies: 10
    Last Post: 06-Oct-21, 12:47 PM
  3. Earth loop impedance testing
    By ians in forum Electrical Contracting Industry Forum
    Replies: 16
    Last Post: 24-Jan-19, 09:34 AM
  4. high loop impedance reading
    By ians in forum Electrical Contracting Industry Forum
    Replies: 3
    Last Post: 20-May-15, 07:00 PM
  5. [Question] Earth Loop (Can it be achieved?)
    By Neal in forum Electrical Contracting Industry Forum
    Replies: 2
    Last Post: 19-Jun-13, 12:49 AM

Did you like this article? Share it with your favourite social network.

Did you like this article? Share it with your favourite social network.

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •