    Pscc and earth loop

    So we do the PSCC and Earth loop at the main switch, we get a reading that in hopes allows a current enough for double the rating of the main switch,

    Now why not like the UK we test the the earth loop and PSCC at a socket and the furthest socket to make sure the CB feeding the socket can trip, we just have to make sure the ECC is of low resistance that of a table.

    So is it assumed here that is the current tested at the main switch being enough to trip that then the ECC of the socket circuit being in range of the table then it will trip?

    In the UK they do the Zs=ZE+(R1+R2)

    Where they make sure the resistance of the the whole circuit to the TX is taking into account to make sure it trips.

    To me, testing at the main switch the Ze or the PSCC / Eloop at the main switch is not ideal as the only measurement.

    We should do the PSCC and E loop at sockets as well to make sure the CB will trip. It will also pick up if the earth cable not there or high resistance due to the readings obtained.

    Anyway just something I think of and have some time to type it haha

    Sent from my CPH2197 using Tapatalk

  2. #2
    Full Member
    Join Date
    Aug 2018
    Location
    Capetown
    Posts
    42
    Thanks
    0
    Thanked 1 Time in 1 Post
    Hi, testing pscc at sockets will just tripp the earth leakage and the reading will be lower at the socket since it's further from the transformer, while the mcbs will have to withstand the pscc since they're closer.
    Testing earth loop impedance at a socket will also just tripp the earth leakage. Your max reading will be 5.75ohms provided there's 230v and fed from a 20mcb.
    I don't see what there is to gain by doing that but will experiment a bit and find out.

    Sent from my R1PLUS_1 using Tapatalk

  3. #3
    Full Member
    Join Date
    Aug 2018
    Location
    Capetown
    Posts
    42
    Thanks
    0
    Thanked 1 Time in 1 Post
    We also have sans10142 , full of tables containing min. wire size , max. length, current carrying capacity , ect and a whole lot of safety features. South Africa introduced the earth leakage to the world. It must say something about us.

    Sent from my R1PLUS_1 using Tapatalk

Similar Threads

  1. Earth loop impedance test result
    By Andrew_van_Zyl in forum Electrical Contracting Industry Forum
    Replies: 1
    Last Post: 19-Jun-22, 12:49 PM
  2. Earth loop impedance testing
    By ians in forum Electrical Contracting Industry Forum
    Replies: 16
    Last Post: 24-Jan-19, 09:34 AM
  3. Earth loop impedance and prospective short circuit (PSC)
    By mikilianis in forum Electrical Contracting Industry Forum
    Replies: 11
    Last Post: 21-Jan-16, 04:10 PM
  4. [Question] Earth Loop Impedance on COC test.
    By Jasond MIE in forum Electrical Contracting Industry Forum
    Replies: 8
    Last Post: 06-Mar-15, 01:42 PM
  5. [Question] Earth Loop (Can it be achieved?)
    By Neal in forum Electrical Contracting Industry Forum
    Replies: 2
    Last Post: 19-Jun-13, 12:49 AM

Did you like this article? Share it with your favourite social network.

Did you like this article? Share it with your favourite social network.

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •